dobies vs plastic chairs vs slab bolsters

foodie

Well-known member
Joined
Mar 16, 2018
Messages
1,342
Location
Michigan
Hi everyone, in regard to my garage floor. Yes I am going to place rebar. But what is your opinion on dobies vs pastic chairs vs slab bolsters. I have read the dobies are better. However the plastic chairs and slab bolsters allow for "holes" in the mix when poured, thus allowing a possibility of water penetration between the outline of the chairs or bolsters. Another engineering article stated the plastic chairs are better for contraction and expansion because plastic has the same properties as cement/concrete. Your opinions are greatly appreciated. Thank you in advance.
 
To avoid these ads, REGISTER NOW!

ConCretin

Well-known member
Joined
Jan 20, 2011
Messages
3,379
Location
Central Maine
Hey foodie. You are venturing into into the area of overthinking this thing. Any of the supports you mention are just fine. Just make sure the height is right to hold the bar in the middle third of the slab. Also, if you have a vapor barrier, you want a support with won’t poke through.
 
Last edited:

wgasa84

Active member
Joined
Jul 24, 2014
Messages
30
Location
Valley Center, CA
Hi everyone, in regard to my garage floor. Yes I am going to place rebar. But what is your opinion on dobies vs pastic chairs vs slab bolsters. I have read the dobies are better. However the plastic chairs and slab bolsters allow for "holes" in the mix when poured, thus allowing a possibility of water penetration between the outline of the chairs or bolsters. Another engineering article stated the plastic chairs are better for contraction and expansion because plastic has the same properties as cement/concrete. Your opinions are greatly appreciated. Thank you in advance.
No difference in what you're doing. We use dobie's in all of our pours flatwork.

Sent from my SM-G955U using Tapatalk
 
OP
F

foodie

Well-known member
Joined
Mar 16, 2018
Messages
1,342
Location
Michigan
Thanks so much to all of you guys for your time and response. Yes I will definitely have a vapor barrier.
LLWillysfan,...you are so right!! I do over think everything,...but there is only one chance to do it right. And that is exactly what I was thinking in terms of what is less of a hassle so the contractor staff doesn't poke a hole in the vapor barrier and tip over the bar supports, despite the fact that they will be wired to the rebar. Have a great day everyone.
 

tapered-pin

Well-known member
Joined
Sep 12, 2017
Messages
277
Location
Alpharetta, GA
hold the bar in the middle third of the slab

you mean the area that sees essentially no tension or compression?
bending_stress_beam_compression_tension.png


reinforcing bar should always be in the lower 1/3 with no less than 1" of concrete all around it (preferably 2-3")
 

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,741
Location
SE Michigan
I used Pro-Lok chairs, 2" tall in a 6" slab, for rebars 16" oc. Design for heavy machine-shop machinery and forklift rigging of same. Nothing but good to say about them, it definitely speeds up forming the grid. It looks like a weak thing but the bars snap in place quite well, as I recall I only lost 1 chair to splitting apart on the top. Home Depot had some of them but seemed like they were selling out/phasing out, my local lumberyard special ordered them for me. It seems like dobies are more of a west-coast thingy. I would have probably used those if I could have found them locally. The end result (of the wire-tied grid) was that it was solid and no person could have knocked it out of place, it was easy to walk over and not get "stuck". However it did require the pump truck for placement.

http://www.grip-rite.com/us/en/products/concrete-construction-products/prolok
 
Last edited:

ConCretin

Well-known member
Joined
Jan 20, 2011
Messages
3,379
Location
Central Maine
you mean the area that sees essentially no tension or compression?
bending_stress_beam_compression_tension.png


reinforcing bar should always be in the lower 1/3 with no less than 1" of concrete all around it (preferably 2-3")

You would be correct if we were talking about structural elements but we are talking about relatively thin, non-structural slabs on grade.

To start with, 1” of cover is not adequate for surfaces exposed to soil but even if you go with that, the middle third of a 4" slab starts 1.33” above sub grade so your example essentially locates the reinforcing in the middle third just as I suggest.

