I’m planning to install a Reznor natural gas garage heater with a dedicated circuit and I have a few questions. The on-line manual says the “full load amps” is 2.4. It also says the “Maximum Over Current Protection” is 15. It requires a minimum temperature rise rating of 60C. What it doesn’t say in the manual is the wire size and type. It says the minimum wire size will be listed on the unit, which I don’t have yet, but I want to start pulling wire to get a little ahead of the game.

My question is what size wire & breaker do I need? I’m guessing the Maximum Over Current Protection value dictates the breaker size. Is this correct? If so, would 14/2 with ground work for the wire?

The wire will be run from my breaker panel in the basement, through an adjoining wall between my garage & family room, and then terminating in the garage. Do I need any special wire since it will be run in the basement and out in the garage? Not sure if there is a moisture requirement for potentially damp environments.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
14 AWG wire is fine. On a phone so hard to comment further.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,995
Location
Modesto, CA
Since this is a gas heater, I cant imagine the manu. requiring a dedicated circuit for a 2.4a load.

Do you have a 15a lighting circuit that is lightly loaded?

#14 is the smallest building wire available and @ 60c temp rating, the ampacity is 15a...
 
To avoid these ads, REGISTER NOW!

mrramsey

Well-known member
Joined
Sep 23, 2016
Messages
261
Location
North East Ohio
I’m planning to install a Reznor natural gas garage heater with a dedicated circuit and I have a few questions. The on-line manual says the “full load amps” is 2.4. It also says the “Maximum Over Current Protection” is 15. It requires a minimum temperature rise rating of 60C. What it doesn’t say in the manual is the wire size and type. It says the minimum wire size will be listed on the unit, which I don’t have yet, but I want to start pulling wire to get a little ahead of the game.

My question is what size wire & breaker do I need? I’m guessing the Maximum Over Current Protection value dictates the breaker size. Is this correct? If so, would 14/2 with ground work for the wire?

The wire will be run from my breaker panel in the basement, through an adjoining wall between my garage & family room, and then terminating in the garage. Do I need any special wire since it will be run in the basement and out in the garage? Not sure if there is a moisture requirement for potentially damp environments.

15 amp breaker in the panel, 14/2 w ground for the wire. You will need to add a switch (standard single pole light switch) at the unit. If the wire in the garage is behind drywall romex is fine. If it is exposed run conduit. Here is mine just waiting for the heater. I ran a dedicated line for it because I will likely add an outlet for a new door opener.
 

Attachments

  • IMG_20171116_081740508.jpg
    IMG_20171116_081740508.jpg
    138.2 KB · Views: 51

BlackJackJim

Member
Joined
Oct 31, 2017
Messages
17
I’m planning to install a Reznor natural gas garage heater with a dedicated circuit and I have a few questions. The on-line manual says the “full load amps” is 2.4. It also says the “Maximum Over Current Protection” is 15. It requires a minimum temperature rise rating of 60C. What it doesn’t say in the manual is the wire size and type. It says the minimum wire size will be listed on the unit, which I don’t have yet, but I want to start pulling wire to get a little ahead of the game.

My question is what size wire & breaker do I need? I’m guessing the Maximum Over Current Protection value dictates the breaker size. Is this correct? If so, would 14/2 with ground work for the wire?

The wire will be run from my breaker panel in the basement, through an adjoining wall between my garage & family room, and then terminating in the garage. Do I need any special wire since it will be run in the basement and out in the garage? Not sure if there is a moisture requirement for potentially damp environments.

A 15A breaker is fine, as well as 14 AWG size conductors. You could argue that the cable involves a damp or wet space, and you would be safe using something like THWN in conduit. I like PVC conduit since it is simple to cut and use. Those are nice heaters and I have been thinking of getting one.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
A 15A breaker is fine, as well as 14 AWG size conductors. You could argue that the cable involves a damp or wet space, and you would be safe using something like THWN in conduit. I like PVC conduit since it is simple to cut and use. Those are nice heaters and I have been thinking of getting one.

A 15A overcurrent device is required since 15A is the maximum allowed although standard circuit breakers are available in 10A they are not stocked everywhere.
 