Im planning out my shop and I’m stuck at one thing. I have 400 amp service running to the house, then it’s split off 200 to the house and 200 to the shop. There’s 2 cut off switch box’s next to the meter, one for the house, one for the shop. I see the ground wire coming out of th main meter box connecting to the ground rod. In the main panel in the house I see that neutral and ground are bonded with the green screw.
I’m assuming when I install the main panel in th shop I will also have it bonded. Correct me if I’m wrong. And do I need to run a ground rod at the shop and ground the panel at the shop?
I’m a novice.
Who wired all this up? And are these pictures current?
There are many things wrong here.
All panels after the first means of disconnect need to be 4-wire with isolated neutral bars.
The panel in the house with the 4-wire SER should most definitely NOT be bonded.
The bare aluminum is the EGC/ground wire and that needs to be on a separate bus bar. The green bonding screw needs to be removed as well.
You will probably have to purchase a ground bar kit. Needs to be listed for the panel. Any grounds on the neutral bar need to be moved over to the new bars.
The 3-wire running to the shop is wrong as well. NEC requires 4-wire to all subpanels including detached as of 2008 code cycle or if there are parallel metallic pathways. 4-wire is best regardless.
The panel you put in the shop is considered a subpanel NOT a main panel. This subpanel also needs isolated neutral bars (unbonded). You also need 2 ground rods here.
The disconnects, in your case, are the mains and the neutrals need to be bonded here with the GEC from the rods.
All of these situations are covered in the electrical FAQs here (post #3):
https://www.garagejournal.com/forum/showthread.php?t=356460
Here’s the main panel in the house and the service entrance and meter with 2 cut offs outside the house. The 3 strand is what’s running to the shop
Need to add an EGC/ground wire to the feeder to the shop.
Hmm... are you saying I need a grounding wire from the panel in the shop to the cut off next to the meter panel? That may be a problem, the cable is already buried and ran to the shop which is about 200ft from the house. Is there another option?
I had the electrician do it when he was wiring my house, it’s interesting that he didn’t mention it.
I’m located in Texas, out in the country.
Yes that is what we are saying.
Whoever this electrician is, he isnt a very good one and doesnt know what he is doing evidenced by your pics.
There is no other option. The ground wire needs to be ran to the shop.