Secondly, a typical slab on grade is not thick enough to take advantage of the compressive strength of the concrete and the tensile strength of the rebar and act like a beam. It simply bends and cracks when loads are applied unless supported by the soils below.

Even if you question this, most structural cracks occur at the perimeter of the slab, where the top of the slab is in tension. Putting the rebar in the bottom does you no good here either.

Steel reinforcing in a slab on grade simply prevents cracks from opening up and displacing vertically. Rebar adds minimally to the slab's load bearing capacity until you get into much thicker sections.
 
Last edited:

tapered-pin

Well-known member
Joined
Sep 12, 2017
Messages
277
Location
Alpharetta, GA
Steel reinforcing in a slab on grade simply prevents cracks from opening up and displacing vertically. Rebar adds minimally to the slab's load bearing capacity until you get into much thicker sections.
then why use something as expensive as rebar when WWF sheets would suffice at a fraction of the cost.
 

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado
You are venturing into into the area of overthinking this thing.

I'd respectfully disagree.

Voids in the concrete make the concrete weaker. Concrete will bond much better to concrete than it will to plastic.

Additionally, when the guys pouring the concrete walk all over the supports, the concrete dobies won't shatter and break like the plastic ones will. In this same vane, use 6 x 6-W2.9 x W2.9 welded wire mesh sheets (not rolls). It will spring back into place after it has been walked on. It's heavier than the 10 ga wire most of the big box stores use.

Therefore the concrete dobies are better than plastic chairs. Any support is better than no support, but why not use the best.

attachment.php


attachment.php
 

Attachments

  • Dobie 002.jpg
    Dobie 002.jpg
    152.9 KB · Views: 327
  • Dobie 000.jpg
    Dobie 000.jpg
    97 KB · Views: 327
Last edited:

ConCretin

Well-known member
Joined
Jan 20, 2011
Messages
3,379
Location
Central Maine
then why use something as expensive as rebar when WWF sheets would suffice at a fraction of the cost.

I use rebar because it is more rigid and easier to support than wire. I think a lot of people use it with the mistaken understanding that they are getting a stronger floor.

Millions of square feet of commercial floor are placed every year with no steel reinforcing.
 

ConCretin

Well-known member
Joined
Jan 20, 2011
Messages
3,379
Location
Central Maine
Therefore the concrete dobies are better than plastic chairs. Any support is better than no support, but why not use the best.

You might be right lakeroadster but I've been doing commercial/industrial concrete up here for 30 years and have never laid eyes on one. There are all kinds of ways to support to support reinforcing and I doubt anyone could tell the difference in the first 100 years or so. Might have to track down a pallet of them though and give em a try. :beer:
 

ConCretin

Well-known member
Joined
Jan 20, 2011
Messages
3,379
Location
Central Maine
Alright lakeroadster, ya talked me into it. Called my main supply house yesterday. Said they'd never sold any but could get concrete dobies. Ordered a pallet to try. You're never too old for a good idea.
 
To avoid these ads, REGISTER NOW!

Tejay

Well-known member
Joined
Dec 29, 2014
Messages
105
I usually just buy 2” thick ashlars, wack them with a hammer to break up into smaller pieces and place under the rebar as the pour is going along. That way the rebar is flat on the ground and wheelbarrows can roll right over. Many times supply yards will have a bunch of broken ashlars that they will just throw in as freebies
 

audioworks04

Well-known member
Joined
Oct 6, 2015
Messages
141
Location
Olathe KS
I used Lotel Mesh-Ups in my slab, supporting 6-gauge wire mesh sheets.



Mesh ups are the best thing to happen in flat work chairs. They can be walked on and not break and spring back up. Plastic castle chairs are a close second. Dobies cause voids due to a large piece of different material embedded in the mix. Any chairs with metal runners can allow moisture to work it’s way up to the reinforcing and cause it to rust.
But in the end anything that keeps the reinforcing up in the slab is better than it on the ground.


