i would put the incomming feed through the left side.because of the short bend radius from the right side.also don't forget the ground.you also say 1/0.do you have a 150 plus feet run in or out?
here is why people leave a loop: Imagine how screwed you would be if your wire ended up an inch short...
the slack is also a good idea incase something has to be reterminated later.
Yes, 150 feet + out to the shop.
Tis makes sense, I'll try to leave a loop, but the outdoor box is kind of small and the 1/0 doesn't seem to bend very easy.
Thanks
The loop in most installs is a drip loop, such that if a small amount of rainwater comes down the feed line, it will reach the bottom of the loop and drip off harmlessly from there, rather than being wicked into the connections, corroding them and causing a hazard.
In your case, feeding from the bottom, I'd have no issue not using the loop, but would prefer to use one, so that if the line ever needed re-terminated in the future, you'd have a little slack to play with.
do the neutral and ground both attach to the ground bar in the breaker panel?
If this is a subpannel (fed off a breaker in your main panel) with a 4-wire feeder then the neutral and ground must be kept separate.
You may need to purchase a grounding buss bar to install below the existing neutral buss. (There are pre-drilled mouting holes in your panel.) The incoming ground wire in your feeder can connect to the ground lug at the bottom of the box or to the new grounding buss bar. The ground wire in your outgoing feed should connect to the grounding buss bar.
Out of curiosity, where is this box located? i.e. where the feeder enters your shop building?
What kind of earth ground do you have at your shop building? I.e. grounding rods and/or "UFER" ground attached to footing rebar?
OK, so it sounds like you are going to use a double-lug meter base to feed both your house as well this 100A disconnect feeding the detached shop building. Presumably, neutral and ground are tied together in your main house pannel.
So neutral and both hots will come from the meter to this disconnect. It seems then the question is where should the ground for the 100A disconnect panel originate? And should neutral and ground be bonded or kept separate in this disconnect panel?
Perhpas one of our NEC gurus can comment...