I am trying to help son who spends all his money on hunting and stays too broke to fix things right
The resistance heat is powered by a 50 amp double pole Murray breaker through 6ga copper nm-b. The furnace has an internal 60 amp breaker so I assume it should have been powered by a bigger wire and 60 amp breaker. Some jake leg sold and installed this as a surplus’s unit for a very low price to replace a unit that ran off the 50 amp service.
But it ran for a couple of years with an occasional breaker pop my son say once or twice a season. This year it has become more of a nuisance of coming home to a cold house, because heat pump also will be off due to no power to blower or and thermostat.
My question, — my thinking was to install a 55 amp breaker to help this border line situation since the wire is rated at 55 amps. But I cannot find a 55 amp breaker.
The breaker itself could be going bad but if I replace it I would want a 55 amp if such exists in a Siemens or Murray, maybe cutler hammer equivalent.
But last of all would you dare put a 60 amp in there. I can’t believe I said that. Furnace is about 15 feet from main panel and wire is in open air except for about 2 feet exiting panel.
The resistance heat is powered by a 50 amp double pole Murray breaker through 6ga copper nm-b. The furnace has an internal 60 amp breaker so I assume it should have been powered by a bigger wire and 60 amp breaker. Some jake leg sold and installed this as a surplus’s unit for a very low price to replace a unit that ran off the 50 amp service.
But it ran for a couple of years with an occasional breaker pop my son say once or twice a season. This year it has become more of a nuisance of coming home to a cold house, because heat pump also will be off due to no power to blower or and thermostat.
My question, — my thinking was to install a 55 amp breaker to help this border line situation since the wire is rated at 55 amps. But I cannot find a 55 amp breaker.
The breaker itself could be going bad but if I replace it I would want a 55 amp if such exists in a Siemens or Murray, maybe cutler hammer equivalent.
But last of all would you dare put a 60 amp in there. I can’t believe I said that. Furnace is about 15 feet from main panel and wire is in open air except for about 2 feet exiting panel.