Sent from my iPhone using Tapatalk
 
OP
F

foodie

Well-known member
Joined
Mar 16, 2018
Messages
1,342
Location
Michigan
Wow guys you are All amazing! Thanks so much for the discussion and responses. Audioworks 04, the Lotel mesh do look awesome, I just watched a video on them.
Matt i the pro lock chairs look great also. However, I just read an article from Molenaar North America, scientifically speaking they state that plastic spacers have a coefficient of friction 10 to 15 Times that of concrete. Plastic continues to expand and contract at higher temperatures. Dobies concrete spacers are the same material as the poured concrete so thermal contraction and expansion on are the same. This theory supports what Lakeroadster was stating. Who knew all of this goes into pouring a slab of concrete, wow.
The Molenaar company was describing their system of MoClips. These plastic spacers are placed at the top of the spacer and does not come in contact with the concrete . So essentially these are concrete dobies with a plastic clip on top. The plastic in the MoClip is only used for easily attaching the reinforcement, thus leaving the concrete part to do the work as the spacer. I have no idea if they work, but it certainly brings in the best of both worlds, easy of use and a dobie.
 
OP
F

foodie

Well-known member
Joined
Mar 16, 2018
Messages
1,342
Location
Michigan
Mesh ups are the best thing to happen in flat work chairs. They can be walked on and not break and spring back up. Plastic castle chairs are a close second. Dobies cause voids due to a large piece of different material embedded in the mix. Any chairs with metal runners can allow moisture to work it’s way up to the reinforcing and cause it to rust.
But in the end anything that keeps the reinforcing up in the slab is better than it on the ground.


Sent from my iPhone using Tapatalk
I have also read that everything you are stating is exactly true regarding the metal runners. But as a matter of discussion don’t the plastic chairs cause voids also. I don’t know I am just asking because as a matter of information to me and use of the best products. I would suppose it depends on what the dobies are truly made out of. Do you have any experience using the rebar-ups?... I saw those on the website also.
 

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado
I have also read that everything you are stating is exactly true regarding the metal runners. But as a matter of discussion don’t the plastic chairs cause voids also. I don’t know I am just asking because as a matter of information to me and use of the best products. I would suppose it depends on what the dobies are truly made out of. Do you have any experience using the rebar-ups?... I saw those on the website also.

Very astute observation foodie. Yes, any plastic style chair does create a void. As far as the concrete is concerned, each plastic support creates multiple stress risers.

However the concrete dobies adhere to the concrete, much like bricks adhere to mortar.

Technical data on dobies here>>>> http://daytonsuperior.com/docs/defa...e-dobie-tech-data-sheet.pdf?sfvrsn=416fb260_4

And Bar Support Handbook here >>> http://daytonsuperior.com/docs/default-source/handbooks/bar-support-handbook.pdf?sfvrsn=6dffd560_42
 
Last edited:
OP
F

foodie

Well-known member
Joined
Mar 16, 2018
Messages
1,342
Location
Michigan
Very astute observation foodie. Yes, any plastic style chair does create a void. As far as the concrete is concerned, each plastic support creates multiple stress risers.

However the concrete dobies adhere to the concrete, much like bricks adhere to mortar.

Technical data on dobies here>>>> http://daytonsuperior.com/docs/defa...e-dobie-tech-data-sheet.pdf?sfvrsn=416fb260_4

And Bar Support Handbook here >>> http://daytonsuperior.com/docs/default-source/handbooks/bar-support-handbook.pdf?sfvrsn=6dffd560_42


Thanks so much lakeroadster! Yes, that makes sense how bricks adhere to mortar!! I will read the technical data. Thanks for the links and your time.
 
OP
F

foodie

Well-known member
Joined
Mar 16, 2018
Messages
1,342
Location
Michigan
So if they pour a 5 inch floor, how far down are the dobies/rebar supposed to be?
At 2 1/2 inches? Half the thickness of the slab?
 

