10 gauge 15A breaker?

machsnell

Well-known member
Joined
Jun 12, 2010
Messages
942
Location
Northern Virginia
I have some old 10 gauge 3 wire that was run to an outside pool pump. No more pump and not going outside.

Can I tap into it and run 14 UF to outside lights and put it on a 15A breaker?

So I would have 10ga coming out of the panel to 14 ga in jb. One leg switched to lights and the other leg to outlet (15A). Share neutral and ground.

This kosher?

Sent from my SM-G960U using Tapatalk
 
To avoid these ads, REGISTER NOW!

xyster101

Well-known member
Joined
Jul 3, 2013
Messages
640
Location
Upstate NY
Yes you can under code, but there are good reasons that you might not want to. Google search 3-wire circuit and do some reading.

What are the "good" reasons not to?

You can use each hot on it's own circuit as long as they are alternating voltage (AKA breakers are above and below each other in the panel).

You must always put the breaker size for the smallest wire you are using. That will be 14 awg in your case, so the 15amp breaker is good. You can always put a smaller breaker on wire, never put a larger one.
Make sure to use a proper slice kit to connect the 14 awg to the 10 awg. Either a waterproof box that is accessible or you can get a burial rated splice kit at HD for about $15 to connect the 10 to the 14s.
 

TRWham

Well-known member
Joined
Aug 11, 2017
Messages
1,970
Location
East Cobb County, Georgia
If you are running a multi-wire branch circuit (MWBC) with the light(s) on one leg and the receptacle on the other, then, yes, you can install a 2 pole 15A circuit breaker (or 2 single poles with a handle tie) and use the existing cable. The fact that the cable is oversized is not a problem.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
Might be a good idea but not required to mark, that there are smaller conductors on the circuit so some doofus does not slap a 30A breaker on it in the future, it is a "what if" so take it as that. Otherwise I see no problem.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
If this circuit is direct buried depending on the depth (12" to less than 18") it may require GFCI protection at the source. Another issue is if making it a MWBC it will have 240V potential across the hots and must be buried at least 18 inches if in conduit, 24" if direct bury. The 12" direct bury is limited to 120V 20A circuits with GFCI protection from the source.
 
Last edited:

TRWham

Well-known member
Joined
Aug 11, 2017
Messages
1,970
Location
East Cobb County, Georgia
Is the existing cable 10/3 with ground or 10/2 with ground? If only 3 wires total, it would not work for an MWBC after all. As for the voltage, I was assuming it was already 240V and installed to code. That it is now serving an MWBC should not change any requirements related to line to line voltage.
 
Last edited:

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
One thing I did not notice in the original post until now was the part sharing neutral and ground this is not code compliant.
 

TRWham

Well-known member
Joined
Aug 11, 2017
Messages
1,970
Location
East Cobb County, Georgia
One thing I did not notice in the original post until now was the part sharing neutral and ground this is not code compliant.

I have the same concern. First read it as there would be a separate ground and neutral shared by the 2 legs, but now I am not sure. I don't know why there would have been 4 wires run to the pump, so now think it's only 10/2, so no joy on the MWBC. May be simpler just to keep it together on a single 20A.
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
Well, I interpreted what he was asking as something different than all of you. I think everyone is thrown off by his use of "3-wire". This is normally considered a romex cable with 2 hots and a neutral, the ground isn't counted. I think he is referring to a 2-wire cable, one hot, one neutral, but he is counting the ground. If I'm right, then he's not talking about a MWBC at all and is just going to attach a normal 120v circuit to a single pole 15A breaker. In which case there's no issue with OP's plan of using the 10awg spliced to 14. The only thing that makes me not certain of this is he says "one leg here" and "one leg there", implying 2 circuits, but he may just be referring to the circuit being split in 2 directions. We shall see....
 
To avoid these ads, REGISTER NOW!
OP
M

machsnell

Well-known member
Joined
Jun 12, 2010
Messages
942
Location
Northern Virginia
Sorry gents out in snow plow action.

It is a 10/3 romex. Red blck neutr and grnd.

It's in the basement and goes to a jb where it splits to 14 uf wire to lights and another 14 uf wire to lights. They are both buried once they leave the basement wall.

My main concern was if it was ok to use the 10 ga wire in a 15A circuit w 15A breaker.

Secondary and not totally needed but would install an outlet or 2 off the unused leg (red).

If I use a tied together 2 pole 15A breaker is it ok or no go?

Yes they share a neutral and ground.

Sent from my SM-G960U using Tapatalk
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
What about GFCI protection for the #14 that's buried? Do you know if it buried deep enough not to require GFCI protection?
 
OP
M

machsnell

Well-known member
Joined
Jun 12, 2010
Messages
942
Location
Northern Virginia
Got it. Tied together breakers.

Line is buried 12 to 18" and comes up to go up the trees 50 feet.

What does the gfi do for the circuit anyway? I can add pretty easily if better.

Sent from my SM-G960U using Tapatalk
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Got it. Tied together breakers.

Line is buried 12 to 18" and comes up to go up the trees 50 feet.

What does the gfi do for the circuit anyway? I can add pretty easily if better.

Sent from my SM-G960U using Tapatalk

GFI protects anyone from shoving a shovel in the ground and getting a surprise when its buried at 12", but that only applies to 120V 20A circuits or less. Since its on a double breaker the minimum direct bury depth needs to be 24", not 12 to 18". Minimum 18" bury depth is when the wire is run within conduit.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
GFI breaker does not satisfy the NEC because it's more than 120V. Not sure if you are worried about code or not, but 2" of concrete on top of the wire satisfies NEC depth requirement to only be 6" and no GFI breaker required.
 