Removing An Outside/Exterior Outlet

D45

Well-known member
Joined
Mar 21, 2014
Messages
4,842
Location
NW INDIANA
I am resurfacing and doing some deck work.......and I have this dual duplex outlet box

It is falling apart and I really have no use for it, since there are other outlet boxes nearby

I want it gone like the wind

Can I just remove the outlets/wiring/vertical conduit and install a ground level/water tight junction box? Or whats the best way to get ride of it?


20170917_141617_zpsyl7hbtbl.jpg



20170917_151323_zpso5khs52y.jpg
 
To avoid these ads, REGISTER NOW!

Leaflessshadetree

Well-known member
Joined
Aug 1, 2013
Messages
7,197
Location
Don't ask.
Are there two separate circuits or does the second conduit continue the circuit to another box?

Myself I'd repair/replace it. Appears to be in a convenient location, (cords won't cross access to the deck) and I believe that you can never have too many outlets.
 
OP
D

D45

Well-known member
Joined
Mar 21, 2014
Messages
4,842
Location
NW INDIANA
There are two outlets (that you can see) on the outside wall of the deck.......only about 12 feet away. I never used any of these outlets anyways, but they are good to have for sure.

I thought about keeping it, but I am also removing the railing...........would just like to remove it all
 

zak77

Well-known member
Joined
Sep 18, 2014
Messages
1,359
Location
Monson, MA
Cap the wires that feed it in a junction box on the inside of the home and if it feeds another circuit, figure out another way to feed that circuit and once it's all disconnected, rip it out!!!
 
OP
D

D45

Well-known member
Joined
Mar 21, 2014
Messages
4,842
Location
NW INDIANA
Thanks, but I am hoping to just save time and install a ground level junction box, which will be hidden under the deck
 
Last edited:

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,336
Location
Alexandria, VA
Install a junction box close to ground level, but face it toward the vertical side of the deck. It should be easier to seal that way, and since the box faceplate ends up on the side of the deck it will still meet requirements for access to the electrical connections.

If it was mine I would use a waterproof receptacle cover instead of a plain faceplate, and include a duplex receptacle in the new box. You never know where you might need power.

Bruce
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,340
Location
Minneapolis
Does the existing wiring go in and then out of those two conduits, and does it need to remain connected to something downstream? If not you could just pull the wire out, take the conduits down below grade and abandon them. If you need to keep the wiring intact, I would go with a new box down lower, but not right on the ground - in reality, over time most ground level boxes will end up not being watertight. The box will have to remain accessible as well.
 

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
We had one like for a spot for the spa, the previous owner just cut it flush with the concrete and then patched cement over it, which took a while to find as I only had an idea where the conduit should end up.
I still have the conduit going into the concrete on the panel side, but the wires pulled out. I WISH they haven't done that, it will be very hard to restore the use now having that one end under concrete.. I would vote you just leave some conduit and leave a box there but no wires so it can still be restored later.
 
OP
D

D45

Well-known member
Joined
Mar 21, 2014
Messages
4,842
Location
NW INDIANA
Well upon further inspection, I have one line going from the house, in the plastic conduit, to the outlets.

Then the other vertical plastic conduit is buried and "I believe" going underground and supplying power to the outlets for the pool

So, While I do want the two outlets gone.........I do need to keep some wiring for the underground line to the pool.
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
Just do the j-box. You can go as low as any flooding would allow. There apparently is no provision in the NEC for minimum box height unless there is a body of water present, meaning a pond or river.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,204
Location
NJ
A jbox can not be concealed where removal of the structure is required to access it.

You could cut the existing 90 off of the horizontal conduit and dig out around the vertical conduit. Cut the vertical conduit so a 90 added onto it will be at the same height as the horizontal conduit. Connect the new 90 to the horizontal conduit. You will need a few couplings, pvc cement, and new wire. You can re-use the straight conduit pieces cut from the recept to piece back the horizontal run.

This assumes that doing this will not put you over 360 degrees between outlets.
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
I would keep it -- for $40 get a midwest metal box. Removing a proper exterior outlet is a crime against humanity in my book.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,179
Location
Modesto, CA
Well upon further inspection, I have one line going from the house, in the plastic conduit, to the outlets.

Then the other vertical plastic conduit is buried and "I believe" going underground and supplying power to the outlets for the pool

So, While I do want the two outlets gone.........I do need to keep some wiring for the underground line to the pool.

Typically pool outlets are fed off of the GFCI in the pool pump panel...

you should definitely trace this circuit before you do anything with it...
 

MikeF2316

Well-known member
Joined
Dec 29, 2012
Messages
9,605
Location
Thornhill, ON
I'd keep it too. It's in a great spot. Maybe you'll need to reposition it slightly. And since it appears to be "middle of the run" you're going to need some kind of box there that's accessible, so it might as well be functional.
 
OP
D

D45

Well-known member
Joined
Mar 21, 2014
Messages
4,842
Location
NW INDIANA
All the outlets around the pool are GFCI

I have more than enough outside outlets and want this one gone

This is obviously just outside, waterproof plastic conduit.......does it get glued together like PVC or is it just pushed together?

