What wire do I need to run subpanel to main panel?
bmsemple1
I want to add a 100 amp subpanel in my garage but I'm having trouble determining exactly which wire I need to run to the main panel. It will be approximately 75 feet away from the main panel. I thought I needed 2-2-2-4 but I've also read that I could use 3-3-3-5 copper SER cable. I've discovered that these wires are more expensive than I thought. Any tips on where to buy it? I've already called several local electrical supply places and I'm being quoted $500 or more.
pattenp
Virginia - USA
You can use 2-2-2-4 Al SER for 90A, 1-1-1-3 Al SER for 100A, or 3-3-3-5 Cu SER for 100A. SER installs like NM-b and needs protection if subject to physical damage.
wyliesdiesels
Modesto, CA
#2 al is good for 90a not 100a.
If you really need 100a then you will need #1 al or #3 cu.
But 75' of al ser shouldnt cost $500.
I will find some prices for u when i get home.
Norcal
The OP is specing copper conductors. Aluminum would be a good way to reduce costs.
wyliesdiesels
Modesto, CA
ok so #3 cu SER may be $500 but #2 al SER is no where near that price.
https://www.wireandcableyourway.com/2-3-4-ground-ser-aluminum-building-wire.html
80' for $110
If you want 100a:
https://www.wireandcableyourway.com/1-3-3-ground-ser-aluminum-building-wire.html
80' for $134
100A? Really?
Especially 240Vac....
Why?
huh? :headscrat :dunno:
bmsemple1
Thanks everyone. We are adding a 700 sq ft addition on top of our garage. I also want to make sure I have enough for workshop machines running like fans, heaters, welder, saw, etc. In the future there will be additions on the back of the garage and I want to make sure I have enough power to run another box. It might power a small living quarters and pool equipment someday.
wyliesdiesels
Modesto, CA
Well in that case i would start off with a load calc.
You dont want to out 100a in then discover down the road that you meed more.
Do it right the first time.
It boggles my mind how most dont do load calcs...
That should be the first step for someone that wants to add that much load in the future.
Planning planning planning!
6 Ps....