I have an existing 100A sub panel in my garage supplied by 3-wire NM cable (haven't verified the AWG yet but it's big). The neutrals and grounds are all mingled in the sub panel, which is OK from what I've read elsewhere since it's a 3-wire supply. I want to change the 240V outlet on that sub panel from a 3-wire NEMA 6-50 to a 4-wire 14-50 outlet. Can I wire the neutral and ground from the 14-50 outlet to the mixed neutral/ground in the sub, or should I separate the neutral and ground in the sub and run a separate ground back to the main panel?
Backstory: The 14-50 outlet will supply a rotary phase converter to power some small industrial equipment (208 3ph) and I want to be able to use the neutral at the machines for 120 lighting/power instead of running separate 120V accessory circuits to the machines--but keep the safety ground separate for fault protection. The plan is to use an appliance cord from the outlet to the RPC, then THHN stranded in conduit from the RPC to a 3-phase breaker panel and on to the machine outlets. I'm using 5-wire SO cable from the outlets to the machines as well, so the neutral and ground will be separate all the way to the machine panel.
I've considered hardwiring the RPC to the sub panel and eliminating the outlet, but the sub panel is recessed. I've looked at what's involved in making it surface mounted instead and it seems to be just a matter of running the NM cable into the *back* of the sub panel, patching the drywall and putting a sheet of plywood up for the panels.
Backstory: The 14-50 outlet will supply a rotary phase converter to power some small industrial equipment (208 3ph) and I want to be able to use the neutral at the machines for 120 lighting/power instead of running separate 120V accessory circuits to the machines--but keep the safety ground separate for fault protection. The plan is to use an appliance cord from the outlet to the RPC, then THHN stranded in conduit from the RPC to a 3-phase breaker panel and on to the machine outlets. I'm using 5-wire SO cable from the outlets to the machines as well, so the neutral and ground will be separate all the way to the machine panel.
I've considered hardwiring the RPC to the sub panel and eliminating the outlet, but the sub panel is recessed. I've looked at what's involved in making it surface mounted instead and it seems to be just a matter of running the NM cable into the *back* of the sub panel, patching the drywall and putting a sheet of plywood up for the panels.