I am going to start taking it apart this coming weekend
 
To avoid these ads, REGISTER NOW!

CJ7VFR

Well-known member
Joined
Jan 13, 2015
Messages
2,942
Location
Central New Jersey
All the outlets around the pool are GFCI

I have more than enough outside outlets and want this one gone

This is obviously just outside, waterproof plastic conduit.......does it get glued together like PVC or is it just pushed together?

I am going to start taking it apart this coming weekend

If you are going to use PVC conduit, then you have to glue the pieces together just like you do any other PVC pipe and push on fittings.

If you didn't, it would not be water tight and differences in hot and cold temperatures could make hand fitted pieces come loose and fall apart.

Jim
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,736
Location
Long Island
... in reality, over time most ground level boxes will end up not being watertight...

THIS.

I would suggest that if you go with a ground level box, you use DB rated wire nuts for the splices in it. It will save you from future headaches when the box ends up wet inside.
 
OP
D

D45

Well-known member
Joined
Mar 21, 2014
Messages
4,842
Location
NW INDIANA

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
They also have a flexible one in 3/4" if you need to shoe horn it in there. But usually if the conduit is long enough there is enough play to do the splice.
 

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
DryConn is what I usually get but they are same. You don't direct bury line voltage wire nuts so it doesn't matter for that rating.

Make sure you read the package for how many wires you are capping together, the small size is probably useless for this job, they are for sprinkler 18 gauge wires.
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
Can you burry a line with them attached ???

I had to fix a feed to a post light one time -- it was an assembly that completely covered the cable and then was injected with sealant ... it had to be 8-10 inches long.
 
OP
D

D45

Well-known member
Joined
Mar 21, 2014
Messages
4,842
Location
NW INDIANA
I will not be burying the line or wiring

My plan is to remove the vertical lines and the outlets

I will get a waterproof box, that will not be buried either

The wiring will be spliced/connected together, inside the waterproof box, using the outside rated wire nuts

I will reinforce all connections and seals with silicon
 

Wirepuller

Banned
Joined
Oct 6, 2014
Messages
305
Use a PVC bender or heat dun and shape the conduit to secure under the deck somehow. Or cut the PVC change to a female adapter and use seal tite to do the same. I'm not a huge fan of boxes that close to the ground.


Sent from my iPhone using Tapatalk
 
OP
D

D45

Well-known member
Joined
Mar 21, 2014
Messages
4,842
Location
NW INDIANA
I was able to get the two outlets disconnected, the box removed and the two vertical pieces removed

There were a lot more wires inside than I though there would have been

Tomorrow I will shop around and see what I can find, regarding an outside waterproof j-box

I also need to find some 3/4" PVC bends and figure out an orientation on what will work


20171007_151954_zpsgb80nhgh.jpg



20171007_151954_zpsgb80nhgh.jpg



20171007_153609_zpsxrhmqakr.jpg



20171007_164137_zpsxkspzezc.jpg



20171007_164145_zpshfzguema.jpg
 
OP
D

D45

Well-known member
Joined
Mar 21, 2014
Messages
4,842
Location
NW INDIANA
I cut the one vertical pvc section close to the ground and used a balled 90 degree bend piece, and installed a liquid tite fitting on the end of the bend.........and glued the bend to the cut off stub

I then cut the long pvc run and installed another liquid tite fitting on the end

I mounted a small pvc box and connected both

I used some DryConn wire nuts on all the connections

The pvc box had a good rubber gasket, but I used some silicon on the lid and also around the fittings on each side of the box

Pleased how it looks and how it turned out, maybe $35 into this small project


20171008_154403_zpslib3qz6f.jpg



20171008_154406_zpscubdi3uv.jpg
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,179
Location
Modesto, CA
Liquid tight fittings are meant for liquid tight NOT PVC.

Shouldve used a male terminal adapter.

Also, will that j box be accessible with the deck in place?
 
OP
D

D45

Well-known member
Joined
Mar 21, 2014
Messages
4,842
Location
NW INDIANA
I use the words "liquid tite" loosely, I am not sure what they are specifically called

I told the parts guy at the electrical supply house what I was doing and he sold me the fittings with the 90 degree bend

Yes, of course it will be acceissible
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,179
Location
Modesto, CA
I use the words "liquid tite" loosely, I am not sure what they are specifically called

I told the parts guy at the electrical supply house what I was doing and he sold me the fittings with the 90 degree bend

Yes, of course it will be acceissible

Do they look like either of these?

rp6950.jpg


66fc35e5-a887-4509-ac26-2d94b7e4d322_1000.jpg


Shouldve used this:

11cc5600-c2bc-49ae-914d-1fb67adf3bb5_1000.jpg
 
OP
D

D45

Well-known member
Joined
Mar 21, 2014
Messages
4,842
Location
NW INDIANA
Definately not the top two fittings

Looks "close" to the bottom one, but mine has a rubber oring (for up against the j box) and a 'nut washer' for inside the box.....

Also, mine has threads like a screw, and the entire fittings is 'self tapping' and is screwed inside the conduit, with another rubber washer that seals up against the end of the conduit

I used silicon everywhere and have no doubts it is all water tight
 
Last edited: