1. In a single phase and 3-phase system, are branch circuit neutrals considered CCC's? NEC is quite vague on this.
2. A friend of mine intends to surface mount a 42 pole sub-panel in a finished
commercial garage and use wiremold as a raceway. A conversation came up about maximum number of circuits in a raceway (NEC 376.22) as 30 CCC's in a particular cross section. Hypothetically, does this rule limit to 15 circuits, considering neutrals as CCC's?
wyliesdiesels
Modesto, CA
1. yes a neutral is a CCC by definition. need to read the definition in article 100
2. i think youre skipping the first part of that code which says that adjustment factors in 310.15(B)(3)(a) are only applied when the number of CCC exceeds 30 at any cross section of the wireway.
I see no circuit limiting factor in that code section and not every circuit has a neutral.
klassenl
Southern Alberta
The neutral on a three wire, single phase circuit is not counted as a current carrying conductor and the neutral on a 4 wire, 3 phase circuit is not counted as a current carrying conductor.
klassenl
Southern Alberta
...if the loads are linear. With non linear loads (computers, motors, ballasts etc) on Wye systems have to be counted.