Truss bottom chord PSF ?
vortech91
Will 5 PSF dead load for the bottom chord support a metal ceiling with blown in insulation? I have the option for 5 or 10 pound per square foot bottom chord dead load. I will not be putting up drywall or OSB, so I thought 5 PSF would be sufficient. Let me know Thanks:rocker:
This is for a pole barn with trusses 48" OC truss specs 25-5-0-5 or 25-5-0-10
mike93lx
Richmond, VA
Is it a significant price difference? If not, i would go with 10 anyway.
lakeroadster
Central Colorado
Cellulose weight varies based on how it is installed (just pour it in, blow it in with the setting set at a high air mixture (fluffing). or dense packing.
So these variables need to be evaluated.
But lets make some assumptions and then do the math...
  • The weight ratio per square foot of 8-1/2" thickness of cellulose is usually .97 pounds per square foot = 0.12 psf per 1 inch of insulation.
  • Menards Dura-Panel weighs approx. 56 lbs. per 100 sq. ft. = .56 lbs per sq. ft.
So if the truss is good for 5 psf and you use Menards Dura-Panels for the ceiling steel you can have as much as 37 inches of insulation.
But don't forget to take into account the weight of light fixtures and other items you may want to hang from the ceiling.
rburke65
Canfield, Ohio
Yes....ask your truss mfg. Ask also the price increase for trusses every 24" while your at it. You'll never be sorry.