I'm installing a 150amp subpanel to my new garage. The run is about 125ft, my research shows that I need two #1 copper lines for that long of a run. Does this sound correct?
I'm installing a 150amp subpanel to my new garage. The run is about 125ft, my research shows that I need two #1 copper lines for that long of a run. Does this sound correct?
Better ? No. More expensive ? HELL YES.Is copper a better choice then aluminum?
Is copper a better choice then aluminum? From my reading, I would need 2/0 in aluminum correct?
2 is good for 90
How is this panel going to be fed?
I'm installing a 150amp subpanel to my new garage. The run is about 125ft, my research shows that I need two #1 copper lines for that long of a run. Does this sound correct?
Fed off my main 200amp panel. I'm debating on either pulling off the main feed (always hot) or installing two 70amp breakers. I went with two runs of #4 cooper as it showed #4 rated 85amps each.
I don't think I will ever use 150amps but it was the only one I could find with 15slots, above 125amp, and had a main breaker.
Items on the panel;
-A/C
-hot tub
-air compressor
-welder
-40 T5 lights
-RV
Fed off my main 200amp panel. I'm debating on either pulling off the main feed (always hot) or installing two 70amp breakers. I went with two runs of #4 cooper as it showed #4 rated 85amps each.
you need a little help with this. Did you already buy the wire?
............. yea. I got a good deal on it.
You need a pro electrician, seriously. You are way off on how to do this and are going to end up with major code issues.
Put a breaker in the panel, connect to the breaker, the same way every circuit in your house is fed. Wire and breaker sized correctly according to load.Ok, let's start from the beginning... What is the preferred method of pulling power off the main panel?
Ok, let's start from the beginning... What is the preferred method of pulling power off the main panel?
Fed off my main 200amp panel. I'm debating on either pulling off the main feed (always hot) or installing two 70amp breakers. I went with two runs of #4 cooper as it showed #4 rated 85amps each.
I had a similar situation with my shop that I'm building now. I installed a 150 amp panel with its own meter from the pole 100 feet away. Most of the charts say that I could use 2/0 aluminum, but that ultimately wasn't correct. Since it was a detached garage, the code assumes a higher duty cycle and forced me to use 3/0 aluminum.
In this project, I've discovered a lot of details like this that you'll get wrong if you don't dig in.
So an item like this is what is recommend to pull power off the main panel?
https://www.amazon.com/dp/B002KGFTXU/?tag=atomicindus08-20
I'm surprised nobody has commented on this one yet. You can't parallel conductors smaller than 1/0, so your plan of 2 runs of #4 won't be code compliant, and connecting them to 2 different breakers is certainly not. There are absolutely TONS of threads on people installing sub panels just like you, with lots of good advice given. There's even an FAQ sticky with info from Wylies on feeding separate structures. Do some more research before you waste any more money on parts.
It basically boils down to this:
You don't need to match the rating of subpanel with your feeder breaker/cable. You can feed your 150A sub with any size breaker and properly sized wire you want.
You most likely don't need anywhere near 150A
Most people go with #2 MHF in 2" conduit and a 90A breaker. Simple, cost effective and works.
You haven't stated if this is an attached or detached structure, that will also effect how this is wired, and particularly grounded. (you're slipping on asking that question Wylies)
I had a similar situation with my shop that I'm building now. I installed a 150 amp panel with its own meter from the pole 100 feet away. Most of the charts say that I could use 2/0 aluminum, but that ultimately wasn't correct. Since it was a detached garage, the code assumes a higher duty cycle and forced me to use 3/0 aluminum.
In this project, I've discovered a lot of details like this that you'll get wrong if you don't dig in.
So an item like this is what is recommend to pull power off the main panel?
https://www.amazon.com/dp/B002KGFTXU/?tag=atomicindus08-20
Going to return the wire tomorrow and get 1/0...
WAIT!
Figure your loads first before you buy wire.
I bet you could get by with 90a or less....
After we yanked him somewhat firmly, I was encouraged when he came back and asked. "OK, lets start from the beginning"
And gave him what I thought was a decent plan for him to explore with us what is needed to get to a 'purchase parts, install them". Basically 5 steps.
Instead he is asking about specific 125A breakers and buying very expensive wire.
Whatever.... Horse>>>>Water>>>Dead Horse.
PS I did catch his '85A for#4 so that and two 75A breakers gives you 150A service'...my comment was "The idea that you can add wires and breakers like preschool math problems is...scary."
Power needs:
-40 to 50 T5 lights 50x32=1600W=13,3A @ 120
-Smaller 220v air compressor (not purchased yet) 20A @ 240?
-AC/Heat pump. ??? Just for the 1300 sqft shop? 15A @ 240 ??
-220v tig ??20A @ 240
-Hot tub. 15A @120... Or ????
-Lift 15A @ 120
-beer fridge misc
-stereo misc
-misc chargers misc
Just guessing from these numbers you have: 43A @ 120, figure another 27 with misc'... So 70A @ 120 or 35A at 240.
Then you have 55A at 240.
Add them up, 90A at 240 (I **swear** this is a coincidence.)
This is a rudimentary calc- there is no allowances for continuous load versus stop/start. Also, I just guessed at some of your loads as you didn't provide.
Your wild card is the hot tub plus the HVAC. These are not usual loads on an attached garage. My hot tub is on a 50A240V breaker. One of my HVAC units is on a 40A240V breaker- how ever as I recall this might only draw 20-24 A when running?
Let's see what others say
running even though nameplate says 14a (i measured with my 381)...my last place had an older 3 ton unit and it pulled closer to 20a. They get more efficient every year...You need 4 wires for a sub panel, 2 hot, one neutral and one ground.So with no rods needed, I'll need to install three runs, two HOT and one common... As per the diagram in the FAQ section?
So with no rods needed, I'll need to install three runs, two HOT and one common... As per the diagram in the FAQ section?
So with no rods needed, I'll need to install three runs, two HOT and one common... As per the diagram in the FAQ section?