Emt. Ground wire to receptacle

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
Running emt with no ground wire. Is it true the receptacle ground don’t have to be tied to the metal box if I use the cover that has recessed corners ?
 
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
If you're talking about a surface mounted box, with a surface 1/2" 'raised' cover, then some inspectors look at differently. Some will pass it if the cover is the same brand as the box (ie: Raco, Steel City).
Some look at as "the cover might separate from the box if the mounting screws loosen" (a definite possibility) and won't allow it.

To be on the safe side, run the ground wire from the receptacle to the box. Grounding pigtails are cheap insurance.
 
OP
P

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
I was thinking about this picture that I saw earlier

outlet-jpg.414763
 
To avoid these ads, REGISTER NOW!

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,826
Location
SE Michigan
If you have Menards, they have the stranded 12awg jumpers with 10-32 screw and a fork terminal on the other end. I believe Ideal also makes a stranded version of same.

If working with stranded I hate to introduce a solid into the picture, but thats just me.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I twist them around screws all the time. reverse twist it and its pretty secure. The outlets are designed a bit different but twist hundreds and even thousands of them and never a problem. I got a box of green screws and a box of forks too, make them up with fork on one end all the time, usually from scrap wire, takes a minute. In some places even crimp an eye on it.
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,979
If you're talking about a surface mounted box, with a surface 1/2" 'raised' cover, then some inspectors look at differently. Some will pass it if the cover is the same brand as the box (ie: Raco, Steel City).
Some look at as "the cover might separate from the box if the mounting screws loosen" (a definite possibility) and won't allow it.

To be on the safe side, run the ground wire from the receptacle to the box. Grounding pigtails are cheap insurance.

Code says the cover is good enough, if the device is attached to the cover with suitable fasteners (which include the serrated nuts included with good quality covers, but also things like rivets), and the device is listed for such use (which means it's got a copper jumper around one of the screw holes, in most cases.). 250.146 is very clear on how to meet the requirements.
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,979
Well I guess I will probably add it, helps to hold the receptacle while I am wiring those boxes mounted on the ceiling!

Wire the device on the ground, with pig tails. Then you just need to attach your wire nuts, and screw the cover in place.
 