Hi, I am new to this forum. I have been reading through it and have found it is a great place for info. I have been looking through threads on air compressor wiring and can't seem to understand a few things
First, I have very limited electrical experience which is probably why I am having difficulty.
I received a new 3 HP air compressor, it has no cord. It is 60 gallon and not portable. I have seen it stated that 3 HP or less motors allow the use of a cord and plug/receptacle for power. I would not be using the plug/receptacle as a disconnect.
The specs on the motor state 3 HP, volts 208-230, amps 13.1-12.3. In the manual for the compressor it states under power requirements: amps 20, dedicated NEMA receptacles 6-30R. I thought this receptacle might be listed incorrectly and upon writing to them they claim that is a typo and it should read 6-20R.
I have a 30 amp dedicated circuit. I would have the breaker changed to a 20 amp.
What I can't seem to understand is I have read in many threads that the receptacle should be rated at a minimum of the motors HP, but all the 6-20R and even 6-30R receptacles I have found are only rated at 2 HP.
I am lost and can't seem to understand how this can be hooked up with the receptacles and plugs available and listed in the compressor literature. Any input would be appreciated as I just don't get it. Thanks.
First, I have very limited electrical experience which is probably why I am having difficulty.
I received a new 3 HP air compressor, it has no cord. It is 60 gallon and not portable. I have seen it stated that 3 HP or less motors allow the use of a cord and plug/receptacle for power. I would not be using the plug/receptacle as a disconnect.
The specs on the motor state 3 HP, volts 208-230, amps 13.1-12.3. In the manual for the compressor it states under power requirements: amps 20, dedicated NEMA receptacles 6-30R. I thought this receptacle might be listed incorrectly and upon writing to them they claim that is a typo and it should read 6-20R.
I have a 30 amp dedicated circuit. I would have the breaker changed to a 20 amp.
What I can't seem to understand is I have read in many threads that the receptacle should be rated at a minimum of the motors HP, but all the 6-20R and even 6-30R receptacles I have found are only rated at 2 HP.
I am lost and can't seem to understand how this can be hooked up with the receptacles and plugs available and listed in the compressor literature. Any input would be appreciated as I just don't get it. Thanks.