Kitchen: recommended appliance circuits

Lightman 1

Active member
Joined
Apr 20, 2019
Messages
25
Location
England Ar
Back when I wired houses I put all 240 volt appliances on their own circuit. Every major 120 volt appliance got its own circuit. Things like the refrigerator, ice maker, dish washer, compactor, ect. I would run #12 to them but would use a 15 amp breaker. The counter tops would get a minimum of 2 circuits that were independent from anything else. This depended on how the counters were laid out, there may have been more. Minor loads like the vent-a-hood might come off of the fridge or dishwasher circuit. I would usually put the lighting on the circuit with the few general purpose outlets not involving the appliances.
 
To avoid these ads, REGISTER NOW!

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
Back when I wired houses I put all 240 volt appliances on their own circuit. Every major 120 volt appliance got its own circuit. Things like the refrigerator, ice maker, dish washer, compactor, ect. I would run #12 to them but would use a 15 amp breaker. The counter tops would get a minimum of 2 circuits that were independent from anything else. This depended on how the counters were laid out, there may have been more. Minor loads like the vent-a-hood might come off of the fridge or dishwasher circuit. I would usually put the lighting on the circuit with the few general purpose outlets not involving the appliances.

That's not up to code. All of the "general purpose" receptacles in a kitchen are part of a SABC, and lighting is not allowed to be on a SABC.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,674
Location
Long Island
That's not up to code. All of the "general purpose" receptacles in a kitchen are part of a SABC, and lighting is not allowed to be on a SABC.

My understanding is that ONLY countertop outlets are SABC. My kitchen has outlets behind the range and refrigerator that are not SABC (though for my purposes, I felt better having dedicated circuits for each), plus I have wall outlets away from the counter that are also not SABC.
 
To avoid these ads, REGISTER NOW!

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
My understanding is that ONLY countertop outlets are SABC. My kitchen has outlets behind the range and refrigerator that are not SABC (though for my purposes, I felt better having dedicated circuits for each), plus I have wall outlets away from the counter that are also not SABC.

No, the NEC says that ALL kitchen receptacles (with exceptions, which I will get to in a moment), as well as ALL receptacles in the pantry, breakfast nook/eating area, and dining room are part of a SABC.

The exceptions are receptacles installed for a specific appliance, such as the microwave receptacle, the receptacle under the sink for the dishwasher and/or disposal, receptacle for a range hood, 120V receptacle behind a gas range* and the fridge receptacle*. All other receptacles are part of a SABC.
* The ones marked with a * CAN be on a SABC if you want, or they can be on a dedicated circuit. The rest of the exceptions cannot be on a SABC.
 
OP
E

engineer2

Well-known member
Joined
Dec 13, 2009
Messages
11,825
Location
Chicago burbs
Just want to thank you guys for the NEC refresher course. New home run for the stove and microwave got done. The wife and I got the last of the wires pulled. Kitchen should now meet code:
20A for gas convection range
20A microwave
20A countertop outlets "A" GFCI
20A countertop outlets "B" GFCI
20A dishwasher/disposal, dead front GFCI by countertop light switches
20A refrigerator (overkill but that's what the mfr says)
15A lighting
 
Last edited: