Shop panel main or a sub?

CJseven

Well-known member
Joined
Mar 4, 2007
Messages
344
Location
Southeast Missouri
I am fixing to install my 200 amp breaker box in my new shop, the question I have is this considered a sub panel or main since I have the meter base with a built in 200 amp milbank breaker on the pole? Reason is I’m trying to figure out if I bond or not in the breaker box in the shop.
 
To avoid these ads, REGISTER NOW!

Jlarson

Well-known member
Joined
Mar 27, 2015
Messages
738
Location
AZ
Your bond should be in the meter/main on the pole, four wire feeder to building.
 
OP
C

CJseven

Well-known member
Joined
Mar 4, 2007
Messages
344
Location
Southeast Missouri
Thank you, that’s what I thought I was understanding from the reading I’ve been doing. I guess i will have to get a 4th wire, I have a roll of triplex already.
 
OP
C

CJseven

Well-known member
Joined
Mar 4, 2007
Messages
344
Location
Southeast Missouri
I was going to direct bury, but have decided to use the pvc conduit this time.

As for the wire it’s sweetbrier 4/0-4/0-2/0
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I was going to direct bury, but have decided to use the pvc conduit this time.

As for the wire it’s sweetbrier 4/0-4/0-2/0

That wire is UD and is only rated as USE-2 so it is not allowed to enter the structure and needs to be terminated outside. Sweetbrier is just the code name for the size of the UD cable.
 
To avoid these ads, REGISTER NOW!

nsula_country

Well-known member
Joined
May 23, 2013
Messages
1,534
Location
Northwestern Louisiana
That wire is UD and is only rated as USE-2 so it is not allowed to enter the structure and needs to be terminated outside. Sweetbrier is just the code name for the size of the UD cable.

Clarify this. If panel is on inside wall, conduit through wall into panel, is the URD/USE-2 "inside" the structure?

CT
 

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
Clarify this. If panel is on inside wall, conduit through wall into panel, is the URD/USE-2 "inside" the structure?

CT
Yes, that's considered inside the structure. To use the URD cable, you would have to install a junction box on the outside of the shop, and splice the URD with a different kind of wire that's suitable for inside use, then run that wire the rest of the way to the panel.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Clarify this. If panel is on inside wall, conduit through wall into panel, is the URD/USE-2 "inside" the structure?

CT

I know there are sometimes things in code that aren't obviouszbut why wouldn't you consider it inside the structure when you are penetrating the exterior? How else would you describe it?
 

nsula_country

Well-known member
Joined
May 23, 2013
Messages
1,534
Location
Northwestern Louisiana
I know there are sometimes things in code that aren't obviouszbut why wouldn't you consider it inside the structure when you are penetrating the exterior? How else would you describe it?

Its inside a conduit and inside the load center.

Inside the structure would be exposed or within the structure walls or attic.

It was once explained to me that if it was in listed conduit or enclosure it was acceptable and not "inside the structure". (ie: ****** thru exterior wall to load center lugs and dead front installed)

If it had to run through a space to get to load center w/o conduit, then it required SE cable.

I have been incorrect before and do not want to cloud anyone's decisions if this is incorrect.

CT
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,275
Location
Modesto, CA
Its inside a conduit and inside the load center.

Inside the structure would be exposed or within the structure walls or attic.

It was once explained to me that if it was in listed conduit or enclosure it was acceptable and not "inside the structure". (ie: ****** thru exterior wall to load center lugs and dead front installed)

If it had to run through a space to get to load center w/o conduit, then it required SE cable.

I have been incorrect before and do not want to cloud anyone's decisions if this is incorrect.

CT

The way it was explained to me is that the conduit doesnt change the insulation rating nor does the conduit stop fire.

If fire got inside the pipe the insulation would still burn because it is not fire resistant rated.
 