Someone near me has a used Kobalt 30 gallon air compressor for $150. It is 240v or 120v. I have a basic knowledge of electricity. What is the advantage of wiring the compressor 240v as opposed to 120v?
 
To avoid these ads, REGISTER NOW!

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
25,867
Location
Niagara Region, Ontario, Canada
it is not cheaper to run on 220, but with 120 you are limited to primarily a 15 amp circuit.any 120v compressor that has any umff to it will be at the high end of amp draw on 120. even at that you will have limited air supply.
depends on what you're doing and how much air you need.
also do you need portability etc.
 

dtnel

Active member
Joined
May 17, 2018
Messages
34
Location
Attached to my house as most are.... Lol
Personally if you're doing work regularly a 60gal or larger belt driven compressor will help you long term vs getting something you'll struggle with which is my situation the last 16 yrs. I have a 60 gallon in the garage that I bought new that I need to wire up. It'll be 230 if I recollect properly and from when I checked the wiring I needed it was 2 12 gauge wires but I'll go larger since I have them ran and available as I'll be switching from a electric garage heater to a gas heater so I'll use the wiring from that to run the compressor.

Sent from my SM-G955U using Tapatalk
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
I believe it will actually use less electricity, thus be cheaper to run on 240.

Nope, the amperes are 1/2 of 120V but 120V X 2A, or 240V X 1A, equals the same, above 1 1/2 HP it becomes more common sense to use a 240V circuit because of the limits of a 20A 120 volt circuit, 1 1/2 HP is the iffy zone, where a 20A 120V circuit could be taxed enough to cause excessive breaker tripping, example was my Delta 10" contractors saw w/ a 1.5HP motor would trip the breaker it was on when doing a lot of ripping, solution was to move it to another circuit even though could have changed it to 240V with ease, saw was mothballed after getting a vintage Unisaw.
 

6PTsocket

Well-known member
Joined
Mar 12, 2014
Messages
4,593
I believe it will actually use less electricity, thus be cheaper to run on 240.
Not so. At the lower voltage it draws twice the current. The wattage is the same in either case. There is no free lunch.

Sent from my SM-G900V using Tapatalk
 

6PTsocket

Well-known member
Joined
Mar 12, 2014
Messages
4,593
The advantage of 240 is that the wiring can be a lighter gauge. That is detirmined by the current. As pointed out, on 120 you are pushing the 20A limit of the circuit and may start tripping the breaker

Sent from my SM-G900V using Tapatalk
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,075
Location
Minneapolis
As mentioned, the power consumption in watts is the same, and you're paying for watts so the cost of operation is the same.


If a motor is small enough to run on a standard 120vac circuit there's no advantage to converting it to 240vac. You may as well leave it at 120vac, then you can plug it in anywhere.
 

jsaw

Well-known member
Joined
Oct 11, 2008
Messages
1,784
Location
Geneva, N.Y.
one of My compressors can be wired to run with either 120 or 240. when run on 220, it started up a lot quicker, especially when cold.
the biggest disadvantage was that it was not as portable, because 240 outlets are not as common as 120 outlets
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,048
dual voltage motors have two sets of windings - the windings are in parallel on 120V, and in series on 240V. either way, the windings only see 120V.

if you dual voltage motor works better on 240V than 120V, you're starving it for current, and that's why it doesn't work as well.
 
To avoid these ads, REGISTER NOW!

6PTsocket

Well-known member
Joined
Mar 12, 2014
Messages
4,593
dual voltage motors have two sets of windings - the windings are in parallel on 120V, and in series on 240V. either way, the windings only see 120V.

if you dual voltage motor works better on 240V than 120V, you're starving it for current, and that's why it doesn't work as well.
The wiring on the 120 circuit is probably not heavy enough to suppy twice the current with the same minimal drop he sees on 240.

Sent from my SM-G900V using Tapatalk
 

Ike4160

Active member
Joined
Feb 18, 2014
Messages
29
A friend of mine bought the same exact speedaire 30 gal compressor as me the same week. I wired mine for 240 and he wired his for 120. Not sure why, but his motor burned up after the first year. Mine is still original from 2003. Mine is also always on in an unconditioned garage.
 

nelstomlinson

Well-known member
Joined
Jul 27, 2009
Messages
649
Location
Interior Alaska
The heat in your motor is proportional to I^2*R. If you double the current by going from 240V to 120V, you have four times the heat. Always run at the highest available voltage.
 

BukitCase

Well-known member
Joined
Apr 11, 2017
Messages
1,075
Location
Oregon
" If you double the current by going from 240V to 120V, you have four times the heat" -

NOT true - see post#11; the windings themselves will see the SAME current (AND voltage) in either configuration. The only place that would see twice the current on 120 volt is the wires TO the motor... Steve
 

bsaint

Well-known member
Joined
Apr 26, 2010
Messages
5,109
Location
Manchester, CT
" If you double the current by going from 240V to 120V, you have four times the heat" -

NOT true - see post#11; the windings themselves will see the SAME current (AND voltage) in either configuration. The only place that would see twice the current on 120 volt is the wires TO the motor... Steve

No you spread the current out across more windings. You have less heat. If the current is half the heat is less also. Basic electricity.
 

BukitCase

Well-known member
Joined
Apr 11, 2017
Messages
1,075
Location
Oregon
Each half of the total windings would be designed to work on 120 volts, and wouldn't care which "hot" the non-neutral end sees - so each half of the winding would get the same WATTAGE either way. Same wattage, same heat. Again, the ONLY place that would change is in the SUPPLY wiring TO the motor, which would need to supply TWICE the current in order to feed BOTH windings (when wired for 120 volts)... Steve
 

Citation

Well-known member
Joined
Jan 20, 2016
Messages
3,212
Location
Indy
The heat in your motor is proportional to I^2*R. If you double the current by going from 240V to 120V, you have four times the heat. Always run at the highest available voltage.

Remember that when you change the motor over to 240V operation you double the resistance. Think of it as two resistors. In 120V mode the resistors are in parallel thus each sees 120V and half of the current (15A so 7.5 each). In 240 V mode you put the resistors in series. Now the current from one resistor flows into the other (7.5A). The 240V is spread over two resistors in series so each sees half the total or 120V. This each sees the same load.

Your thinking would be correct if the resistance was unchanged and the voltage was doubled.

To the OP's question, the advantage is less voltage sag under load or during start up. Generally 240V wiring is going to be the same gauge as 120V wiring but now the load is half. The voltage sag is lower which makes starting easier. It also might save some insignificant amount of electricity in terms of lower line loses.
 