Connector between main and sub
mike93lx
Richmond, VA
Edit: sub is installed. New question in post 15
I am adding a Sub next to my main and want to connect the two with some sort of rigid connector to run the feeder through. I plan to use 4-4-4-6 Al SER.
I've found "box spacer connectors" for 1/2 and 3/4 knockouts, but that obviously won't work. I'd like something like 2" diameter. Length should be around 2". Can someone help me with what I need?
hammlm
SE PA
How about:
https://www.homedepot.com/p/1-1-2-in-Rigid-Conduit-******-64315/100112701
https://www.homedepot.com/p/1-1-2-in-Rigid-Offset-Conduit-******-04015/100190206
These are both 1-1/2" trade size, but you get the idea. They are available in about any combination of diameter and length you want.
mike93lx
Richmond, VA
How about:
Yep, that's it, thanks. A ****** with a couple locknuts should work.
teamextreme
Lakewood, CO
Offset ******, as linked to above, is what you want. They are not available in different lengths, however. Standard ******* are, but they do allow you to line up knockouts with differing depths from the back of the panel. Offset ******* work perfect for this. Don't forget plastic bushings to put on the ******.
mike93lx
Richmond, VA
Thanks, that's helpful.
Mr. T
Central PA
I already have some leftover cable. Any reason not to just use what I have?
Not really, if you’re talking about function. However, given that it would only be a few bucks worth of THHN, the install would be a bit easier. I’d rather spend a couple dollars on copper wire than a tube of Noalox I’d never use again. Unless you already have some laying around.
mike93lx
Richmond, VA
I do happen to have some in my toolbox. I was going to make sure it was still good first though. If not, i agree, some #6 thhn would be the right answer
mike93lx
Richmond, VA
Since were throwing around wire gauges what size breaker are you using OP?
Planning on a 125. Its just me, but you never know when i might be welding while the compressor, drill press, table saw, a/c, and a couple angle grinders are running...
Seriously though, a 60a breaker was the plan.
wyliesdiesels
Modesto, CA
Youll need a lot larger wire for 125a...
Also, your main may not be able to support a 125a.
What is the HP rating on the compressor motor nameplate?
Is this a one man shop?
If not and you will have compressor welder and AC running, you will need more than 60a...
mike93lx
Richmond, VA
Maybe i should have added an emoticon in that...
I was joking. 60a is plenty. My 100a main panel is full and instead of switching to a bunch of tandems, i'm putting in a 12 space sub.
It will get a few 120v circuits and 240v circuits for a 1/2 hp drill press and a welder.
mike93lx
Richmond, VA
So the sub is installed and i used the al SER that i had on hand. 1-1/2" Offset ****** with nuts and bushings on both sides.
New question: Do i need any wire clamps in either/both boxes?
As an aside, i don't really do much with conduit, so i had never worked with 10 stranded thhn before (used it for the welder and heater circuits i put in)... Holy ****, it was so much easier to work with than 10 solid romex.
pattenp
Virginia - USA
If the wire is run through a continuous conduit ****** between the two panels there is no need for an internal clamp in the panels where the wire enters the panel.