my house has an old murray panel less main breaker...i guess it was considered a budget panel back in the day...home built in 1965...i have asked a few electricians about this over the years..one old guy said he remembers them...
ok-so i have worked with it over the years i have lived here...no problem...my issue was with the grounding of service...i don't know if you will believe this but it was grounded to the aluminum siding only...:dunno:...i changed that out rite away to ground rods-seems interesting to me that way back when this was ok vs. today's code's.
anyone ever seen this type of setup before?
 
To avoid these ads, REGISTER NOW!

Stuff

Well-known member
Joined
Aug 31, 2013
Messages
572
Two different issues. GEC needs to go to ground and it was always the water pipe. For safety other metal likely to be energized needs to be bonded. Most of the time aluminum siding is ignored but some inspectors have been known to require it.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,013
Location
Modesto, CA
Are you sure there wasnt another GEC bond going to water pipe somewhere?

Metal siding would not be a proper electrode in any shape or form seeing as how its not in the earth.

But as said above, any metal structure that should NOT be energized SHOULD be bonded to neutral(main service panel only) or ground to prevent the metal from becoming energized.
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
Are you sure there wasnt another GEC bond going to water pipe somewhere?

Metal siding would not be a proper electrode in any shape or form seeing as how its not in the earth.

But as said above, any metal structure that should NOT be energized SHOULD be bonded to neutral(main service panel only) or ground to prevent the metal from becoming energized.
That would be my guess also.
 
To avoid these ads, REGISTER NOW!
OP
B

bobbyjean

Well-known member
Joined
Aug 25, 2017
Messages
319
Location
hudson valley n.y.
well...i traced the ground wire from panel to a clamp at the bottom of siding...i would guess that a ground rod may have been installed , could not locate the wire/rod...only found clamp...wire size at clamp was large so i guess they junctioned at that point
 

Stuff

Well-known member
Joined
Aug 31, 2013
Messages
572
Check at the meter box. Sometimes GEC attached there.
 