realigning wires in my two panels?

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,480
Location
Richmond, VA
Hi all,

So with the pending hurricane, it has me thinking of one of my "to do" projects (number 478 of 1,257!).
I have twin 200A panels in my garage:
Boxwv-2GO2n4a_phztIFeQZbt8irU7S3HqSPmQhFKuBeIuBycP0-x6w4XdPIULy-HZd_qgGpMc6EDCRisCq_TJE_0MbWcf6-m5mW7MJ3XOwzFJcJkIFyv2vkfdoEIa7S3b_Una8AkMQqAQhGzzbr-LX6KxjtjsL6D_ISTPhH-oqX7uyloyhYvQ39suCO0w77ElJGqHya7GrcWsakEiidzD_kHqjjCnvObXLVo4kkHzEBEGqLnHeLqxu8v0BEIyxmq0Oi4WA04BHayuujNV2Dr1yHgm_ImkZeAyvP9v-8Ht5ZoIsYStrP7FMMUKFrJ3lIVme6JmpsgkKb5pxZoiaDDjWKcqcgMLkOSjJIqT6UMMWIf6AxLh5xBgFV_Vp81SD6dHXzlAE9A_JiH6EPlaiQl4pkIDExbPz_bNJP6Rjw9GJWydCkJk_bdaX8bPZlp8FE2gJj2ny-aj52lF8rqOAk-Vc5QP9J4tdSyEL2BaV2gJsJkZcDZcZMUwgVOFLS65sottbznEwvjSX4XASuMtKvczOuOIxOgQW1KpXJH3Q8AFVzXOGtZPqrHkivmSB3OOfQt7ALWGju1eDmu8I7S7CeeRoxsRX8I8yf-yd0F48=w497-h662-no


I have a generator plug below the left panel and that gets my kitchen fridge, upstair lights, well pump and other stuff. My garage fridge is in the right panel and so are the family room lights, etc.
What I would like to do is put all my "essentials" in the left panel and that have the generator just run those.
I then will install a manual interlock kit on that panel.
What is the code compliant way to move wires between the panels? I figure I am cutting some drywall above the panels to access the wires Most are going to be too short - so how can I do this?

Thanks,
Joe
 
To avoid these ads, REGISTER NOW!
OP
J

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,480
Location
Richmond, VA
Darn. Sorry about the picture not working. I’m going to attach it
 

Attachments

  • C4B6E6DF-2E77-4F46-8827-AA3F38C25BBA.jpg
    C4B6E6DF-2E77-4F46-8827-AA3F38C25BBA.jpg
    105.9 KB · Views: 320

Warrenator

Well-known member
Joined
May 31, 2008
Messages
781
Location
Newberg, OR
If you need to splice wires you can use wire nuts and add a bit of the appropriate wire to make it long enough but this must be inside either a junction box or inside the panel, can't hide the splices inside a wall.
 

Radix2

Well-known member
Joined
May 28, 2014
Messages
1,853
Location
the thumb!, MI
Put another interlock in the second panel and power it from a breaker in the first. Then you can pick any circuit in any panel to power with your generator safely. No need to move any wires, cost is two breakers and the interlock.
 

tyme2par4

Well-known member
Joined
May 16, 2016
Messages
571
Location
NH
Put another interlock in the second panel and power it from a breaker in the first. Then you can pick any circuit in any panel to power with your generator safely. No need to move any wires, cost is two breakers and the interlock.

That's clever. I wouldn't have thought of that option.
 
OP
J

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,480
Location
Richmond, VA
Put another interlock in the second panel and power it from a breaker in the first. Then you can pick any circuit in any panel to power with your generator safely. No need to move any wires, cost is two breakers and the interlock.

Great idea!
So the concept is to have the 2nd panel (right one in the pic) powered, in the event of a power loss, by the first panel because the main in the 2nd panel must be off for the "new" breaker (the interlock breaker in the 2nd panel) to "power" the rest of the panel.

So the question is what size breaker should the two new ones be?
The largest breaker I can get in the panel is 125A. The 2nd panel will also have a 125A breaker eventually to power my detached garage.
I guess it can be reasonable - 40-60A since my generator is only 8K running and cannot power any HVAC systems (I am 100% electric).
Just need to make sure I manually cut those larger draw items off in the panel. This includes house HVAC and in the future detached - compressor, welder, lift, etc. I don't want to cut the "main" 125A to the detached because there more than likely be a fridge out there also and want to have access to lights.

Am I interpreting this correctly?

