This will only be a 240 sub panel. No neutrals needed. Only ran a 6/2. My question is per code do I need to go buy a separate Ground Bar. Or can I use the neutral bar as the ground bar since there will be no neutrals whatsoever. Brevard Florida
You have a total of three conductors... 2 hots, and one grounding conductor.. Correct ?
So then you can use the "Neutral" Bar as a "Grounding Bar", making SURE it is bonded to the box.
AFAIK... In practical use anyway.. code Guys will chime in.
Marc
I dunno, this bothers me though...Someday you will be gone, and some future Yahoo will take over.. and say "Gee, I don't have a neutral here, and I want a 120 outlet..... OOOOO but I DO have a ground !! ... so thats 120 to the ground.... Martha,,, I'm all set !!
Not good.
Marc
Holy ****. Marc, take a deep breath and step away.
We can't solve for every ***** to come after us.
OP, you are fine. Add a label to the panel if you want. Use the panel, the world will not end.

Ok, so let me try to explain maybe better..
First, I am not talking "Code" because it has been years since I worked with it... I am just talking practical reality.
OK, so, for YOUR needs what you have is fine.
Bond your grounds from your outlets, and the incoming ground all together opn a strip that is ALSO bonded to the box.
All fine.
Here is the potential future REAL problem....
now, you know that from either one of your hots to your ground you have 120v.. CORRECT ??
Yes, you know that.
Now, you die, Wifes new Husband that is a hack says... HMMMM I need another to run some BigASS lighting in the shop here.. I have the power right here (referring to your new 220 only subpanel)
BillyBob sez to himself "There ain't nun of dem whi9te mwarrs here.. how do I hook up my BigAss lights?
He gets out his little free HF tester, and realizes he has the 120 he needs .. but it to the ground you have.. NOT to a legitimate insulated current carrying Neutral
So, he feeds his lighting w a single pole breaker and the Ground bar you installed... Girlfriend, or the Wife, gives him extra special reward saying "You are MY Electrician Man".
BillyBob sleeps extra good that night.
Couple months later, BillyBob wrecks driving drunk on a beer run.
Wife gets new Boyfriend.
Roscoe.
New boyfriend w OCD, decides he want to rearrange and straighten up the wiring in the MAIN panel.
He was just in the shop to get his HF screwdriver, and left those Big *** lights on that previous BillyBob installed.
Roscoe starts removing and straightening up the grounds on the ground bar in main panel.
Sweaty greasy hands.. he is grabbing those grounds NOO problem cuz he "Knows" they are dead.
He lifts the ground that fed the subpanel you put in, and, being Roscoe, he has no shoes on. staning in the damp grass, and allasudden... HE is the major load in the cjkt...completing the ckt to Ground through his body in series w the BigAss lights.
Roscoes heart goes ded, Wife needs to go out again.
Marc
Did I skeer everyone away?
I know what I was saying was Fact.
Watching "Red October" for the umpteeth time as I type.
Marc
Yes I didn't notice when I started it. I apologize.
Instead of another verse of "50 ways that Billy Bob will electrocute himself," why don't we just state the obvious: Whether it's code required or not, it would be a really good idea to run a neutral wire to the subpanel.
Sent from my iPad using The Garage Journal mobile app
I would like to know if it's code or not. Running a neutral is not an option. I am not pulling down walls that are painted. it was a mistake. But I only planned on running 240. And if I add AC I will still will have the slot to add that.
You'll find there is no topic in the electrical section, no matter how simple, that it can't be beat to death with a sledgehammer.![]()