CJ7VFR, I found this at another site:
Depends on where it's being installed.
250.8 Connection of Grounding and Bonding Equipment.
(A) Permitted Methods. Grounding conductors and bonding jumpers shall be connected by one of the following
means:
(1) Listed pressure connectors
(2) Terminal bars
(3) Pressure connectors listed as grounding and bonding equipment
(4) Exothermic welding process
(5) Machine screw-type fasteners that engage not less than two threads or are secured with a nut
(6) Thread-forming machine screws that engage not less
than two threads in the enclosure
(7) Connections that are part of a listed assembly
(8) Other listed means
250.126 Identification of Wiring Device Terminals. The terminal for the connection of the equipment grounding conductor shall be identified by one of the following:
(1) A green, not readily removable terminal screw with a hexagonal head.
(2) green, hexagonal not readily removable terminal nut.
(3) A green pressure wire connector. If the terminal for the grounding conductor is not visible, the conductor entrance hole shall be marked with the word green or ground, the letters G or GR, a grounding symbol, or otherwise indentified by a distinctive green color. If the terminal for the equipment grounding conductor is readily removable, the area adjacent to the terminal shall be similarly marked.
406.9 Grounding-Type Receptacles, Adapters, Cord Connectors, and Attachment Plugs.
(B) Grounding-Pole Identification. Grounding-type receptacles, adapters, cord connections, and attachment plugs shall have a means for connection of an equipment grounding conductor to the grounding pole.
A terminal for connection to the grounding pole shall be designated by one of the following:
(1) A green-colored hexagonal-headed or -shaped terminal screw or nut, not readily removable.
(2) A green-colored pressure wire connector body (a wire barrel).
(3) A similar green-colored connection device, in the case of adapters. The grounding terminal of a grounding adapter shall be a green-colored rigid ear, lug, or similar device. The equipment grounding connection shall be so designed that it cannot make contact with current-carrying parts of the receptacle, adapter, or attachment plug. The adapter shall be polarized.