Does a New Detached Garage Require Two Circuits?

jerlane

New member
Joined
Nov 2, 2017
Messages
2
We are building a two car 24x24 detached garage and I am GC'ing the build. An electrician is doing the work as a side job, so I pulled the permit.

The electrician that did the house work (just finished the house) ran a line from the circuit breaker to the outside of the house for the garage. He ran a single 20A 120v line. We're planning to run that to the garage underground through conduit.

I reached out to our inspector to try to avoid any mistakes and he said we need a circuit for the outlets and a separate circuit for the lights. Does this make sense? Both electricians I've talked to said one single 20A line should be fine.

The basement is already finished, so running a second line from the breaker will be a challenge.

Thanks in advance!
 
To avoid these ads, REGISTER NOW!

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,328
Location
Alexandria, VA
Maybe you didn't ask the inspector exactly the right question, or he misunderstood.

You do need switched lights inside, and outside next to the man door, and you do need a minimum number of GFCI receptacles (usually one per car bay). However, I believe they can all be on one circuit.

Bruce
 

BillK

Well-known member
Joined
Aug 24, 2006
Messages
9,368
Location
Beautiful Southern Maryland
I am just curious. Does the inspector understand that this is a DETACHED garage ?? I didn't think you had to have any electric to a detached garage.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,089
Location
Modesto, CA
Can NOT run 2 separate circuits to a detached building- code does not allow it.

If it were mine, i wouldve ran a feeder thats a lot larger than 20a especially since its brand new.

EDIT: damn phone left out a word.
 
Last edited:

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
A first time poster going cheap on the electrical with a supposed "electrician" that's side jobbing and he can't answer your simple questions???

Good luck.

You get what you pay for.
 

bruincounselor

Well-known member
Joined
Sep 12, 2015
Messages
84
Location
North Dakota
I put 200 amps in my smallish garage, and 19 outlets in the single size shop bay. 20amps will probably do the minimum to meet most local code requirements, buy why not have a little extra for future use?
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,636
Location
Northern Virginia
I build production homes in Montgomery County MD and one of our models has a detached garage about 15' from the house.

The bear bones wiring approach is a single 14/2 15A dedicated circuit run to detached garage where it terminates in a single gang box centered on the end wall of one of the two car bays. This box is fitted with a GFCI outlet which then feeds the exterior (jelly jar) and interior (2 keyless) lighting circuits, another outlet centered on the other car bay end wall, the single overhead plug for the 16' garage door opener, and one exterior outlet. So tripping this single GFCI kills the entire detached garage.

Not my choice on this method, cost derived minimum for a production home. Have built about 15 of these and not one customer wanted any garage power upgrades.
 

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
This box is fitted with a GFCI outlet which then feeds the exterior (jelly jar) and interior (2 keyless) lighting circuits, another outlet centered on the other car bay end wall, the single overhead plug for the 16' garage door opener, and one exterior outlet.

I've read different interpretations of the new "The branch circuit supplying this receptacle(s) shall not supply outlets outside of the garage" section. Is "outside of the garage" being interpreted as "not on the inside" or as "other than the garage"?

From 210.52(G) or thereabout.
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,636
Location
Northern Virginia
I've read different interpretations of the new "The branch circuit supplying this receptacle(s) shall not supply outlets outside of the garage" section. Is "outside of the garage" being interpreted as "not on the inside" or as "other than the garage"?

From 210.52(G) or thereabout.

Well in my case I’m assuming garage structure only. They all pass inspection this way which doesn’t mean much.
 

Leaflessshadetree

Well-known member
Joined
Aug 1, 2013
Messages
7,182
Location
Don't ask.
Required by who?
If it's mine it requires at least a 240V 20A feed (more Amps even better). It doesn't add much cost to do 240V and have 2 circuits in the garage so you don't have to kill power to the whole building when you need to do work.
 

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
Well in my case I’m assuming garage structure only. They all pass inspection this way which doesn’t mean much.

Actually it looks like they cleaned that up for 2017. Garage receptacle outlets may power outdoor outlets, but nothing else and it must be 20A. 2014 had the "outside the garage" wording.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
First mistake was running only a 120V 20A feed to the garage. At an absolute minimum I would have installed a 240V 30A feeder. If the inspector is in fact requiring the outlets and lights to be on separate circuits then you will need to install at least a 2 space subpanel to branch out the circuits and put the outlets on a 20A breaker and lights on a 15A breaker. You need to be mindful that both the lights and outlets will only have 20A to draw on. You should use LED lights to keep the amp draw for the lights to a minimum.
 
To avoid these ads, REGISTER NOW!

Bolson32

Well-known member
Joined
Dec 6, 2016
Messages
541
Location
Lake Elmo, MN
I build production homes in Montgomery County MD and one of our models has a detached garage about 15' from the house.

