Grounding connections

mcbane

Well-known member
Joined
Jul 23, 2017
Messages
794
Location
California
A question for the electrically inclined:

I am about to submit permit docs for a pre-engineered metal building. I need to install the grounding system when the footings are poured. The code is pretty clear that splices in the grounding conductor need to be mechanical, irreversible and I have the tool to do that.

My question is: is there any value in using irreversible connections at points where rebar and ground rods are connected? The code allows screw clamps at those points as long as they are "DB" rated and the irreversible lugs are costly.

Besides meeting electric code, my priorities are 1) suppress Emi problems associated with running a TIG high frequency starter in a metal building, and 2) lightning (but I hope lightning would prefer to hit a nearby 100 ft tree than my 35 ft metal building).
 
To avoid these ads, REGISTER NOW!

tyme2par4

Well-known member
Joined
May 16, 2016
Messages
571
Location
NH
A question for the electrically inclined:

I am about to submit permit docs for a pre-engineered metal building. I need to install the grounding system when the footings are poured. The code is pretty clear that splices in the grounding conductor need to be mechanical, irreversible and I have the tool to do that.

My question is: is there any value in using irreversible connections at points where rebar and ground rods are connected? The code allows screw clamps at those points as long as they are "DB" rated and the irreversible lugs are costly.

Besides meeting electric code, my priorities are 1) suppress Emi problems associated with running a TIG high frequency starter in a metal building, and 2) lightning (but I hope lightning would prefer to hit a nearby 100 ft tree than my 35 ft metal building).

I think you need to correct your third sentence. There is no such thing as mechanical and irreversible. Irreversible connections are either crimp or exothermic.
Is there a value in irreversible at other points? Sure. Compression connections are a much tighter and better connection. I would rather use them if you have the option.
 

joe_padavano

Well-known member
Joined
Feb 26, 2011
Messages
1,789
Location
Northern VA
I think you need to correct your third sentence. There is no such thing as mechanical and irreversible. Irreversible connections are either crimp or exothermic.

As an engineer, I would call a crimp connection "mechanical" as opposed to welding or solder.
 
To avoid these ads, REGISTER NOW!

Gummi Bear

Well-known member
Joined
Nov 5, 2006
Messages
524
Location
Sunset, Texas
You can also Cadweld your connection to the rebar and ground rod.

Some municipalities require this.

There are clamps made and listed to clamp your grounding conductors to rebar.




I went to the woods because I wished to live deliberately...

Henry David Thoreau
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,796
I think you need to correct your third sentence. There is no such thing as mechanical and irreversible. Irreversible connections are either crimp or exothermic.
Is there a value in irreversible at other points? Sure. Compression connections are a much tighter and better connection. I would rather use them if you have the option.

Crimped connections are irreversible,as would a exothermic, unlike a set screw connection.
 

tyme2par4

Well-known member
Joined
May 16, 2016
Messages
571
Location
NH
As an engineer, I would call a crimp connection "mechanical" as opposed to welding or solder.

Crimp connections are known as compression in the industry. Mechanical connections are anything secured with a screw or fastener.

You can also Cadweld your connection to the rebar and ground rod.

Some municipalities require this.

There are clamps made and listed to clamp your grounding conductors to rebar.
Cadweld is Exothermic.
 