If I read the code right, I need to put a support between my light fixtures on the tin ceiling (mounted flat on tin) about 4 feet between each fixture end to end. Is this correct?
They allow 10 feet before a support is needed for straight run.

Thanks!
David
 
To avoid these ads, REGISTER NOW!
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,584
Location
Fullerton, CA
It's got to be within 3' of any termination, and not over 10' between supports.
A conduit body qualifies as a termination as does a box or panel.

The distance can be increased to 5' in cases where there isn't any possible way it can be supported 3' or less.
 

cory58

Well-known member
Joined
Dec 23, 2015
Messages
234
Location
Charlotte, NC
A conduit body qualifies as a termination as does a box or panel.
.


Thanks aen! Just ran a circuit using a couple of conduit bodies to make sharp turns. Didn’t think of them as termination points because the wires just pass through them
Instead of being spliced in the conduit bodies.