I am going to wire my 50x50 steel building using 3/4" EMT. My question is the building has 6 - I beam main frame supports, one on each corner and one on each side in the middle. The base of the building has a base angle running along the floor, one 8" purlin 7' above the ground, and then one at the top.
I was planning on attaching the conduit and outlet boxes to the middle purlin on the building but I did not realize it was going to be 7' off the ground.
Any ideas? 7' high outlets do not seem like a good idea neither does putting them all the way down on the floor. My I beams are 25' apart so the emt can't span that without support.