Rheem Tankless Water Heater

jim1450

Active member
Joined
Jun 11, 2013
Messages
27
Location
Sandusky, OH
I have a Rheem rte 13 http://www.rheem.com/product/point-of-use-tankless-electric-rte-13
Looking @ the table it says use # 6 with a 60 amp breaker but the whip that came pre wired to it is labeled Romex 10, it's 2 conductor with a ground.
I've had other small cheap electric tankless heaters before & you can run them for a long time.

Can anyone explain the #10 ?
 

Attachments

  • screenshot-www.manualslib.com-2017-09-13-17-25-50.jpeg
    screenshot-www.manualslib.com-2017-09-13-17-25-50.jpeg
    31.5 KB · Views: 66
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
OP
J

jim1450

Active member
Joined
Jun 11, 2013
Messages
27
Location
Sandusky, OH
Did you buy this new?

NM aka Romex isnt the proper wire to use for a whip.
Bought it new from Amazon, other 2 ebay heaters I had were wired different.

https://www.amazon.com/dp/B003UHUSGQ/?tag=atomicindus08-20
Sorry about picture size
81MuCWiag1L._SL1500_.jpg
 
Last edited:
OP
J

jim1450

Active member
Joined
Jun 11, 2013
Messages
27
Location
Sandusky, OH
Opened up, funny the mounting holes are all blocked by the chambers.
 

Attachments

  • 20170913_180832_LLS.jpg
    20170913_180832_LLS.jpg
    125.1 KB · Views: 136
Last edited:

MrSurly

Well-known member
Joined
Jan 15, 2014
Messages
1,671
Location
East Texas
It looks like the wire is labeled #6 2 cdr with a #10 ground wire. And it's NM-B and stranded and with a solid ground wire. Weird.
So, yeah it is legit, if unusual.

However, depending on where and how it's mounted, the NM-B may not be the proper type of wire as it must be protected if not inside a wall, etc
(As Wylie said)
 

Attachments

  • 2017-09-13_18-08-55.jpg
    2017-09-13_18-08-55.jpg
    11.2 KB · Views: 39
Last edited:

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,033
Location
NJ
It might be a returned item. that whip looks janky.

I think so too. Website indicates it comes with a 2' cord. The pic has a cable and the rx con is installed bass ackwards.

I would confirm the wattage of the unit (from nameplate) and wire according to that.

Unless of course they shipped a 3kw unit instead of 13.

You can always remove the cable and add your own cord with plug.
 
Last edited:
Joined
Sep 11, 2017
Messages
18
As an electrician I have not installed a unit that came w/cord. I would send it back if you are not sure[emoji848]


Sent from my iPhone using Tapatalk
 
OP
J

jim1450

Active member
Joined
Jun 11, 2013
Messages
27
Location
Sandusky, OH
Thanks
It's been sitting in my basement for a few years & I never got around to using it but since I'm getting a new barn built I thought I should.

After looking closer @ the whip it's #8 with a 10 ground, tag on it says 54 amps.
It's not as bad as I 1st thought but #8 seems small for something that could run for an extended period of time.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
Bought it new from Amazon, other 2 ebay heaters I had were wired different.

https://www.amazon.com/dp/B003UHUSGQ/?tag=atomicindus08-20
Sorry about picture size

yeah thats not 10/2 NM-b since the jacket is black and the wire stranded.

It is either #8 or #6....

It might be a returned item. that whip looks janky.

Agreed.

A manu. wouldnt use the wrong wire on a listed appliance.

It looks like the wire is labeled #6 2 cdr with a #10 ground wire. And it's NM-B and stranded and with a solid ground wire. Weird.
So, yeah it is legit, if unusual.

Not weird.

#6 and #8 NM-b comes with stranded hot and neutral conductors and solid ground wire.

http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheetOEM10

However, depending on where and how it's mounted, the NM-B may not be the proper type of wire as it must be protected if not inside a wall, etc
(As Wylie said)

NM-b can be ran outside of a wall as long as its not subject to pysical damage.

The proper wire for this equipment is cordage.

Thanks
It's been sitting in my basement for a few years & I never got around to using it but since I'm getting a new barn built I thought I should.

After looking closer @ the whip it's #8 with a 10 ground, tag on it says 54 amps.

It's not as bad as I 1st thought but #8 seems small for something that could run for an extended period of time.

NM-b wire is limited to 60* ampacities, so #8 NM-b is limited to 40a.

