Yet Another Garage Subpanel Question
Cruzan80
Denver, CO
After much research, I think I have figured out what I need to do for running a subpanel into my garage. But, since I am not as experienced as some on here, figured I would turn to the group for final confirmation and suggestions. Tried to bold what I think is the most relevant information. The garage is a detached structure, located about 75ft away from the house in Colorado. I am looking to add a 100a subpanel, and my main box is 200a. The main feeder is located on the exterior of my house, and I will be putting EMT conduit down from there, buried 24” in the ground from the house to the garage, and then back up the exterior of the garage, and finally thru the wall to an interior mounted subpanel. I had the main panel replaced by a licensed electrician when we moved in under a year ago, and it only has a single grounding rod.
I am going to be having the following circuits installed:
30A 240V for an electric heater (hardwired), 30A 240V for an air compressor motor (hardwired), 20A 240V for an EV charger (mine is a hybrid with an extended battery pack, can’t take advantage of higher amp chargers)(plug-in), 20A 240V for machinery (plug-in), two 20A 120V for machinery (plug-in), a 15A 120V for garage lighting and the garage opener (mix of hardwire and plug-in). At the end, I am also asking for advice on a three way circuit and how to handle it in this situation.
Questions:
Type of Cable (THWN/XHHV):
I am trying to figure out if it would be better to run THHN/THWN or XHHV between the main panel and the subpanel. Looking around, I have found a place where the difference between THWN and XHHV is under 5 cents more for the same gauge. From reading about the differences, I think XHHV would pull easier, and be more resistant long term. However, at the gauge I am using, XHHV only comes in black and green sheathing. Can someone confirm I can tape each end of the second hot red and neutral white to designate which is which? From my reading, it seems like if the wires are over #6ga, you are allowed to re-mark the ends for hots and neutrals (but not grounds).
Wire Gauge: Looking at ampacity charts, I see that I can go with #3 copper (never worked with AL) for the hot wires. I have read that I can downsize the neutral to a #4, since I have at least half of the circuits as 240V without using a neutral (I don’t need 120/240 on any of those circuits). I also understand that I can use #8 as a ground up to 100A service. So therefore I am thinking 3-3-4-8 (B-R-W-G) is correct. Suggestions?
Conduit Size: If I am going to be going with 3-3-4-8, I think I will need to be using at least 1.25” EMT, as 1” EMT is rated for no more than 3x #3ga wires. Since a #4 and a #8 added together (diameter-wise) exceed a #3, it would not allow 1” correct? Is it worth it to go up to 1.5” EMT? There will be two 90deg sweeps and a hard 90deg elbow to go inside the building, right into the panel.
Grounding Rod: Since the main panel was swapped out last year by certified electricians (former panel was a Zinsco, and we swapped it out within a week of moving in), and there is only one grounding rod (due to only seeing one copper wire coming down to a clamp, and one small pole sticking up), am I then ok following this for the grounding rod at the subpanel? Or do I need to add two rods? I have also read it is better to err on the side of caution and get a 10ft ground rod if I am going to leave a bit exposed to clamp onto, rather than an 8ft, as NEC calls for <=8ft of rod to be touching the dirt.
Load Calculation: Rather than do a traditional load calculation, I figured with me being a one-man shop, I added up the potential draws I could have at one time max (heater, compressor, car charging, 240V tool and lights) to decide on a 100A subpanel. As none of these actually draw full capacity of the breaker (heater is actually 23A, most of my 240V tools are <10A, etc), I do not think I will be exceeding the overall capacity by accident.
GFCI: Because I know a garage is a wet location, where/when do I need GFCI protection? Do I simply use a GFCI breaker at the main board, protecting everything downstream, use GFCI breakers in the subpanel or some other solution? I know I can get GFCI outlets easily for the 120V lines, but not sure for any 240V line (especially when it is hardwired).
Two circuits on duplex outlets: I am planning on running two 120V lines to all of the outlets I am putting in, having the top outlets be on one circuit and the bottoms on another. My plan is to pull 12/2 NM-b to each, and then break off the connecting hot tabs. Do I just wirenut the neutral for the top together and same for the bottom? Is it better to pigtail the ground and have three #12 into a wire nut, rather than 2 #12 under a grounding nut on the outlet?
Circuit/Spaces: Adding up what I currently see myself wiring, I come up with 11 or 12 spaces (see below for the 12th) occupied. I do want to leave a few empty spaces in case I need to add anything later. Looking around, I see that most boxes are offered in either a 12 or 20 space configuration. Is this standard, or are their sizes in between (16 space, for example)?
Bonus Extra Credit Question: WTF do I do here?
