Sec. 8-238. Classification of wiring methods and materials.
The type of wiring used in buildings of various types of construction and occupancy shall be as follows:
(a) In the installation of new electrical wiring and/or equipment, wire shall be installed in metal raceways of the type approved for the location. Flexible metal conduit shall be permissible only in short lengths where flexible connections are necessary or by special permission.
Exception No. 1. In a fire-resistant building, as defined in the National Building Code of 1973, containing three (3) or more apartments or condominiums, not exceeding three (3) floors above grade and where cable will pass through holes in metal framing members, Type NM, NMC cable of the grounded type or flexible metal conduit shall be permitted to be used in concealed locations. Type NM, NMC cable shall not be permitted to be used in air plenums or exposed areas.
Exception No. 2. In any residential building not exceeding three (3) floors above grade or twelve (12) units, apartments or condominiums, Type NM, NMC cable of the grounded type or flexible metal conduit shall be permitted to be used in concealed locations. Type NM, NMC cable shall not be permitted to be used in air plenums or exposed areas.
In multilevel one-and two-family dwellings an empty three-fourths-inch metal conduit shall be installed to the attic and crawl space.
In a single or two-level one-and two-family dwelling with a basement an empty three-fourths-inch metal conduit shall be installed to the attic.
In a single level one-and two-family dwelling without a basement an empty three-fourths-inch metal conduit shall be installed to the attic and crawl space.
(b) In the installation of cable through wood frame members:
(1) Bored holes. In concealed locations where a cable type wiring method is installed through bored holes in joists, rafters, studs or similar structural wood members, holes shall be bored at the approximate center of the member but not less than one and one-half (1 1/2) inches from the nearest edge or shall be protected from nails and screws by a steel plate one-sixteenth of an inch thick.
(2) Cable shall be protected from physical damage where necessary by conduit. Where passing through a floor the cable shall be enclosed in metal conduit extending six (6) inches above the floor.
(3) Cable shall be secured by straps so designed and installed as not to injure the cable. Straps shall be installed every five (5) feet and within twelve (12) inches of a box or cabinet.
(4) The installation of cable in accessible attics or roof spaces. If run across the top of the floor joists the cable shall be installed as close to the point where the roof meets with the attic floor joists as possible, or holes may be bored in the center of floor joists for the cable to pass through. Where cable runs parallel to the joists, the cable shall be secured to the side or face of the joists.
(c) In the installation of cable through metal framing members: In concealed locations where cable passes through slots or holes in metal framing members, the cable shall be protected by bushings or grommets, approved for the purpose, securely fastened in the opening. Where nails or screws are likely to penetrate the cable, a steel sleeve not less than one-sixteenth-inch in wall thickness shall be used to protect the cable.
(d) Remodeling of existing structures:
(1) In any building other than in fire-resistant buildings of the type listed above in Exception No. 1, and residential buildings as listed above in Exception No. 2, the wiring shall be installed in metal raceways of the type approved for the location. Flexible metal conduit may be run or fished in air veins of concrete masonry block or tile walls where such walls are not subject to dampness; flexible metal conduit may be run or fished in existing walls or partitions where it is not possible to install conduit; flexible metal conduit may run in existing floors or ceilings where it is not possible to install conduit; flexible metal conduit shall never be used in buildings or parts of buildings being remodeled where it would be subject to mechanical injury; flexible metal conduit may be used in existing partitions where it is fished through the partition; and flexible metal conduit shall not be used between outlets in new partitions where the exterior finish of the partition has been removed for remodeling.
(2) In a fire-resistant building(s) of the type listed above in Exception No. 1, and in residential buildings as listed in Exception No. 2, concealed wiring may be installed in metal rigid conduit, flexible metal conduit or nonmetallic sheathed cable of the grounded type where the conductor is concealed. Metal rigid conduit shall be required for all exposed wiring.
(Ord. No. 6554, § 8.3, 10-5-76; Ord. No. 7456, § 3(C), 1-6-81)
Sec. 8-239. Extensions.
Where a building, structure, area or enclosure has been previously wired in complete metallic wiring, no nonmetallic circuit extensions will be permitted, irrespective of class of wiring required by occupancy or location.
(Ord. No. 6554, § 8.4, 110-5-76; Ord. No. 7456, § 3(C), 1-6-81)