Thanks,
Joe
 
OP
J

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,480
Location
Richmond, VA
30A - of course - brain fart. Now as for routing my 10 gauge wire between the two 30A breakers in the panels - what is acceptable for code? Do I need to go up, over and down or can I drill between the two panels and go right through?
 

slow

Well-known member
Joined
Feb 26, 2006
Messages
2,596
Location
near Orlando
Is there any concern with using a larger interconnect breaker? ie a 50 in case you upgrade generators in the future?
 
OP
J

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,480
Location
Richmond, VA
Is there any concern with using a larger interconnect breaker? ie a 50 in case you upgrade generators in the future?

Good question - can I use 50 between the panels - as long as the generator is plugged into a 30A? Then if I upgrade generators, I would just need to upgrade the breaker the generator is plugged into (30 to 50 in this case?)
 

Radix2

Well-known member
Joined
May 28, 2014
Messages
1,853
Location
the thumb!, MI
Great idea!
So the concept is to have the 2nd panel (right one in the pic) powered, in the event of a power loss, by the first panel because the main in the 2nd panel must be off for the "new" breaker (the interlock breaker in the 2nd panel) to "power" the rest of the panel.

So the question is what size breaker should the two new ones be?
The largest breaker I can get in the panel is 125A. The 2nd panel will also have a 125A breaker eventually to power my detached garage.
I guess it can be reasonable - 40-60A since my generator is only 8K running and cannot power any HVAC systems (I am 100% electric).
Just need to make sure I manually cut those larger draw items off in the panel. This includes house HVAC and in the future detached - compressor, welder, lift, etc. I don't want to cut the "main" 125A to the detached because there more than likely be a fridge out there also and want to have access to lights.

Am I interpreting this correctly?

Thanks,
Joe

You have it right, the breakers can be whatever size you want, just be sure to size the wire appropriately. Alternatively you can split your generator feed and run it to the interlocked breakers in both panels.

If you go with the breaker feed, you should leave the feed breaker normally off to avoid any live wires in the second panel when it's main is off and the backup is not being used.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,903
Location
Richmond, VA
While there are certainly generators over 30a, they get quitr large and use a ton of fuel. I'd be realistic about what you'd actually run and wire it accordingly.
 
OP
J

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,480
Location
Richmond, VA
You have it right, the breakers can be whatever size you want, just be sure to size the wire appropriately. Alternatively you can split your generator feed and run it to the interlocked breakers in both panels.

If you go with the breaker feed, you should leave the feed breaker normally off to avoid any live wires in the second panel when it's main is off and the backup is not being used.

When you say split your generator feed, do you mean like the attached crude pic? :)
So wouldn't this be "safer" overall? This would prevent 2nd panel main being on and someone turning the feed breaker on accidentally in panel 1?
 

Attachments

  • Generator.jpg
    Generator.jpg
    34.6 KB · Views: 43

Radix2

Well-known member
Joined
May 28, 2014
Messages
1,853
Location
the thumb!, MI
When you say split your generator feed, do you mean like the attached crude pic? :)
So wouldn't this be "safer" overall? This would prevent 2nd panel main being on and someone turning the feed breaker on accidentally in panel 1?

Yep, although you will want to splice the wires with wirenuts or whatever since the breaker is probably not approved for two wires under the clamp.

Since your panels are set up for it, the split feed is probably simpler to understand and so safer.
 
OP
J

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,480
Location
Richmond, VA
So like the attached picture?

Also - regarding my question around the wire from panel 1 to panel 2.
Do I need to go "up and around" or can I drill a hole between the two(like the attached pic)? I am assuming that one of the panels is on a stud between the two.
 

Attachments

  • Generator-2.jpg
    Generator-2.jpg
    35.2 KB · Views: 31
Last edited:
To avoid these ads, REGISTER NOW!

tyme2par4

Well-known member
Joined
May 16, 2016
Messages
571
Location
NH
Yep, although you will want to splice the wires with wirenuts or whatever since the breaker is probably not approved for two wires under the clamp.

Since your panels are set up for it, the split feed is probably simpler to understand and so safer.
Most 30A and lower breakers are rated for 2 wires. It's common to run smoke detectors, or the outlet adjacent to the panel off of breaker that is used for other things.

So like the attached picture?

Also - regarding my question around the wire from panel 1 to panel 2.
Do I need to go "up and around" or can I drill a hole between the two(like the attached pic)? I am assuming that one of the panels is on a stud between the two.