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado
So if they pour a 5 inch floor, how far down are the dobies/rebar supposed to be?
At 2 1/2 inches? Half the thickness of the slab?

2-1/2" would be fine. You want it within the middle 1/3 of slab but with 2" of cover.

From LLWillysfan https://www.garagejournal.com/forum/newreply.php?do=newreply&p=7002912

Rebar or mesh should be positioned in the middle third of the slab and must be able to stand up to finishers walking all over it.

Which agrees with: http://www.concreteconstruction.net/_view-object?id=00000153-8bb4-dbf3-a177-9fbd50fe0000.

"Some authorities recommend placing the steel 2 inches below the top surface of the slab. Others recommend placing the steel one-third of the depth down from the top of the slab."
 
Last edited:
Joined
Apr 4, 2013
Messages
5
with using regular 2 inch dobie bricks it can put your rebar to high up if your grade isnt spot on and might poke threw the surface which is bad. if your using using #4 rebar that put the top of your rebar at approximately 3 inches. if your doing a 5 inch thick floor you can get away with 2 inch dobies. if your floor is under 5 inches thick you can use concrete patio paver bricks. they"re 1 to 1.5 inches thick and can also get them at the local menards.
one bad thing with having rebar within a inch of the surface is the rebar can get rusty and pop the surface off after enough winters.
 
OP
F

foodie

Well-known member
Joined
Mar 16, 2018
Messages
1,342
Location
Michigan
Ok so maybe a 6 inch floor is better in order to compensate for the dobies height? However, lakeroadster with the different heights available which one would you choose if doing a 5 inch floor? The engineer I hired for his specs recommended 6 inches of base with a minumin 4 inch floor in his written report. But in my discussion with him he stated a 5 or 6 inch floor. Now I am really torn. Any thoughts?.
 

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado
Ok so maybe a 6 inch floor is better in order to compensate for the dobies height? However, lakeroadster with the different heights available which one would you choose if doing a 5 inch floor? The engineer I hired for his specs recommended 6 inches of base with a minumin 4 inch floor in his written report. But in my discussion with him he stated a 5 or 6 inch floor. Now I am really torn. Any thoughts?.

It really depends on what you will be using the slab for. Passenger cars, diesel work trucks, tractors, construction equipment or ?

I have a Rotary SPOA10 lift attached to the slab using epoxied 3/4" studs that specified 5.10" concrete thickness. So I used 5-1/2" thick - 4,000 PSI concrete, Angel Hair Mesh and Welded Wire Mesh 6 x 6 - W2.9 x W2.9 on 2" dobies in the bay where the lift is and 5" thick in the vehicle storage area.
 
OP
F

foodie

Well-known member
Joined
Mar 16, 2018
Messages
1,342
Location
Michigan
Thanks lakesroadster that gives me an idea of what to ask for. I have printed all the responses and will compile them.
 

mygarageone

Well-known member
Joined
Oct 16, 2013
Messages
2,691
Location
Munising , Mich
I use rebar because it is more rigid and easier to support than wire. I think a lot of people use it with the mistaken understanding that they are getting a stronger floor.

Millions of square feet of commercial floor are placed every year with no steel reinforcing.
Your correct about this , I have worked just about ever type of commercial job out there. No steel rebar or mess layer Down . Commercial contractors are now using the 4 wheel laser power screed machines , no way can they deal with rebar .
Over the yrs we have done Walmart’s , Kmarts , Sears stores ,shopping malls warehouses , water bottling plants , other than the outdoor loading docks , no reenforcement .
 

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado
Your correct about this , I have worked just about ever type of commercial job out there. No steel rebar or mess layer Down . Commercial contractors are now using the 4 wheel laser power screed machines , no way can they deal with rebar .
Over the yrs we have done Walmart’s , Kmarts , Sears stores ,shopping malls warehouses , water bottling plants , other than the outdoor loading docks , no reenforcement .

It can handle rebar.. Watch the video: Somero S-840 Laser Screed / Double Rebar
 