Air compressor issue - gfci tripping

JustinS

Well-known member
Joined
Jul 19, 2010
Messages
366
Location
Altoona, IA
I picked up an air compressor (1.6hp 20 gallon vtwin Sanborn) with a "bad" motor. I've disconnected the belt and powered the motor, the problem is that it spins up and then trips my gfci within 5 seconds.

Im not that great with electrical items. Tips on what i should start with first as far as testing goes?
 
To avoid these ads, REGISTER NOW!
OP
J

JustinS

Well-known member
Joined
Jul 19, 2010
Messages
366
Location
Altoona, IA
Why have an air compressor on a gfci?

Sent from my SM-G930V using Tapatalk

All of my garage outlets run through a gfci. Just the way the house was built.

I do need to add a 220 outlet so maybe ill add a dedicated 120 20 amp outlet as well.
 
Last edited:
To avoid these ads, REGISTER NOW!

jakemac

Well-known member
Joined
May 21, 2013
Messages
9,035
Location
New England
How old is the GFCI ?
I've had issues with the trip switch on GFCIs getting "tired" with age or exposure to humid conditions.
 
OP
J

JustinS

Well-known member
Joined
Jul 19, 2010
Messages
366
Location
Altoona, IA
How old is the GFCI ?
I've had issues with the trip switch on GFCIs getting "tired" with age or exposure to humid conditions.

I had to replace it last summer so its only 1 year old.

Im going to try a non gfci outlet and see what happens.
 

jakemac

Well-known member
Joined
May 21, 2013
Messages
9,035
Location
New England
Another issue could be the size of the wiring in the wall.
If it's a long run from the breaker box, sometimes 14ga might not be heavy enough for a compressor.

If the compressor can be moved, try plugging in to a 20a outlet close to the breaker box or sub-panel. Compressors work best with as short a run to a power source as possible. (a convenient outlet doesn't necessarily count)

I had a 1-1/2hp compressor that if I plugged it in on the far end of my shop, it would pop the breaker every time. If I plugged it in on the same circuit next to the sup-panel, no problem.
 
Last edited:

byoungblood

Well-known member
Joined
Apr 6, 2011
Messages
2,590
Location
Berryville, VA
GFCI outlets can be touchy on inductive/capacitive loads, ie., motors.

I just got rid of the one in my garage. There was one a short distance from the panel, and everything else in the garage was in series with it, so any time I'd turn on my drill press or band saw the silly thing would trip. By nature of the way my garage is laid out, plugging those tools directly into the GFCI wasn't an option since it was on the other side of the garage from them.
 