Wiring in wall convection oven...HELP
Quick01GT
SoCal
I think my “electrician” put the wrong size romex in the wall for my kenmore elite in wall convection oven/microwave combo.
He installed 10/3 (60 feet) and a 40 amp breaker. I believe for starters the wire is too small for the breaker installed. Either way I want to do it right!
Below is a picture of the label inside my oven, there is only one set of wires coming out of the combo.
Q
Quick01GT
SoCal
Yeah 8/3 is what I thought I needed as well.
What kind of connectors do I need? Any special ones or are the Home Depot ones fine?
wyliesdiesels
Modesto, CA
You only need 8/2. Its 240v 3-wire
Connectors? This is getting hardwired correct?
Only thing you need is the right size wire nuts.
But i would make him come back and fix it
EDIT: You need 8/3. I missed the 120/240 at the nd
Bert_
NW Iowa
Did you give him specs for the new oven when he was roughing in the wiring? I say that because most built-in ovens will run on a number 10.
It's not a big enough wire for this oven. If you didn't give him the correct information this is on you though.
AntonLargiader
Charlottesville, VA
I'd check the actual appliance before determining that you need 8/2 rather than 8/3. I just looked at a random manual for a similar unit and it showed a neutral and a ground.
u2slow
BC
How many kW is the oven? Mine was 10.7kw so a #8 wouldn't do.
I ran #6/3 to a small subpanel next to it. A 30amp 2pole breaker for each oven a 15amp 1P for the controls and oven lights.
Q
Quick01GT
SoCal
I gave him the same information I posted here, he allegedly called kenmore to verify. I don’t believe he did because when I called kenmore they told me to call an electrician.
wyliesdiesels
Modesto, CA
Then its on him to rip it out and put the correct wire in.
Is this guy licensed?
Putting #10 NM-b on a 40a breaker is no bueno.