90A is the max size not 100A. Permitted ampacity is reduced to limit voltage drop to approx 3%.
You said that like it was a Code Requirement.
90A is the max size not 100A. Permitted ampacity is reduced to limit voltage drop to approx 3%.
I upsized the wire because of the voltage drop. I used 3% and 75C.
My Dad did the calculations and said I could probably get away with #3AWG, but because of the distance, #2AWG would be a better choice.
You said that like it was a Code Requirement.![]()
Nope. I said it as a smart design requirement based upon the existing stated distance...
How so? The code enforces smart design requirements that are scientifically based on safety. There is nothing inherently unsafe about the voltage drop of the circuit at 100A. And tripping the breaker is not a good cure to the voltage drop issue. The right answer is to plan out your wire for the intended loads.
...Allowing any larger cb than 90a will permit the feeder to deliver lower than recommended voltage to the loads. You don’t know what the supply voltage is and can’t assume it is always 120/240v. What if it is 110/220v at the pole? A 5% loss between pole and loads provides for 104/209v at the loads. Low voltage conditions do nothing to promote equipment life or adequate performance...
just to add.A circuit breaker is not a magical device that holds the load below 90A. You're saying that if the voltage drops, without actually encountering a dangerous situation, it is preferable to shut off the power. I'm saying that that's a nuisance trip.
The code allows you to plug a 100' 16 gauge extension cord into a 20A outlet. And there's nothing to stop you from running a heat gun or 18A miter saw on that cord. Should outlets that might have extension cords plugged in have lower rated breakers in them?
Breakers are simple safety devices that protect the wiring. They are NOT control devices that protect the devices plugged into them. That control must be done at the load-calc and device level.
How many times can a guy use you and your in a post?You're putting words in the NEC that aren't there, mm08822.
VD isn't enforceable.
You know that, and used poor word choice saying it isn't "permitted." Then your argument morphed into saying "the code is a minimum, this is actually just good design using a 90."
Your posts are misleading.
Everyone makes mistakes, including myself, but it appears not everyone can admit when they make them.
just to add.
I need to figure out how to cut on my phone,, but the breaker only protects the wire on a general circuit (with a couple of exceptions) it also can/does protect against fault within connected equipment.
Proper terminology is minor.
You're putting words in the NEC that aren't there, mm08822.
VD isn't enforceable.
You know that, and used poor word choice saying it isn't "permitted." Then your argument morphed into saying "the code is a minimum, this is actually just good design using a 90."
Your posts are misleading.
Everyone makes mistakes, including myself, but it appears not everyone can admit when they make them.
A circuit breaker is not a magical device that holds the load below 90A. You're saying that if the voltage drops, without actually encountering a dangerous situation, it is preferable to shut off the power. I'm saying that that's a nuisance trip.
It is a way to enforce the vd correction applied to a feeder at the time of design. You design it for x and it eventually trips above x. Proper voltage level delivered or it is not. I’m fine with that.
The code allows you to plug a 100' 16 gauge extension cord into a 20A outlet. And there's nothing to stop you from running a heat gun or 18A miter saw on that cord. Should outlets that might have extension cords plugged in have lower rated breakers in them?
We’re talking about permanent building wiring properly sized to deliver expected voltage at the point of connection. That’s where it ends. Stupid people tricks out of scope.
Breakers are simple safety devices that protect the wiring. They are NOT control devices that protect the devices plugged into them. That control must be done at the load-calc and device level.
Aceman,
Since you and others interpreted my use of the word “permitted” as meaning “permitted by code” without fully understanding the intent

A guy told me that a poco engineer said there was no such thing as number 2 alum wire,,,