I agree with the others. Some previous buyer returned it and for whatever reason didnt have the original factory cord so they put a scrap piece of NM-b on it.

I would remove it and get, at minimum, some 6/3 SOOW cordage which is rated 55a.

Im not sure if the cordage would need to be upsized for continuous loading. If it does, you would need some 4/3 SOOW.

http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet282

It will need to be hardwired as well.

A better idea is to call Rheem and see if they can tell you what gauge cord comes with the unit from the factory.
 
OP
J

jim1450

Active member
Joined
Jun 11, 2013
Messages
27
Location
Sandusky, OH
yeah thats not 10/2 NM-b since the jacket is black and the wire stranded.

It is either #8 or #6....





NM-b wire is limited to 60* ampacities, so #8 NM-b is limited to 40a.

I agree with the others. Some previous buyer returned it and for whatever reason didnt have the original factory cord so they put a scrap piece of NM-b on it.

I would remove it and get, at minimum, some 6/3 SOOW cordage which is rated 55a.

Im not sure if the cordage would need to be upsized for continuous loading. If it does, you would need some 4/3 SOOW.

http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet282

It will need to be hardwired as well.

A better idea is to call Rheem and see if they can tell you what gauge cord comes with the unit from the factory.
Thanks again, plan on calling Rheem tomorrow.
Was a brand new unit, I bought plenty of stuff from Amazon Warehouse deals but not this & I believe if it was a return they would sell it as open box through warehouse.
Guess they could've mistakenly used the Romex from a RTE9 on my 13
The whip is too short anyway so I'll get a longer piece of #6 & connect it to the 100 amp sub panel.

I still have my last ebay heater from my old house along with the nm cable was on a 60 amp breaker, I'll have to look but it should be 6/2 with a ground.

Thanks everyone, I'll update tomorrow after I call Rheem
 
OP
J

jim1450

Active member
Joined
Jun 11, 2013
Messages
27
Location
Sandusky, OH
I emailed Rheem on Wed night, reply had the manual attached & a phone # to call.
I called the tech support & got transferred a few times & was told by the last clueless rep I talked that he had to put me on hold & check on it, I waited a long time & finally hung up.

I'll get a 6' piece 6/2 & run it from the heater terminals directly into the 100 amp sub in my basement.

I live in a rural part of north central OH & have a propane furnace, the only other thing that runs on propane is my older water heater so for now this will see limited use.
 

AP514

Well-known member
Joined
Jan 23, 2014
Messages
768
Location
Pearland, Tx
I had a buddy run one of these keep tripp'n the C/B..come to find out the water line into it was not higher than the unit it self No real head pressure. he ended up replumbing his water lines going into the unit.

you have Propane --use a Boche Gas unit way more efficient.....
I have 2 gas units in my house have been running for over 14 years.
1 runs off it's own Impeller so if power goes out I still have hot showers...
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
Depends on what you mean by "efficient". Electric tankless heaters are usually around 100% efficient.

Except there is more energy in a therm of gas than a kilowatt of electricity.

Out here in cali, where elec prices are through the roof and NG prices are cheap, its far more cost efficient to use natural gas for heating than elec.

I dont know about LPG, as its a bit more pricey than NG.
 
OP
J

jim1450

Active member
Joined
Jun 11, 2013
Messages
27
Location
Sandusky, OH
Except there is more energy in a therm of gas than a kilowatt of electricity.

Out here in cali, where elec prices are through the roof and NG prices are cheap, its far more cost efficient to use natural gas for heating than elec.

I dont know about LPG, as its a bit more pricey than NG.
A few winters ago propane was 2.5 times what it is now & was hard to get, I was running low & was worried about running out so I turned down the temp of my heat pump compressor lockout.
I own my own 500 gal tank, they normally will only put 400 gal in it but the min fill is 250, if I do 250 in the spring there's not enough room for another 250 until it gets cold & I start using it so the price goes up.
I figure with the heat pump & tankless water heater I can better manage my propane usage if I need to.
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
11,009
Location
Rhode Island
Except there is more energy in a therm of gas than a kilowatt of electricity.

Out here in cali, where elec prices are through the roof and NG prices are cheap, its far more cost efficient to use natural gas for heating than elec.

I dont know about LPG, as its a bit more pricey than NG.
Cost efficiency is a whole different thing than efficiency ;)
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA

dw1

Well-known member
Joined
Jan 26, 2015
Messages
1,335
Location
Ky
what is the temp rating on the wire?