Exterior Light: Here is where it gets interesting. Right now, there is an exterior light mounted on the garage, facing the house and driveway. Currently, it is on a three way switch, with a switch inside the house and one inside the garage. From my understanding, I would need to move the circuit this is on to the subpanel, as otherwise there is a possibility of a live wire inside the detached building, even when turning off the subpanel (the exterior light is currently supplied by the main). My wife still wants this light to be able to be controlled by a switch inside the house, but doesn’t care if there is a switch inside the garage. Currently, it is powered by a direct-buried line from the house to the garage. I see myself having a couple of options. One option is to remove all wire from this circuit from the garage, and run conduit up the outside of the garage to the light. Therefore, by having it exit the ground outside the detached structure, and never enter the detached structure, it would not be subject to the subpanel. Or do circuits in conduits attached to a building still need to be supplied by the panel in that building? Second option, I move the circuit to the subpanel, route the interior garage wiring to the relevant switch and light (easy) but how do I get the access back to the house? Do I use the existing buried cable, and follow the wiring back to the switch, disconnecting it from the main feeder? Or do I need to pull a second set of cables through a second conduit back to the house? From my understanding, I can’t have the cables feeding a subpanel in the same conduit as a subpanel circuit running to a switch, correct? If I use a second conduit, I still would not be able to access that conduit for any other low-voltage circuits such as telephone or Ethernet, correct? That would require a third conduit.
exranger06
CT
Questions:
#3 copper with #8 ground is good for 100A. I don't know if you can downsize the neutral.
EMT is a terrible choice for underground conduit. It will rust away to nothing in less than 5 years. Use PVC conduit. I recommend 1.5".
Just because you only see one wire doesn't mean there's only one rod. It's very possible there's another wire that's buried underground that goes from one rod to the other. Both rods should be completely buried though. I would try to hammer the rod that's sticking up down. Install 2 more ground rods at the garage.
None of your 240V circuits need GFCI. Lighting does not need GFCI. All 120V receptacles need GFCI.
You have two options here: Wire the receptacles as a multi-wire branch circuit. It's basically 2 circuits that share the same neutral wire. Use 12/3 wire instead of 12/2. Break off the tab on the hot side of the receptacles only, leave the tab on the neutral side alone. Connect black wire to top outlets, red wire to bottom outlets (or vice-versa, but keep them consistent). Since all of the receptacles need to be GFCI protected, you'll need to use GFCI double-pole breakers.
The other option is to break the tabs on both the hot and neutral sides and run two 12/2 cables to each receptacle. The neutrals for each circuit will need to be kept separate. You can use regular (non-GFCI) breakers, but you'll need to install 2 GFCI receptacles (one for each circuit).
The screws on receptacles are designed for only one wire, unless they have the little plate things (can't think of the proper name for them right now) under the screw. Use pigtails.
Use the existing wire, disconnect the feed at the switch in the house, re-feed the circuit from the garage panel. Done. You COULD run new wire in the same conduit as the subpanel feed, but you'd need to derate the conductors. Or you could run a new, separate conduit. Low voltage and Ethernet cables cannot be in the same conduit as electric.
I wasn't able to answer all of your questions, but I answered at least some of them in red above.
teamextreme
Lakewood, CO
exranger pretty much nailed it. I can add a few things. On your question on conductor choice, either THWN or XHHV will work. I've always used THHN/THWN and it pulls as easy as anything else, IMO. I ran 100A service to my detached shop and ran 3 #3's and can't remember the size ground, all in 45ft of 1.25" PVC with 2 90's and a 45. I pulled it by myself with no problem at all.
You can phase tape the second hot, but it's not necessary. They're both hot, they can both be black. The neutral can be phase taped white.
I second what exranger said about the ground rod, just because you only see one wire doesn't mean there's not 2 rods. I only have 1 wire leaving my panel to my 2 rods. However, you would see the wire looping through the connector at the rod you can see and continuing on to a second rod. Having said that, there's a large percentage of electricians (and inspectors) that are not aware of the 2 rod requirement and it seems to be very common even for permitted, inspected work to only have 1 rod. You are required and should install 2.
Regarding EMT underground, that is an absolutely terrible idea, as previously mentioned, and I can't stress enough to NOT do it (I frankly don't understand how it's still even allowed by NEC). PVC is cheaper, easier to work with and will last forever.
I would re-think the double circuits on each duplex recep. I think it's total overkill (even by GJ standards) and introduces a bunch of issues. You need expensive double pole GFI breakers, if anyone replaces the outlet in the future they are likely to screw it up with all the tab breaking required, etc., and I don't see any advantage to it. Are you really going to be running such heavy, mulitple loads from the same recep that 2 20A circuits would be required? Doubtful. Just use a simple 2-wire circuit and drop a GFI recep at the first box and limit the number of recep's on a circuit if your concerned with loading.
C
Cruzan80
Denver, CO
Thanks guys. Like I said, I was sure I wasnt thinking of some things (like putting EMT underground). Sounds like THHN is fine, and then I dont have to tape anything (can get it in multiple colors). I will look and double check if there is one or two ground rods at the house. I read the requirement as needing to measure at least X for one rod (forget the number), or install two rods to reach/exceed X. I figured if one rod was good enough for the main dwelling (met X), then 100ft away would also meet X. A second rod isn't so expensive that it is worth skipping if needed.
This is for a forever house for us, and I wanted to make sure if I had a machine running (which some come close to 15A), and I plug in a vacuum, I dont flip the circuit. Not as worried about someone else screwing it up later, as there will be two lines of 12/2 entering and leaving, so it should make someone stop and question.
