Turning a 120v run into 240v

Ironcrow

Well-known member
Joined
Sep 30, 2005
Messages
1,169
Location
Arizona
I have a 15A 120 volt receptacle I'd like to turn into a 15A 240 volt plug. The wire is stranded THWN run in EMC. White neutral, black hot, green ground. All kosher.

I have room in the panel for the 240 volt breaker. To avoid removing the neutral wire and re-pulling a red wire, can I tape the white wire red at both ends and re-purpose it? Code compliant?
 
To avoid these ads, REGISTER NOW!
OP
I

Ironcrow

Well-known member
Joined
Sep 30, 2005
Messages
1,169
Location
Arizona
I was afraid of that. I found conflicting claims in my web search (as is typical) but a couple of sources agreed on that "no". I guess it's a "save" for romex since you can't pull the wire and replace it. I can, so I should...

Sorry about fat ********* "EMT". Need to finish my coffee before typing.

Thanks!
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
Since it is in EMT just pull in a new conductor, but sometimes it's not as easy as it sounds.
 

davetulk

Well-known member
Joined
Feb 2, 2009
Messages
101
Location
Mid Florida
As long as your emt fill is ok I would leave the white in the pipe caped at the ends. Just pull the new red. incase you ever need to go back.
 

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
It is technically a code violation. Not a safety thing.

Of ZERO consequence if you are doing it on your own home. Your insurance doesnt care. When you sell the home you will need to 'disclose work done without a permit', which will include either 'pulled a new red wire and changed breaker and plug' -or- 'changed breaker and plug'.

IMO
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
Not being a professional is there allot of things in the NEC that are as arbitrary as this? Seems if safety is not the motivator it must be something else.

For smaller conductors it's a good rule, with 8 & 6 AWG I think it needs to go away.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,775
Location
NW Iowa
I think the intention of that code section is to prevent someone from pulling and re-identifying white wires in a new installation. It does technically apply to existing installations also, but I see very little safety issues with this as long as the wire is re-identified anywhere it is accessible ( J-boxes/ ect.).

I would not hesitate to re-color the wire you have unless the wire was extremely easy to replace.
 
OP
I

Ironcrow

Well-known member
Joined
Sep 30, 2005
Messages
1,169
Location
Arizona
I started to look at pulling a red wire, removed the cover from a conduit body adjacent to the panel, and discovered I had already pulled and extra red wire coiled it up and nutted it off in the conduit body. Ha! I love it when I think ahead, Even if I forgot I did it.

So, never mind...I just swap the wires and coil the white one up for later.:bounce:
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,590
Location
Fullerton, CA
When you sell the home you will need to 'disclose work done without a permit', which will include either 'pulled a new red wire and changed breaker and plug' -or- 'changed breaker and plug'.

The 'plug' isn't being changed. The 'outlet' or 'receptacle' is.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Seems there is a lot of this in the NEC
It isn't in there cause they didn't have anything better to do. There are millions of hours of combined forensics, incidents and fires for all that. I had a service call the other day, some little deal that wasn't code compliant caused the problem.
 