The pex splitting like copper has been my experience. The shop where I work was built in 1998. The Ingersoll Rand compressor charges all the pex lines to 175 max six days a week since then. It is shut off and the tank drained each night. All the lines are zip tied to the steel ceiling beams where the air hose reels hang except for three drops, one to a work bench in the middle of the shop, and two drops to two of the lifts which have air release safety locks. After 18 years in constant use the drops to both lifts failed this year months apart.
Both lines made a loud pop and split about 4-5" long. Each line or drop coming off the main line has a shut off so we were able to shut the lines off until repair could be made with minimal down time to the rest of the shop. Both the splits happened where the pex ran within 6-8" of the fluorescent lighting. When we cut out the broken pieces they felt brittle as described above a foot or so on each side of the split but the rest of the lines felt like normal pex.
We spliced in a new two foot section of pex with a rubber heater hose slipped over it to protect from uv off the fluorescent lights. Even with the pex crumbling and brittle it literally split like a copper pipe does when it freezes with no shrapnel.
After seeing this system in use daily I ran my personal garage with pex as well with no worries.
Sent from my XT1254 using Tapatalk
Just to be clear this is Pex not PexALPex correct? Good to know either way. If I use PEX I'll keep it away from the lights.
Thanks