GFI, can it get weak?
JimVonBaden
Northern Virginia
The GFI in my garage seems to have gotten weak, or I am drawing more power than I used to. If I plug in my 1500 watt oil heater it will pop the circuit breaker. I run lots of other high draw items, like a 110V MIG welder, plus a fan and never an issue. Same with my other power tools and at the same times as my infrared heater, but with nothing else on the oil heater pope the GFI. It is possible the heater is going bad as it is old.
What do you think?
KenC
oklahoma
If it's only that one thing that pops it, it probably has a leak to ground. Bad insulation intermally, cracked element etc.
As you probably know, a GFCI does not trip due to current draw, only an imbalance of current on the 'hot' wire and neutral.
Bert_
NW Iowa
Glad you pointed this out. So many people think that a gfci will trip if you draw over 15, or 20, amps. It doesn't you could draw 50a through one and the GFCI won't trip. Hopefully the breaker in the panel would though.
A GFCI measures current going out, and current coming back. If there is a difference of more than 5 mA it will trip.
GFCI's do seem to get "weak" sometimes. But if you plug the heater into another GFCI and it still trips then the problem is definitely the heater
JimRB
East of Atlanta in the country.
I had a 20 amp GFCI breaker in the panel box protecting 12 gauge wire. The garage door opener would cause it to pop. I took the GFCI breaker out and put in a regular old 20 amp QO breaker and the problem went away. I did install a GFCI outlet in the garage that the door opener is not plugged into.
fastjohnny
SW Michigan
My block heaters in my diesel trucks do not play nice with GFCI's...I think it is the resistance heating elements...
AntonLargiader
Charlottesville, VA
Wow, block heaters are an area where I would definitely want a GFCI. I have never had a problem with my Zerostart coolant heater. I realize it's not quite the same thing as a freeze plug type, but leakage current is leakage current and I don't think you should want it in any type of heater.
J
JimVonBaden
Northern Virginia
I tried it on three different outlets, and on 600, 900 and 1500 watt settings. I suspect it is the heater. My other heater doesn't kick the breaker, but it is a different kind.
Thanks for the info.
Crazyjake8493
Upstate NY
Is it tripping the circuit breaker or the GFCI outlet? Two entirely different scenarios.