Looking for some input and validation of my hydronic heat system planning. Now that my barn has been up for a little while and the floor has been poured with pex circuits installed, I am looking to install the heat.
Here are details of the project:
Metal clad inside and out pole building, area to be heated is 60x64x16 feet with an unheated area 24’ wide attached on one of the 64’ sides (horse stalls). The slab is 5” min. with 2” R-10 insulation underneath and on the perimeter extending down 24” min. Walls are R-19 with house wrap on outside and Visqueen lined inside, ceiling is insulated to R-40+.
An online heat loss calculator gave 50,069 Btu/HR @ 0.35 Ach and 60,851 Btu/HR @ 0.5 Ach. The design temperatures were 0- and 65-degrees Fahrenheit for outside and indoor temps respectively. I believe the heat loss values are a little high due to the 64’ side with the attached unheated room acting as a buffer to outside temps, therefore I am using the 50,069 Btu/HR figure for heating design.
The 60x64 area has 11-300’, ½ pex circuits to a 11-circuit stainless manifold. The pex is placed at or just below middle of the 5” concrete slab. There is also a concrete pad outside the north end of the unheated horse area that will not see direct day light in the winter months with 1 circuit approximately 150’ of ½ pex encased, to clear icing when needed (measurable snow will be removed manually). Dhw required for two sinks and occasional car and horse washing.
For a heat source I have ordered a Westinghouse/HTP UFTC-140WLP combi boiler. I intend to have 1 in. pri/sec loops utilizing Webstone’s 1-1/4" Run x 1" Hydro-Core to interconnect the loops. I see four options for the outdoor slab loop, all installed on the return side of indoor secondary loop: 1. Connect with Webstone’s 1 x 3/4" Primary / Secondary Loop Purge Tee, partially closing the valve just enough to get a small pressure differential between the two sides to get adequate flow to heat pad when needed, 2: Connect with Webstone’s 1 x 3/4" Loop Purge Tee utilizing a small circulator on that loop, 3: Use a heat exchanger and isolate the indoor from out door, 4: use a diverter valve. My thoughts on the three options are: Option 1 would require a higher ratio of antifreeze in entire system and would slightly increase head pressure in system when using the valve. Option 2 adds the cost of a second pump, which may help in selecting the sec. loop pump. Option 3 adds the cost of a second pump and heat exchanger but allows for reduced antifreeze use in indoor heat system. Option 4 diverter valve is costly. Currently considering option 1 with the thoughts that a second pump could be added in if using the valve represents a problem. This loop would not be needed often, but when it is needed it will be worth the effort to prevent injury to any of the horses.
As for sec. circulator, I have calculated that on design day I will need about 0.52-0.78 gpm per circuit for a 19-12.5 deg. drop at 90.3-85.9*F supply temp. respectively (86*F is min. CH setpoint). Nibco’s 0.5 in. pex specifications give 1.0 gpm of water through 300 feet a head loss of 11.07, which changes to 13.18 at 30% pg. Since design gpm range is 0.5-0.8 with correlating head loss of roughly 6.59-10.54 with 30% pg. For circulator selection I am using parameters in the middle at 8.6 ft of head and 7.2 gpm, aiming for a 15*F delta between input/output temps. Using Grundfos selector these values fall just outside of 2nd speed of UPS 15-58 FC – 5989634, the H-10.54, Q-8.58 calculated values land on the high-speed setting as well.
This is where I am at in the design, I appreciate any input on whether I have made any mistakes, wrong assumptions or on the right track.
Here are details of the project:
Metal clad inside and out pole building, area to be heated is 60x64x16 feet with an unheated area 24’ wide attached on one of the 64’ sides (horse stalls). The slab is 5” min. with 2” R-10 insulation underneath and on the perimeter extending down 24” min. Walls are R-19 with house wrap on outside and Visqueen lined inside, ceiling is insulated to R-40+.
An online heat loss calculator gave 50,069 Btu/HR @ 0.35 Ach and 60,851 Btu/HR @ 0.5 Ach. The design temperatures were 0- and 65-degrees Fahrenheit for outside and indoor temps respectively. I believe the heat loss values are a little high due to the 64’ side with the attached unheated room acting as a buffer to outside temps, therefore I am using the 50,069 Btu/HR figure for heating design.
The 60x64 area has 11-300’, ½ pex circuits to a 11-circuit stainless manifold. The pex is placed at or just below middle of the 5” concrete slab. There is also a concrete pad outside the north end of the unheated horse area that will not see direct day light in the winter months with 1 circuit approximately 150’ of ½ pex encased, to clear icing when needed (measurable snow will be removed manually). Dhw required for two sinks and occasional car and horse washing.
For a heat source I have ordered a Westinghouse/HTP UFTC-140WLP combi boiler. I intend to have 1 in. pri/sec loops utilizing Webstone’s 1-1/4" Run x 1" Hydro-Core to interconnect the loops. I see four options for the outdoor slab loop, all installed on the return side of indoor secondary loop: 1. Connect with Webstone’s 1 x 3/4" Primary / Secondary Loop Purge Tee, partially closing the valve just enough to get a small pressure differential between the two sides to get adequate flow to heat pad when needed, 2: Connect with Webstone’s 1 x 3/4" Loop Purge Tee utilizing a small circulator on that loop, 3: Use a heat exchanger and isolate the indoor from out door, 4: use a diverter valve. My thoughts on the three options are: Option 1 would require a higher ratio of antifreeze in entire system and would slightly increase head pressure in system when using the valve. Option 2 adds the cost of a second pump, which may help in selecting the sec. loop pump. Option 3 adds the cost of a second pump and heat exchanger but allows for reduced antifreeze use in indoor heat system. Option 4 diverter valve is costly. Currently considering option 1 with the thoughts that a second pump could be added in if using the valve represents a problem. This loop would not be needed often, but when it is needed it will be worth the effort to prevent injury to any of the horses.
As for sec. circulator, I have calculated that on design day I will need about 0.52-0.78 gpm per circuit for a 19-12.5 deg. drop at 90.3-85.9*F supply temp. respectively (86*F is min. CH setpoint). Nibco’s 0.5 in. pex specifications give 1.0 gpm of water through 300 feet a head loss of 11.07, which changes to 13.18 at 30% pg. Since design gpm range is 0.5-0.8 with correlating head loss of roughly 6.59-10.54 with 30% pg. For circulator selection I am using parameters in the middle at 8.6 ft of head and 7.2 gpm, aiming for a 15*F delta between input/output temps. Using Grundfos selector these values fall just outside of 2nd speed of UPS 15-58 FC – 5989634, the H-10.54, Q-8.58 calculated values land on the high-speed setting as well.
This is where I am at in the design, I appreciate any input on whether I have made any mistakes, wrong assumptions or on the right track.