I currently have a 200 amp main panel and a sub panel in an attached garage protected by a 60 amp breaker. I am setting the garage up for a metal working (hobby) shop. My loads (not all running simultaneously) in the garage will be as follows:
54 FLA @ 240v 3ph 10 hp phase converter [(10 hp x 743 / 240v) x 1.73]*
25 FLA @240v 1ph air compressor
125 FLA @ 240v 1ph welder **
30 FLA @240v heating/cooling
* = not sure if this is the proper way to calculate the draw for a rotary phase converter.
** = FLA @ 100% duty cycle & 100% output power on this machine. I will never come close to utilizing this and will probably put the machine on a 60 amp breaker.
So I need to upgrade the garage's sub panel and would like to go to 200 amp so it won't be an issue if I want to weld, have the AC on, and have the air compressor kick in all at the same time. Adding a second meter isn't an option. What I would like to do is get a subfeed lug kit for my main panel and run aluminum wire 4/0 4/0 4/0 #6 (ground) from the subfeed lug on the 200 amp main panel to a new 200 amp sub panel. Is this the correct way to do this via code? The feeder to the sub panel would technically be protected by the 200 amp main breaker on the main panel. The sub panel would also have a 200 amp breaker on the feed at the top of the panel for a local disconnect. The sub feed lug kit available for my panel is rated for 225 amps and the the wire should appropriately sized for 200 amps and at 150' will have a voltage drop of ~3.5%.
Anything I'm missing? I'd hate to spend $1.5k on materials to find out come inspection that this isn't allowed.
54 FLA @ 240v 3ph 10 hp phase converter [(10 hp x 743 / 240v) x 1.73]*
25 FLA @240v 1ph air compressor
125 FLA @ 240v 1ph welder **
30 FLA @240v heating/cooling
* = not sure if this is the proper way to calculate the draw for a rotary phase converter.
** = FLA @ 100% duty cycle & 100% output power on this machine. I will never come close to utilizing this and will probably put the machine on a 60 amp breaker.
So I need to upgrade the garage's sub panel and would like to go to 200 amp so it won't be an issue if I want to weld, have the AC on, and have the air compressor kick in all at the same time. Adding a second meter isn't an option. What I would like to do is get a subfeed lug kit for my main panel and run aluminum wire 4/0 4/0 4/0 #6 (ground) from the subfeed lug on the 200 amp main panel to a new 200 amp sub panel. Is this the correct way to do this via code? The feeder to the sub panel would technically be protected by the 200 amp main breaker on the main panel. The sub panel would also have a 200 amp breaker on the feed at the top of the panel for a local disconnect. The sub feed lug kit available for my panel is rated for 225 amps and the the wire should appropriately sized for 200 amps and at 150' will have a voltage drop of ~3.5%.
Anything I'm missing? I'd hate to spend $1.5k on materials to find out come inspection that this isn't allowed.