Two (more) Mitsubishi mini split questions

aunsafe2015

Well-known member
Joined
Apr 2, 2016
Messages
436
Location
Northern VA
Thanks for all the help so far. Two more hopefully easy questions.

1) Did I wire the indoor unit correctly? See attached pictures. I stripped the wires by the length the installation manual specified, but it seems like it should have been shorter?

Also, for ground, I literally just wrapped it around the green screw and tightened it down. For red, black, and white, I loosened the screw, stuck the wire into the little slot, and tightened the screw back down.

2) Anybody know what these small filters are for (see picture)? They are listed on the parts sheet, but the manual doesn't actually say what to do with them... And I don't see an obvious place for them.

3) A few other random pictures attached for anybody who is curious to see more.

P.s. I'm a novice DIY-er so I apologize for my absurd questions. I'm having a licensed HVAC guy come by tomorrow to do the nitrogen test, vacuum, and initial turn on.
a3272bbf9b512c99d265cc7a891dc039.jpg
a64f66b40d1715bc4fcc96f3bb1c127e.jpg
4c8ffdc201ef22b3e1e68dc585c8651d.jpg
832808ecf38ac2569f1132eead314229.jpg
dad2c0c8d43192bef9e13b6ad9d6fc71.jpg
66514f9d14c6d9684bc0019aa7141b26.jpg
c870f431a276002fb54009b4a7075cb6.jpg
 
To avoid these ads, REGISTER NOW!

tab2

Well-known member
Joined
Apr 9, 2009
Messages
381
Location
Boston
Thanks for all the help so far. Two more hopefully easy questions.

1) Did I wire the indoor unit correctly? See attached pictures. I stripped the wires by the length the installation manual specified, but it seems like it should have been shorter?

Also, for ground, I literally just wrapped it around the green screw and tightened it down. For red, black, and white, I loosened the screw, stuck the wire into the little slot, and tightened the screw back down.

2) Anybody know what these small filters are for (see picture)? They are listed on the parts sheet, but the manual doesn't actually say what to do with them... And I don't see an obvious place for them.

3) A few other random pictures attached for anybody who is curious to see more.

1. Looks correct in terms of placement, but it could be cleaner. especially with the ground. How long does it say to cut the insulation back? You don't want to leave that much exposed on your two hots and neutral. Back the screws out a enough to make sure you have proper engagement.

2. The green one is a HEPA filter I believe. I threw mine out.

3. The rest of the pictures look good; you will love them. I miss mine so bad at our new house. Thankfully this weekend we are salvaging some equipment that will be my new system (ducted this time around). Hole to the outside is sloped downward, unit is on a pad. The liquid tight is a little droopy but its hard to keep it tight without using 100 hangers. Be careful bending the linesets, but it is hard to damage them.
 

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
if you back the screw out more you should be able to insert it further. Be careful the screw does not fall out. You try wiggle the wire , so the wire strand can hit the very end of the terminal

If you do end up trim the wires move it away from the unit so the little copper strands do not fall anywhere near the unit. As the picture shows, I would trim it.

the small filters snap into a little rectangle on each filter screen, you need to remove the screen.
 

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
Here is a terminal pic I have from another brand, I think you just didn't insert it enough..


When you wire the outdoor double check the colors match the numbers, obviously, that's why I took pictures.
 

Attachments

  • IMG_1645.JPG
    IMG_1645.JPG
    84.1 KB · Views: 54

Git

Well-known member
Joined
May 18, 2008
Messages
6,895
Location
S Cal
That's what I did - just crimped a ring terminal on it

attachment.php
 

Attachments

  • SNAG-1081.jpg
    SNAG-1081.jpg
    123 KB · Views: 173
OP
A

aunsafe2015

Well-known member
Joined
Apr 2, 2016
Messages
436
Location
Northern VA
1. Looks correct in terms of placement, but it could be cleaner. especially with the ground. How long does it say to cut the insulation back? You don't want to leave that much exposed on your two hots and neutral. Back the screws out a enough to make sure you have proper engagement.

2. The green one is a HEPA filter I believe. I threw mine out.

3. The rest of the pictures look good; you will love them. I miss mine so bad at our new house. Thankfully this weekend we are salvaging some equipment that will be my new system (ducted this time around). Hole to the outside is sloped downward, unit is on a pad. The liquid tight is a little droopy but its hard to keep it tight without using 100 hangers. Be careful bending the linesets, but it is hard to damage them.
Does this look better for the ground wire? The problem I'm having is that as I tighten the green screw down, the strands of copper flatten out and some of the individual strands pop out and are not secured down by the screw.

What's the best way to do this? Tighten it down as much as reasonably possible while keeping as many of the individual copper strands under the screw as possible? I don't have one of those terminal rings that somebody mentioned, but I suppose I could get one if this ground wire is going to compromise safety or function.
419011c6d4d66a4f1eeb204e73be8509.jpg
 

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
These filter screens? I don't immediately see where they would attach...?
14146bf07295b434b71e588139cd7036.jpg
eca71bd2a3fb056b921072033743d436.jpg

It goes on the bottom of the screen where the 2 little tabs is, you see the grid have more closely spaced bars? right in the middle of the screen, on the bottom.

