Meter base to Breaker Box HELP!!!

carycooke

New member
Joined
May 2, 2016
Messages
1
Ok so I am new to electrical but I am trying to pass inspections on a limited budget but I have a Electrician trying to help me and he said attached picture will not pass because to much un fused wire from meter base but it would be ok to do that on the outside of the building? I do not understand that anyways because the length of wire will be the same and I have done drilled the hole for the meter base at the specified height of 5'6" to center of base and the Breaker box is at 6' to top like my electrician asked for so there is no other way on height restraints to do it. He said I can stay under 6ft with breaker box. My question is how else could I do it if I ran it straight from the back of the meter base into the back of breaker box it will put it ether really low or way to high up.
view
 

Attachments

  • 20181014_154459.jpg
    20181014_154459.jpg
    81.7 KB · Views: 133
To avoid these ads, REGISTER NOW!

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,536
Location
Minneapolis
Here's how I would have done it...assuming your service conductors outside the building are underground, come up into the bottom of the meter base, then out the top, through the wall, and directly into the panel through one of those knockouts at the top. I'm not sure why you came into the building that low and then mounted the panel over to the side.










attachment.php
 

Attachments

  • service entrance.jpg
    service entrance.jpg
    24.1 KB · Views: 178

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,279
Location
Modesto, CA
Many AHJs have rules about max length of unfused wire inside the building.

I definitely wouldve done that differently.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,796
:thumbup::thumbup::thumbup::thumbup:
As a side note we're allowed no more than 10' between meter socket and main around here before you need an extra disconect.


Some only allow 5', the OP would have been better served to have run it on the outside of the building.
 