I tried searching for answer to this but could not find on here - My outlets will be 45" off the concrete floor. As of 20 minutes ago I have been told they need to be Tamper Resistant when before I was told they do not need to be. Which is correct?
Thanks for your input, it is much appreciated.
the requirement is 5.5' to skip on TR:
All nonlocking type 15A and 20A, 125V receptacles in the following areas of a dwelling unit [210.52] must be listed as tamper-resistant [406.12].
Wall space — 210.52(A)
Small-appliance circuit — 210.52(B)
Countertop space — 210.52(C)
Bathroom area — 210.52(D)
Outdoors — 210.52(E)
Laundry area — 210.52(F)
Garage and outbuildings — 210.52(G)
Hallways — 210.52(H)
Exception: Receptacles in the following locations aren’t required to be tamper-resistant:
Receptacles located more than 5½ ft above the floor.
Receptacles that are part of a luminaire or appliance.
A receptacle located within dedicated space for an appliance that in normal use isn’t easily moved from one place to another.
Nongrounding receptacles used for replacements as permitted in 406.4(D)(2)(a).
Nonlocking type 15A and 20A, 125V receptacles in guest rooms and guest suites must be listed as tamper-resistant [406.13]. In addition, nonlocking type 15A and 20A, 125V receptacles in child care facilities must be listed as tamper-resistant [406.14].
took about a 2 second google search to get that result.