Using a central ac blower as a fan, wiring info needed.

BLACK DEATH

Well-known member
Joined
Oct 16, 2011
Messages
572
Location
CC texas
I have a few central ac unit blower motors that I bought as I’ve seen a lot of people use them as fans in their garages or just to blow air when needed.
I have two 120 and one 240 or whatever the voltage is.
It has on the tag, hi, low medium with different color code for each wire.
How can I wire this up on a switch or switches so I can use each speed it has as I don’t need it to be on hi all the time or low all the time.
I know you may need a pic of the actual unit or tag it has but then maybe a few of you have already done this.

Pics are below of what I am referring to, if the links worked
https://goo.gl/images/sc5vNe

https://images.google.com/imgres?im...lyniy2g_ZvM:&vet=1&w=640&h=480&source=sh/x/im
 
To avoid these ads, REGISTER NOW!
OP
B

BLACK DEATH

Well-known member
Joined
Oct 16, 2011
Messages
572
Location
CC texas
Which one of them rotary switches? I see so many different ones but which one will not burn out
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
4sq metal box with a commercial switch cover.
Wire the neutral from an old extension cord to white wire from motor inside box.
Then wire the black wire from the cord to common side of 3way switch.
Then hook black wire from motor to one of the travelers on 3 way.
Hook red wire from motor to other side of 3 way.
Now you have a low and high speed to choose from when ever you plug it in.
You could also add a 2nd switch for on and off in the box if you want.
 

ABSTIFFGS

Well-known member
Joined
Feb 4, 2014
Messages
304
Location
Twin Cities, MN
4sq metal box with a commercial switch cover.
Wire the neutral from an old extension cord to white wire from motor inside box.
Then wire the black wire from the cord to common side of 3way switch.
Then hook black wire from motor to one of the travelers on 3 way.
Hook red wire from motor to other side of 3 way.
Now you have a low and high speed to choose from when ever you plug it in.
You could also add a 2nd switch for on and off in the box if you want.
That is a really neat idea. I have an old squirrel cage fan I've turned into a floor fan. I've only hot high speed now. I'm going out to the garage to look at this.

EDIT this worked perfectly! I had a white which obviously is neutral, black-super mega high speed, yellow- slightly lower, blue- slightly lower yet, and red- super low speed. I wired a single pole switch first then to the common of a 3-way as described, I used the black and the blue. Thanks for posting this info Zmax.
 
Last edited:

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
That is a really neat idea. I have an old squirrel cage fan I've turned into a floor fan. I've only hot high speed now. I'm going out to the garage to look at this.

EDIT this worked perfectly! I had a white which obviously is neutral, black-super mega high speed, yellow- slightly lower, blue- slightly lower yet, and red- super low speed. I wired a single pole switch first then to the common of a 3-way as described, I used the black and the blue. Thanks for posting this info Zmax.
Da nada.:beer:
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,717
Location
NW Iowa
You will probably need to block off part of the outlet on that fan. They are designed to work with some restriction like a ducted system and furnace filters. The motor will usually be overloaded without any restriction.

Check the motor nameplate for FLA, then use a amp meter to check the running current.
 

KenC

Well-known member
Joined
Dec 20, 2009
Messages
2,578
You will probably need to block off part of the outlet on that fan. They are designed to work with some restriction like a ducted system and furnace filters. The motor will usually be overloaded without any restriction.

Check the motor nameplate for FLA, then use a amp meter to check the running current.

Yep, nearly burned one up when I built my first one. Left it on for a while then notices a 'hot' smell. Checked the draw and it was way over spec. I throttled the inlet by using furnace filters. Killed two birds, one stone, filtered sanding dust out of the air and dropped the amps to the correct level.
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
You will probably need to block off part of the outlet on that fan. They are designed to work with some restriction like a ducted system and furnace filters. The motor will usually be overloaded without any restriction.

Check the motor nameplate for FLA, then use a amp meter to check the running current.

^^This^^ A small piece of sheet metal zip screwed or pop riveted to the lower part of the outlet (closest to the round part of the housing) should do it. Put it on with duct tape until you find the sweet spot with your ammeter.

Tommy
 
OP
B

BLACK DEATH

Well-known member
Joined
Oct 16, 2011
Messages
572
Location
CC texas
What if you dont run it on it’s highest speed, do you still need to restrict the flow?
One of them has a 2” plate already
The switch you all speak of is it like a 3 way light switch?
 
To avoid these ads, REGISTER NOW!

ABSTIFFGS

Well-known member
Joined
Feb 4, 2014
Messages
304
Location
Twin Cities, MN
Yes, this is how mine turned out. Worked perfectly. I played with the 4 different colors to get the 2 speeds I wanted.
790kHo

Edit- I think if you click on the little icon it will bring pic up. I haven’t fully figured out Flickr yet. Damn you photobucket!
 
Last edited:
OP
B

BLACK DEATH

Well-known member
Joined
Oct 16, 2011
Messages
572
Location
CC texas
Now I see the pic and understand.
So you can only utilize 2 speeds then?
Or add another switchand have all 4 speeds?
 

marinusdees

Well-known member
Joined
Oct 30, 2012
Messages
1,325
Location
Edgewood, Washington
You will probably need to block off part of the outlet on that fan. They are designed to work with some restriction like a ducted system and furnace filters. The motor will usually be overloaded without any restriction.

Check the motor nameplate for FLA, then use a amp meter to check the running current.

Typically, the motor will have overload protection (read, circuit breaker) and if unrestricted, will trip the Klixon. When the Klixon cools off, it will reset and the fan will restart.
 

Brian_WK

Well-known member
Joined
Jun 30, 2015
Messages
1,177
Location
NE South Dakota
This rotary switch will work AMAZON LINK
Pos. 0, all terminals open.
Pos. 1, connects T-1 to T-2 only
Pos. 2, connects T-3 to T-4 only
Pos. 3, connects T-5 to T-6 only
Run the hot wire to T-1 and jumper T- 1, 3, & 5 together. Terminals 2, 4, and 6 independently go to the 3 speeds. Run the neutral on the fan to the neutral on the cord.

Brian
 

Milton Shaw

Well-known member
Joined
Feb 11, 2011
Messages
4,837
A lot of those motors also had a run/start capacitor for whatever reason. Don't forget to leave these wired in. I used one of these fans to make a downdraft dust collector used 3 20x20 x2 inch pleated filter and made the top out of 1x2 hard maple strips with 1 by spacers to create air flow. Works really well for projects that will fit on it.
 