The bear bones wiring approach is a single 14/2 15A dedicated circuit run to detached garage where it terminates in a single gang box centered on the end wall of one of the two car bays. This box is fitted with a GFCI outlet which then feeds the exterior (jelly jar) and interior (2 keyless) lighting circuits, another outlet centered on the other car bay end wall, the single overhead plug for the 16' garage door opener, and one exterior outlet. So tripping this single GFCI kills the entire detached garage.

Not my choice on this method, cost derived minimum for a production home. Have built about 15 of these and not one customer wanted any garage power upgrades.

This makes my skin crawl.
 

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,600
Location
East Bay SFO
Not one customer is a GJ member.

As the professional electricians have already said, only one circuit is required and 2 are prohibited.

I'm afraid that for many people a garage is merely a storage unit conveniently located on the same property as their house.
How many of us can look around in their neighborhood and see most of the garages stuffed with old furniture and piles of cardboard boxes full of ****?
 
Last edited:

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
I am reviewing a garage build for my ACC:

1056 sqft
3 car garage
foundation, stick built, stucco, Sheetrock, tile roof

8 ft walls
One circuit, 12 can lights, 8 receptacles,

Makes my skin crawl....
 
OP
J

jerlane

New member
Joined
Nov 2, 2017
Messages
2
OP. it may depend where you are and what code cycle you are on. Why not tell us.

Minnesota, so it looks like we are on 2017. The electrician that did all the house work which included the rough in for the line to the garage said that the code changed or went into effect in July.

I appreciate everyone's comments and wish we could have gone deeper with the garage plans, but this was at the end of our whole house remodel and the budget was maxed out already. I'm not planning on doing any major work out there and will have a dedicated shop area in the basement. So, hopefully the single 20amp line will be adequate. I did get LED lights as suggested by another member here.

As I was typing this message the inspector called me back and was very nice. He said that since the rough in at the house was done prior to the code change, he would sign off on it. So it looks like I am good to go.

Thanks again for the insight. I'll likely be back here to get more info on other projects once it's up and running. Floor finish maybe???
 

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
Might I suggest you use a conduit that can handle a larger wire in the future????

Might cost you $40 more.


(That way of you or someone else ever needs more, at the least you arent re-digging.)
 

bepjrfan

Well-known member
Joined
Aug 14, 2015
Messages
170
Location
North Dakota
I am reviewing a garage build for my ACC:

1056 sqft
3 car garage
foundation, stick built, stucco, Sheetrock, tile roof

8 ft walls
One circuit, 12 can lights, 8 receptacles,

Makes my skin crawl....

That is nuts... I was thinking 6 outlets on a 20 amp circuit was going to be a bit much, much less 12 lights and 8 receptacles... What kinda can lights are getting put in?? Can't imagine there will be too much left over power to power the outlets...

When you run a circuit like this, do you run it through a gfci before the can lights or run the outlets on the backside of the lighting and have the GFCI after the lights in the circuit?
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,636
Location
Northern Virginia
As the professional electricians have already said, only one circuit is required and 2 are prohibited.

I'm afraid that for many people a garage is merely a storage unit conveniently located on the same property as their house.
How many of us can look around in their neighborhood and see most of the garages stuffed with old furniture and piles of cardboard boxes full of ****?

Yes this is it.

We GJ members are a dying breed. Sad
 

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
Yes this is it.

We GJ members are a dying breed. Sad

Not sure what you're referring to but the OP's inspector was apparently right. Two circuits are required under 2017 code. The lights may not be on the receptacle circuit. A MWBC would have met the requirement; it's technically one circuit so it can feed the garage without needing a panel.

As for what a residential garage is used for, what's so wrong with having a garage that you only park cars in? If you want a shop, you can build one or convert your garage into one (or convert it into anything else) but it's basically for parking cars in. Minimal electricity is all that's needed for that.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,061
Location
NJ
Not sure what you're referring to but the OP's inspector was apparently right. Two circuits are required under 2017 code. The lights may not be on the receptacle circuit. A MWBC would have met the requirement; it's technically one circuit so it can feed the garage without needing a panel.

As for what a residential garage is used for, what's so wrong with having a garage that you only park cars in? If you want a shop, you can build one or convert your garage into one (or convert it into anything else) but it's basically for parking cars in. Minimal electricity is all that's needed for that.

This is correct. NEC 2017 has a new requirement - 210.11(C)(4) that did not exist in the 2014 code.

Need at least one 120v 20a ckt for recept outlets in attached and detached garages with power. This circuit shall have no other outlets.

So that wording puts lighting on a separate ckt. Therefore, 2 minimum. A MWBC would be the minimum unless you go the sub-panel route.
 