What are my options for wire and breaker sizing? Motor is 12.2/6.1 amp the max amps are16.2/8.1.
 
To avoid these ads, REGISTER NOW!
OP
R

rodm1

Well-known member
Joined
Feb 17, 2008
Messages
2,275
Well is 25ft

View media item 96308
a298749a9b5ba72e5d98c6fe28365355.jpg
 
Last edited:
OP
R

rodm1

Well-known member
Joined
Feb 17, 2008
Messages
2,275
Would 12ga on a 40amp single pole breaker work? 16.2amp makes it 12ga 2.5 x that for startup breaker 40amps?
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,929
Location
NW Iowa
Would 12ga on a 40amp single pole breaker work? 16.2amp makes it 12ga 2.5 x that for startup breaker 40amps?

Good luck finding a 1 pole 40...

This is going on a dedicated circuit no matter what so just wire it for 240. 14 gauge wire on a 2 pole 20.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,268
Location
Modesto, CA
Why do you insist on running it on 120v?

Also, the multiplier for in-rush current is not 2.5x

In-rush current can be 4x-8x the FLA on the nameplate. But thats not how to size the breaker.

Also, do you have a pump controller?
 
To avoid these ads, REGISTER NOW!
OP
R

rodm1

Well-known member
Joined
Feb 17, 2008
Messages
2,275
No pump controller. But trying to get an ball park idea of what is needed I see breaker and wire size very greatly from chart to chart. Would like to pick up the parts soon will have to order a breaker just might use the 25amp one I have until then.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,268
Location
Modesto, CA
All it needs is a pressure switch. They are usually good to 2hp without a starter.

If this pump has a start winding(3wire with no ground or 4 wire with ground), it will most definitely need a controller/starter.

how would someone run a pump with a start winding without a controller that has a relay, capacitor and overload?

OP what wires does your pump have?
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,929
Location
NW Iowa
If this pump has a start winding(3wire with no ground or 4 wire with ground), it will most definitely need a controller/starter.

how would someone run a pump with a start winding without a controller that has a relay, capacitor and overload?

OP what wires does your pump have?

This is a shallow well pump. It has a regular motor. Capacitor, start switch all that is in the motor. All you need to do is turn the power on and off. Notice how the enclosure type is open drip proof and it has a standard frame size.

A submersible pump would need a pump control.
 
Last edited:

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
3,036
Location
Peace Valley,mo
Having a 1 hp motor. on 120volts really not recommended because thats a lot of amperage on a circuit breaker panel causing a imbalanced load on it.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,268
Location
Modesto, CA
This is a shallow well pump. It has a regular motor. Capacitor, start switch all that is in the motor. All you need to do is turn the power on and off. Notice how the enclosure type is open drip proof and it has a standard frame size.

A submersible pump would need a pump control.

Aww yeah whoops.

I missed that.

Thanks
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,315
Location
NJ
Good luck finding a 1 pole 40...

This is going on a dedicated circuit no matter what so just wire it for 240. 14 gauge wire on a 2 pole 20.

35a would probably be the correct size. Easy enough to order but why?

@240v, the pump can have a total cable length of 130' w/#14.

@120v, #12 cable is needed and only good for 52'.
@120v, #10 cable is needed and only good for 80'.
 