raferguson
Well-known member
In my new shop, I had them pull in a 100 amp 240V subpanel, as well as wire two 240V outlets, 8 ga wire, on 50 amp breakers. (one circuit for the compressor, one for the welder). As I read the code, I could have gone to a 55 amp breaker, but the contractor would not go bigger on the breaker, since the outlet was a 50 amp outlet.
I know that welders have a special section in the NEC, and that it is possible to use smaller wire for a larger breaker, than would be permitted in other applications. As I understand it, this is based on the duty cycle of the welder.
1. Given the 8 ga wire, and the 50 amp outlet, how large a breaker would be reasonable? The primary load would be a Syncrowave 200 welder. It can put out 200 amps, but is rated at 150 amps at 40% duty cycle. The rated input current at 150 amps is around 50 amps at 230V, depending on TIG vs stick, and AC vs DC. I have been living with a 50 amp breaker without difficulty, but this is a new shop with a new breaker, so I don't know if I am going to trip it or not. I suppose that the short answer is that I should not change the breaker unless needed. I would label the outlet as "Welder only," if I were to increase the breaker size. My guess is that I could go up to a 60 amp breaker without being crazy. Going up a wire size would not be a huge deal, since the run is about 6 feet in 1/2 inch conduit.
2. My dream welder is a Syncrowave 250, which is rated for 250 amps at 40% duty cycle, and up to 310 amps output. I would probably hard wire it in on its own circuit. The spec sheet says 250 amps out requires 96 amps in at 230 volts. Presumably I would install a 100 amp breaker for such a welder, although I am unsure what wire size would be appropriate. Even on a 100 amp circuit, I might trip the breaker at full power. Thoughts? I might end up with a welder similar to the Syncrowave 250, if I get a good deal on craigslist. I could use more power for the rare times that I weld thicker aluminum. Whether I need it or not is a separate question. ;-)
Conveniently, the new subpanel has lots of room for additional circuits. I will be adding a 30 amp 240/120 RV outlet, using a 30 amp breaker left over from the subpanel project.
Thanks,
Richard
I know that welders have a special section in the NEC, and that it is possible to use smaller wire for a larger breaker, than would be permitted in other applications. As I understand it, this is based on the duty cycle of the welder.
1. Given the 8 ga wire, and the 50 amp outlet, how large a breaker would be reasonable? The primary load would be a Syncrowave 200 welder. It can put out 200 amps, but is rated at 150 amps at 40% duty cycle. The rated input current at 150 amps is around 50 amps at 230V, depending on TIG vs stick, and AC vs DC. I have been living with a 50 amp breaker without difficulty, but this is a new shop with a new breaker, so I don't know if I am going to trip it or not. I suppose that the short answer is that I should not change the breaker unless needed. I would label the outlet as "Welder only," if I were to increase the breaker size. My guess is that I could go up to a 60 amp breaker without being crazy. Going up a wire size would not be a huge deal, since the run is about 6 feet in 1/2 inch conduit.
2. My dream welder is a Syncrowave 250, which is rated for 250 amps at 40% duty cycle, and up to 310 amps output. I would probably hard wire it in on its own circuit. The spec sheet says 250 amps out requires 96 amps in at 230 volts. Presumably I would install a 100 amp breaker for such a welder, although I am unsure what wire size would be appropriate. Even on a 100 amp circuit, I might trip the breaker at full power. Thoughts? I might end up with a welder similar to the Syncrowave 250, if I get a good deal on craigslist. I could use more power for the rare times that I weld thicker aluminum. Whether I need it or not is a separate question. ;-)
Conveniently, the new subpanel has lots of room for additional circuits. I will be adding a 30 amp 240/120 RV outlet, using a 30 amp breaker left over from the subpanel project.
Thanks,
Richard