I'm finishing up wiring my pole barn and have a few questions to make sure I pass inspection. I have 2 cicruits for my outlets. Am I ok to use gfci breakers instead of putting a gfci outlet on each circuit? Does my indoor lighting circuit need to be on an arc fault breaker? I'm putting the outdoor lights on a separate breaker. Does that need to be arc fault? Also if I decide to put an outlet outside can that be on the same circuit as the outdoor lights?
 
To avoid these ads, REGISTER NOW!

acer66

Well-known member
Joined
Dec 4, 2010
Messages
4,418
Location
Western North Carolina
Not sure if a barns differs from a garage but here also under under NEC2014 there is no requirement for arc fault breakers only in the house.

You can put a receptacle on the same circuit as the the lights but if you use gfci breakers instead of gfci receptacles, which you can, you might end up in the dark when the breaker flips with lights and receptacle on the same circuit.

Also good is to check with your local inspector for any local code amendments.

I am not an electrician but I completly rewired my house and gargage and developed a good relationship with my inspector after he realized that I wanted to do things right.
 
OP
A

AA7483

Well-known member
Joined
Dec 22, 2017
Messages
433
Location
South Jersey
Thanks for your response. An additional question. I used a main lug only panel and am back feeding my main breaker. I inverted the panel (manufacturer made panel to be inverted) since my feed is coming from the bottom. Only place I can install the main breaker is on the bottom right since that's the only place the hold down clip lines up. Any issues?
 

shadycrew31

Well-known member
Joined
Jun 23, 2017
Messages
58
Location
Burbs of Philly
I'm not a sparky but I dabble. Some quick research popped up code 240.81, which requires vertical switches to function up = on down= off. I imagine if you have this panel inverted it is working opposite of that. Outside of that I don't believe there is any code that mandates the main be at the top of the panel.

If you get grilled on it by the inspector ask him to show you the code so you know what specifications you need to follow. If he cant produce the code you don't need to follow it.
 
OP
A

AA7483

Well-known member
Joined
Dec 22, 2017
Messages
433
Location
South Jersey
I'm 99 percent sure it isn't an issue since my switch operates side to side.
 

Attachments

  • IMG_20180730_160840.jpg
    IMG_20180730_160840.jpg
    106.2 KB · Views: 69
To avoid these ads, REGISTER NOW!
OP
A

AA7483

Well-known member
Joined
Dec 22, 2017
Messages
433
Location
South Jersey
Thanks. I inverted the panel to keep the bottom feed cleaner then started second guessing the location of the breaker.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,765
Thanks. I inverted the panel to keep the bottom feed cleaner then started second guessing the location of the breaker.

You need a bushing on the PVC terminal adapter, and make sure there is a hold down on the backfed main breaker which looks like it's there.

With a vertically mounted main breaker the handle in the ON position needs to be up, which is why in the past they have been redesigned to make it code compliant to top or bottom feed it.
 
Last edited:
OP
A

AA7483

Well-known member
Joined
Dec 22, 2017
Messages
433
Location
South Jersey
Thanks guys. I'm an HVACR contractor by trade so I have plenty of dealings with my local inspectors so I don't anticipate any problems but I want it to be right. I have a Siemens q260 60 amp breaker that says it will fit #8 to 2/0 copper or aluminum but I don't see how this #2 wire is going to fit.
 