When installed it stays on the INSIDE of the screen, just snaps on
 

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
Does this look better for the ground wire? The problem I'm having is that as I tighten the green screw down, the strands of copper flatten out and some of the individual strands pop out and are not secured down by the screw.

What's the best way to do this? Tighten it down as much as reasonably possible while keeping as many of the individual copper strands under the screw as possible? I don't have one of those terminal rings that somebody mentioned, but I suppose I could get one if this ground wire is going to compromise safety or function.
419011c6d4d66a4f1eeb204e73be8509.jpg

It should be fine, but you can just use the wire stripper to make a cut about 5-6" from the end, then use pliers to start pulling the insulation back about 1", leave everything, then hook the exposed copper to the screw. You can then trim the "tail" of it but keep it as long as possible, at least 1-2" is preferred. That's what the pros have done, honestly I have done it like you have it has not come off or anything..
 
To avoid these ads, REGISTER NOW!

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
you can counter twist the wires -- that helps. Or screw in a pigtail
 
OP
A

aunsafe2015

Well-known member
Joined
Apr 2, 2016
Messages
436
Location
Northern VA
It goes on the bottom of the screen where the 2 little tabs is, you see the grid have more closely spaced bars? right in the middle of the screen, on the bottom.

When installed it stays on the INSIDE of the screen, just snaps on
Got it, thanks. Does it matter which one goes on which side?
e07e34b5bfcb360691be26dee2d29d03.jpg
 

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
You can only snap it in that way..... now let's see this thing installed before winter :)
 
OP
A

aunsafe2015

Well-known member
Joined
Apr 2, 2016
Messages
436
Location
Northern VA
You can only snap it in that way..... now let's see this thing installed before winter :)
HVAC guy had to reschedule for tomorrow. He had a good reason. Hopefully he makes it tomorrow though!

One more pic for now. It would have looked better centered above window, but I would have had to go above the header, which would have had it further up the wall than I wanted.
2576f81f074e7177a72379b1fb78e942.jpg
 
Last edited:
OP
A

aunsafe2015

Well-known member
Joined
Apr 2, 2016
Messages
436
Location
Northern VA
Still not finished. I had done most everything except connect the lineset to the condenser (I did already have it connected to the indoor unit, though).

He did not deburr the tubes. I asked if he was going to use a torque wrench and he said he doesn't need one.

Then, he is missing the adapter to connect to the service port. So he wasn't able to do the pressure test or vacuum.

So, basically, nothing got done today.

By the way, does anybody know if these newest Mitsubishi hyperheat units (MUZ-FH09NA) even need an adapter for the service port? I have a 5/16 to 1/4 adapter, but the female end won't connect to the service port. Too big.

I then tried to connect to the service port with a 1/4 ball valve I had, and sure enough, the 1/4" ball valve connected right up.

So what adapter does the guy supposedly need? This is the one I have: https://www.amazon.com/gp/product/B00D96EWKQ/?tag=atomicindus08-20. But like I said, the 5/16 female end is too big... 1/4 fits. Am I missing something?
 
Last edited:

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
If the 1/4" works then it is 1/4"
I have heard of some of the mitsubishi are using 1/4"
although mine needed 5/16 adapter, so does daikin, pioneer etc.
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
did you figure out the filters ? They just slid into that long grove to the back top of the unit. The extra little filters are indeed odd - one is a microbial and the other a platinum screen.

I guess they wash the condenser in some type of magic vapor.



I forget -- where did you get your units?

The eye really works -- you will like the units. IMO ..still the best.
 
OP
A

aunsafe2015

Well-known member
Joined
Apr 2, 2016
Messages
436
Location
Northern VA
If the 1/4" works then it is 1/4"
I have heard of some of the mitsubishi are using 1/4"
although mine needed 5/16 adapter, so does daikin, pioneer etc.
He continues to insist that he needs an adapter. Doesn't seem to care that my 1/4 ball valve hooked right up.
 
Last edited:
OP
A

aunsafe2015

Well-known member
Joined
Apr 2, 2016
Messages
436
Location
Northern VA
did you figure out the filters ? They just slid into that long grove to the back top of the unit. The extra little filters are indeed odd - one is a microbial and the other a platinum screen.

I guess they wash the condenser in some type of magic vapor
Yep figured it out, thanks! Ecomfort.
a50b44921959435c482493042557a74e.jpg
 
Last edited:
OP
A

aunsafe2015

Well-known member
Joined
Apr 2, 2016
Messages
436
Location
Northern VA
Just to close the loop, seems that most or all Mitsubishi made after 2010 have 1/4 service ports, including all FH models.
 