1.25 conduit

tedo2007

Well-known member
Joined
May 19, 2014
Messages
104
Looking to run power to my garage, have a 1.25 inch conduit ran, i already installed a 100 amp panel in the garage (can change the main breaker easily)

can i run 2-2-2-4 mobile home feeder through the 1.25 conduit? This is what the city inspector is suggesting and said he would sign off on it (its over fill limit for 1.25 conduit) but im just not sure how easily it will fit.

I have 25 feet to go, through an lb and a 90 on the house, and lb and 90 on the garage.

Thanks!
 
To avoid these ads, REGISTER NOW!

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
I'd just run individual conductors. 25 feet isn't enough $ to worry about, no hassles down the road if in an infinitesimally chance event an inspector fails you during a home inspection.
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
The 2-2-2-4 is going to be a bear getting it to bend through a 1.25 LB. 2-2-4-6 will be slightly easier. You should consider copper thhn/thwn so to use a smaller gauge for the same capacity.
 

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
A home inspector is never going to see that nor comment on it, lol. As patent said, I think it's going to be a tough pull though.
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,004
Location
NJ
The 2-2-2-4 is going to be a bear getting it to bend through a 1.25 LB. 2-2-4-6 will be slightly easier. You should consider copper thhn/thwn so to use a smaller gauge for the same capacity.

If he chooses 3-3-4-8 Cu THWN conductors the fill is cut in half and he gets the full 100A panel rating as well. Not much extra $ for 25'.
 
Last edited:

Crazyjake8493

Well-known member
Joined
Sep 26, 2014
Messages
3,974
Location
Upstate NY
2-2-2-4 MHF should make it through 1.25" but it'll be snug. I ran mine through 45' of 1.5" with two elbows without a problem. 2-2-4-6 would be a bit easier. I'd be absolutely sure he'd sign off on first though.

For 25 feet the extra cost of copper THHN wouldn't break the bank, I'd probably go that route. Easier to work with too.
 