I'll see if I can find it tomorrow (I don't throw anything away:dunno:), trying to stuff 2400 sq ft house items in 1500 sq ft barn, have to be out of house next weekend.
 
OP
J

jim1450

Active member
Joined
Jun 11, 2013
Messages
27
Location
Sandusky, OH
I don't understand some of the things manufacturers do.
Besides the water heater my Everlast 140 mig welder came with a 15 amp plug, #12 wire cord & instructions say to use a 30 amp breaker.
They said there's something in the NEC about welders & start up draw.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
I don't understand some of the things manufacturers do.
Besides the water heater my Everlast 140 mig welder came with a 15 amp plug, #12 wire cord & instructions say to use a 30 amp breaker.
They said there's something in the NEC about welders & start up draw.

Well welders are easy to explain.

Most of them have limited draw based on duty cycle.

Code allows reduced wire size based on that duty cycle.

http://www.ecmweb.com/qampa/code-qa-45
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Everlast likely uses a 12 due to many of the other machines in the lineup require it and they can take it off the same spool. Lincoln uses 14 on these, I think Miller and Hobart may too.
 
OP
J

jim1450

Active member
Joined
Jun 11, 2013
Messages
27
Location
Sandusky, OH
Looks like input amps is 19.5a
Instructions say use a 30 amp breaker.
1 of the reasons I bought it is the 25% duty cycle @ full power, most of the other units I looked @ were dual voltage but multiprocess & since I already have the 210 EXT I just went with the 120 volt 140
 

Attachments

  • screenshot-www.everlastgenerators.com-2017-09-19-21-41-21-652.jpg
    screenshot-www.everlastgenerators.com-2017-09-19-21-41-21-652.jpg
    46.3 KB · Views: 11

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
Instructions say use a 30 amp breaker.
1 of the reasons I bought it is the 25% duty cycle @ full power, most of the other units I looked @ were dual voltage but multiprocess & since I already have the 210 EXT I just went with the 120 volt 140

Thats due to the inrush current rating...
 
OP
J

jim1450

Active member
Joined
Jun 11, 2013
Messages
27
Location
Sandusky, OH
Thats due to the inrush current rating...

That's how it was explained to me but there's still a 20 amp circuit with a 30 amp breaker.
I bought a commercial 20 amp outlet & #10 wire
I guess my ***** is the way it's designed someone could have an older garage with #14 wire & stick a 30 amp breaker in the circuit because of the vague instructions.

I bet it'll run longer than 2 1/2 minutes @ 140 amps, from what I've heard Everlast will run longer than the advertised duty cycle.
 
Last edited:

59 wagon man

Well-known member
Joined
Oct 25, 2010
Messages
1,589
Location
hollywood fla
just so you are aware this heater is made by Niagara manufacturing in Miami. they make the titan brand tankless heater. if yo go to there shop you will see the rheem unit right next to the titan and they are almost identical except for the different color cover. by removing the cover you broke the seal probably and they are not usually warrantyable even if they were new. The instructions clearly state do not open cover. the whip is how they come,i've put in dozens of these and carry them on my truck all the time. very expensive way to heat water but since usually they don't run much it can still save you some money. usually the electrician will mount a junction box within the length of the whip and then we can connect them easily if you open the cover and change the whip as previously stated you void the warranty and make a changeout a pain
 
OP
J

jim1450

Active member
Joined
Jun 11, 2013
Messages
27
Location
Sandusky, OH
just so you are aware this heater is made by Niagara manufacturing in Miami. they make the titan brand tankless heater. if yo go to there shop you will see the rheem unit right next to the titan and they are almost identical except for the different color cover. by removing the cover you broke the seal probably and they are not usually warrantyable even if they were new. The instructions clearly state do not open cover. the whip is how they come,i've put in dozens of these and carry them on my truck all the time. very expensive way to heat water but since usually they don't run much it can still save you some money. usually the electrician will mount a junction box within the length of the whip and then we can connect them easily if you open the cover and change the whip as previously stated you void the warranty and make a changeout a pain
Mine is a few years out of warranty & I'm mounting it 4" from a subpanel so I'm not going to use 2 short pieces of romex.
When it dies I won't replace it with another Rheem ot Titan

The other units I've had say if being used with a tank style mount it before but I've mounted them after because the water is room temperature so it works less, I'm in north central OH & the unit probably isn't recommended for use here.

I'd like to hear their explanation of #10 Romex & 60 amp breaker
 
To avoid these ads, REGISTER NOW!
Top Bottom