I've been poring over posts and research and I think I've got all my bases covered for installing the electrical run from my main panel to my new detached garage. I wanted to post my plans and get a sanity check from the group before I purchased anything. Plan thus far:
125A breaker in my 200A main panel. 1/0 CU THWN in conduit from the main panel through the basement ceiling running 25' across the house and exiting ~6' above grade. 2" PVC LB exiting the brick exterior into Sch 80 PVC down into a 24" trench. 90 degree sweep into ~175' of schedule 40 PVC across my entire yard in a 24" trench. Enters the garage via a 90 degree sweep that's fully grouted into the garage foundation. 125A main breaker panel in the garage. Anyone see any potential red flags?
125A breaker in my 200A main panel. 1/0 CU THWN in conduit from the main panel through the basement ceiling running 25' across the house and exiting ~6' above grade. 2" PVC LB exiting the brick exterior into Sch 80 PVC down into a 24" trench. 90 degree sweep into ~175' of schedule 40 PVC across my entire yard in a 24" trench. Enters the garage via a 90 degree sweep that's fully grouted into the garage foundation. 125A main breaker panel in the garage. Anyone see any potential red flags?