Do your panels have knockouts on the sides? If so, then no reason you can't go through the sides. If you drill a hole, you flirt with voiding warranties and listings.
 
OP
J

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,480
Location
Richmond, VA
Most 30A and lower breakers are rated for 2 wires. It's common to run smoke detectors, or the outlet adjacent to the panel off of breaker that is used for other things.



Do your panels have knockouts on the sides? If so, then no reason you can't go through the sides. If you drill a hole, you flirt with voiding warranties and listings.

I will have to check if they have knockouts on the side when I get home. Not sure what warranty I have since these panels are circa 1993, when the house was built. My concern is code compliance.
 
OP
J

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,480
Location
Richmond, VA
I checked my panel and there are knockouts on the side of the panels, and they line up between the panels. (see pic with red arrow).Of course there is the 2x4 stud between them...

So if I punch the knockouts and drill the wood out, what connector can I use? The other pic shows some clamps that I might be able use. The "ears" would go between the panel and the 2x4 - with the screw side inside the panel like the others. Which makes me wonder - is that even acceptable?

Thanks
Joe
 

Attachments

  • Panel - knockout.jpg
    Panel - knockout.jpg
    134.9 KB · Views: 54
  • Panel - knockout - 2.jpg
    Panel - knockout - 2.jpg
    109.2 KB · Views: 49

EOC_Jason

Well-known member
Joined
Jun 25, 2012
Messages
11,388
Location
Bentonville, AR
The metal clamps have a nut on the back side to tighten down to the panel. Plastic ones you pop in from the outside of the panel too.

... and you still have to drill the hole without hitting any wires in the panel.

Maybe there is something out there just for this kind of situation, I dunno...
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,903
Location
Richmond, VA
The stud between in the problem. I think you'll have to go out the top or bottom, use the proper clamp/connector and drill a hole in the stud elsewhere
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,371
Location
Michigan
If you can get the knock outs out and drill a clean hole between them(and that could be tricky to say the least) you could use a conduit ****** with a couple locknuts and bushings to go between the panels.
 
OP
J

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,480
Location
Richmond, VA
If you can get the knock outs out and drill a clean hole between them(and that could be tricky to say the least) you could use a conduit ****** with a couple locknuts and bushings to go between the panels.

true - i guess since it is in a stud I would need some kind of "protection" from a nail - even though when the panel covers are on they **** up against each other.
 
OP
J

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,480
Location
Richmond, VA
So this project got delayed....(shocker in my life)......and I am coming back around to it.

Since I am always on the prowl for a good deal on a larger portable generator, I plan on running 6 gauge wire everywhere. I figure for the 5-6 feet of total wire I need the cost is minimal. If I upgrade my generator at some point, all I would need to update is the outside outlet box - from a 30A to a 50A and then replace the breakers in the panel from 30A to 50A. Might never happen, but then I don't have to worry about wiring..

Anyway - on to the questions -
The wire will run from the outlet into the "left" panel, to a "connector" and then run one wire to the 30A breaker and the other to the "right" panel 30A breaker. (reference the attached panel pic in earlier post).
As for connecting/splicing the wires, can I use these connectors inside the panel? (attached pic and link below):
https://www.amazon.com/gp/product/B008KNX45M/ref=ask_ql_qh_dp_hza


I assume I can use 6/3 NM-B and 4 connectors? or should I use individual wires - but then I would need conduit inside the walls right?
Also, do I need to have the neutral and ground going to both panels? I read a bunch on neutral/ground bonding and still a little confused on that. I do know that on my current generator the the is bonded to the generator frame.
 

Attachments

  • wire-connector.jpg
    wire-connector.jpg
    58.4 KB · Views: 9
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,073
Location
Modesto, CA
Is your idea to backfeed your panel with generator power through one of these putlets?

If so, how will you handle isolating PoCo power? Will you have an interlock?
 
OP
J

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,480
Location
Richmond, VA
OP
J

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,480
Location
Richmond, VA
You can use them. I don't see the need for more than two though. The panels are already grounded and the neutrals tied together for full service current.

So in other words, I just need one set for the red and black? The neutral and ground from the plug can just terminate in one panel and be done? No need to have a neutral and ground in both panels?
 

Radix2

Well-known member
Joined
May 28, 2014
Messages
1,853
Location
the thumb!, MI
So in other words, I just need one set for the red and black? The neutral and ground from the plug can just terminate in one panel and be done? No need to have a neutral and ground in both panels?

Yes, the other connections are already made
 