Short version: 1970s Thermopride gas furnace with later addition AC. Fan limit switch constantly hits upper limit. I suspect the problem is too little airflow but fan hardware is either original or mfr specified replacements. Opening up blower intake side of furnace box doesn't solve flow issue. Pressure readings just below AC coils seems low based on what I have found on the web (I don't 100% trust my methods). What might be my issue?
The rambling version.
I'm hoping people here might help me diagnose an issue with my home furnace. This thing has given me trouble since I moved into the house but I suspect the issues are not fundamental but instead due to previous service mistakes. I talked about one of those here from spring 2017.
https://www.garagejournal.com/forum/showthread.php?t=363590
The furnace has been in the house since the late 70s. I'm not sure when the AC was added but it's an R-22 unit so I think that means no later than the 90s. The current issue I'm seeing is the fan limit switch on the gas heat constantly hits the over temp limit. The switch is a Honeywell similar to the one in this article. [[https://inspectapedia.com/heat/Fan_Limit_Switch_Guide.php]]
I suspect the fan isn't pushing enough air but I can't understand why.
The motor was replaced recently (though I suspect the old one was fine). Last summer I pulled the blower out and cleaned likely 30+ years of dust off the housing and squirrel cage blower. At that time I also oiled the fan bushings (the service manuals says do this yearly... I suspect it wasn't serviced for many years). So I have a cleaned fan with a new (and verified correct model) motor. The only issue I could think of here is bearings but they don't feel bad to my untrained hands.
So could it be ducts? We the house seems to have a well designed duct system that scales in cross sectional area as lines are run off to air outlets. The return system is distributed throughout the house. To verify the problem wasn't on the return air side I removed the fan housing cover and pulled the air filters. At that point air can come directly from the room. I can't easily verify the outgoing ducts aren't blocked other than opening the duct that is right above the AC coils. That one doesn't feel stupidly strong as I might expect if there was a blockage down stream. Also, the system branches almost immediately after the furnace so a blockage in one line wouldn't impact several others. The same is true of the return lines.
I tried taking some air pressure readings across the blower fan (after the furnace but before the AC coils and after the AC coils). I don't recall the exact numbers but recall they were about 1/3rd of what people said I should see based on random web searches (general numbers, not specific to my system).
I would happily spend a few hundred dollars for a new blower if I knew that was the issue. I feel like this problem would either be blower related, duct related or AC coil blocking things. If the issue were blocked coils or duct work then I think I should see a greater pressure difference across the fan (did these older systems operate at a lower pressure?). If the problem is fan related I can't understand why since the motor is new, and the blower was cleaned and oiled.
Anyway, I would love to know what the experts think. I don't want to spend $7k on a new system just because of this issue.
Thanks!
Other background:
When I first bought the house the fan was staying on when using the heat. Since the house came with a warranty I used the warranty people for repairs. They replaced the fan limit switch but in the process screwed up the AC fan relay. Hence the next spring the AC didn't work because the relay was connected in a way that shorted AC power. As part of this screwy repair process they replaced the fan motor but they also screwed that up. The fan motor can be revered based on wiring. The guy didn't check the wiring and thus the blower was running backwards and my AC was icing over. I figured that out as well as sorting out the incorrectly wired relay. At least I'm learning how all this **** works.
The rambling version.
I'm hoping people here might help me diagnose an issue with my home furnace. This thing has given me trouble since I moved into the house but I suspect the issues are not fundamental but instead due to previous service mistakes. I talked about one of those here from spring 2017.
https://www.garagejournal.com/forum/showthread.php?t=363590
The furnace has been in the house since the late 70s. I'm not sure when the AC was added but it's an R-22 unit so I think that means no later than the 90s. The current issue I'm seeing is the fan limit switch on the gas heat constantly hits the over temp limit. The switch is a Honeywell similar to the one in this article. [[https://inspectapedia.com/heat/Fan_Limit_Switch_Guide.php]]
I suspect the fan isn't pushing enough air but I can't understand why.
The motor was replaced recently (though I suspect the old one was fine). Last summer I pulled the blower out and cleaned likely 30+ years of dust off the housing and squirrel cage blower. At that time I also oiled the fan bushings (the service manuals says do this yearly... I suspect it wasn't serviced for many years). So I have a cleaned fan with a new (and verified correct model) motor. The only issue I could think of here is bearings but they don't feel bad to my untrained hands.
So could it be ducts? We the house seems to have a well designed duct system that scales in cross sectional area as lines are run off to air outlets. The return system is distributed throughout the house. To verify the problem wasn't on the return air side I removed the fan housing cover and pulled the air filters. At that point air can come directly from the room. I can't easily verify the outgoing ducts aren't blocked other than opening the duct that is right above the AC coils. That one doesn't feel stupidly strong as I might expect if there was a blockage down stream. Also, the system branches almost immediately after the furnace so a blockage in one line wouldn't impact several others. The same is true of the return lines.
I tried taking some air pressure readings across the blower fan (after the furnace but before the AC coils and after the AC coils). I don't recall the exact numbers but recall they were about 1/3rd of what people said I should see based on random web searches (general numbers, not specific to my system).
I would happily spend a few hundred dollars for a new blower if I knew that was the issue. I feel like this problem would either be blower related, duct related or AC coil blocking things. If the issue were blocked coils or duct work then I think I should see a greater pressure difference across the fan (did these older systems operate at a lower pressure?). If the problem is fan related I can't understand why since the motor is new, and the blower was cleaned and oiled.
Anyway, I would love to know what the experts think. I don't want to spend $7k on a new system just because of this issue.
Thanks!
Other background:
When I first bought the house the fan was staying on when using the heat. Since the house came with a warranty I used the warranty people for repairs. They replaced the fan limit switch but in the process screwed up the AC fan relay. Hence the next spring the AC didn't work because the relay was connected in a way that shorted AC power. As part of this screwy repair process they replaced the fan motor but they also screwed that up. The fan motor can be revered based on wiring. The guy didn't check the wiring and thus the blower was running backwards and my AC was icing over. I figured that out as well as sorting out the incorrectly wired relay. At least I'm learning how all this **** works.