The other thought I had is if the GFI breaker ends up being more than I want to spend is to have the first set of outlets to be in a double gangbox, with two GFCI outlets (one for each circuit). Then label either on the outlet or the faceplate to keep them straight.
If anyone else has comments or suggestions, I am about a week or so away from running all this.
Sent from my Moto G (5) Plus using The Garage Journal mobile app
mike93lx
Richmond, VA
I would run #2 aluminum and a 90a breaker at the main. Will be a good amount cheaper.
I would also run 2" conduit. Also lay in a smaller conduit, maybe 1" for cable and/or data.
C
Cruzan80
Denver, CO
How would #2 copper be cheaper than #3? From what I read, #3 is good for 100A. Or are you saying a 90A breaker is substantially cheaper than 100A? Why 2" conduit if this is the only line allowed in it?
I am planning on laying a second conduit empty for data usage later.
Not arguing, but trying to understand.
mike93lx
Richmond, VA
Sorry, #2 aluminum is what i meant
Bigger conduit makes for an easier pull
C
Cruzan80
Denver, CO
Thanks for the clarification. Looks like I would need #1 AL to maintain the 100A, but it is still half the price of the #3 CU. I am guessing the upsizing of the conduit is due to the larger gauges? What issues would I have to watch out for if I have never done AL? I have run CU circuits before. What is the minimum neutral for 100A in AL?
mike93lx
Richmond, VA
Why do you need 100a? For a one man shop, the chances of 90a being too little, yet 100a being enough are probably slim to none. It is your money.
2" conduit is not required, just makes it all easier.
Just need to use anti oxidant paste, if the manufacturer calls for it. Nothing tricky.
A sparky would be better to comment on neutral and ground, but with 2 gauge, 2-2-4-6 and 2-2-2-4 are common
C
Cruzan80
Denver, CO
When I added up the full potential load I could have running at one time (heater, compressor, car charger, large 240v tool and some 120v load from lights/vac/etc) I was into the 80s. Would rather give myself some space, just in case I have a buddy over. Since I have to run it all, better to upsize now than get frustrated later that I tried to save a bit. Looks like it would be about $50-60 more in wire costs, total. So more of a why not if I am going to this much effort to save under $100?
Again, I appreciate the viewpoint, and not just being snarky. Answers both in favor of and differing viewpoints each help me narrow down what I want. And maybe someone else who is watching will make a different decision than me, and they are helped in a different way.
mike93lx
Richmond, VA
If you think you could have concurrent usage of 80+Amps, i don't think 100A is building in much room. What if you upgrade to a bigger car charger? For a forever home, i'd plan for the potential of a charger that can pull over 50a on its own.
Plus 30a for an electric heater isn't much. I have one in my 2car and it just takes the edge off.
PCustoms
VT
Did you add the actual draw, or theven breaker size?
80A sounds nuts for a 1 man shop.
C
Cruzan80
Denver, CO
The heater is 23, the compressor may be about the same, the car pulls 15, tool may pull 10+, and lights/etc. So I get at least 70+ from actual draw. Not using too many tools in this scenario, but several high-draw "accessories".
On vacation now, so hard numbers are not in front of me. Going by memory...
wyliesdiesels
Modesto, CA
Whats the HP rating on the compressor motor label?
C
Cruzan80
Denver, CO
Right now, the compressor is on a 20A circuit (SPL HP rating) and pulls about 15-18A, but have a huge Quincy pump and plan on sourcing an actual 5hp motor to pair with it down the road. So that is what enters into my calculations.
wyliesdiesels
Modesto, CA
ok well a 5hp motor requires 35a rated wire- #8 NM-b or #10 THWN in pipe. Motor must be hardwired unless a properly rated outlet and plug is used.
C
Cruzan80
Denver, CO
Yeah, plan is to run a thicker wire than is needed for now, install breaker to match current motor, and swap breaker when I install new motor. Current motor is hardwired, and the new one will be as well.
But when I am calculating overall possible amp draw when planning this subpanel, I am going to be using the larger (potential) motor.
75gmck25
Alexandria, VA
The reason many folks recommend 90 amps is that 2-2-2-4 AL MHF with dual rating (rated for both burial and within building in conduit) is sold everywhere and available for a very reasonable price. Getting that additional 10 amps (for 100 amps) will add more than you think. You can still use a 100 amp panel to get the number of breakers you need, but use a 90 amp breaker in the main panel.
Bruce
C
Cruzan80
Denver, CO
Thanks for this. Was pricing out individual connectors, and wasn't seeing what the deal was. Now that I know there is another option, can better decide on cost vs usefulness.
Kept reading about how various kinds of cabling are not allowed in various parts of this install (no nm-b underground at all, no SER buried underground, no URD inside) that I was going with single strands to be safe. Now I know there is an option for it to be purchased "together".
mike93lx
Richmond, VA
If you are using conduit, buy individual conductors, as it will be easier to pull and there ia no long a benefit of the bundle.
MHF makes the most sense when you are doing direct burial