240 volt wiring - how many wires required?

OptionalStop

Well-known member
Joined
Mar 23, 2018
Messages
128
Location
Rochester NY
Does NEC require all 240v circuits to have a neutral wire in new construction? I know that the neutral is required for some appliances such as washers and dryers that would utilize 120v thus requiring the neutral but what about our garage tools like tablesaws and welders? Is it OK to use 3 wires (hot, hot, ground)?
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,011
Location
Modesto, CA
Does NEC require all 240v circuits to have a neutral wire in new construction? I know that the neutral is required for some appliances such as washers and dryers that would utilize 120v thus requiring the neutral but what about our garage tools like tablesaws and welders? Is it OK to use 3 wires (hot, hot, ground)?

There is no requirement for a neutral in a circuit for 240v utilization equipment.

Also, washers are 120v not 240v.
 
Last edited:

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
I used 10-3 for the lift because 10 was the manual spec (overkill IMHO for the motor draw but whatever) so I could peal off a 120V plug at the lift. The compressor uses a 240V run if 12-2 w/ground romex because it's only 3.2HP. The white is re-tagged as the other hot for the motor - no neutral required. The heater uses 10-2, no neutral required. Unless the end piece needs a neutral for something specific, you could pull whatever was cheaper.
 
OP
O

OptionalStop

Well-known member
Joined
Mar 23, 2018
Messages
128
Location
Rochester NY
I used 10-3 for the lift because 10 was the manual spec (overkill IMHO for the motor draw but whatever) so I could peal off a 120V plug at the lift. The compressor uses a 240V run if 12-2 w/ground romex because it's only 3.2HP. The white is re-tagged as the other hot for the motor - no neutral required. The heater uses 10-2, no neutral required. Unless the end piece needs a neutral for something specific, you could pull whatever was cheaper.

Thanks. And, re-labeling white neutral wires as hot in romex is code compliant?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,011
Location
Modesto, CA
I used 10-3 for the lift because 10 was the manual spec (overkill IMHO for the motor draw but whatever) so I could peal off a 120V plug at the lift.

What did you breaker the circuit at?

The compressor uses a 240V run if 12-2 w/ground romex because it's only 3.2HP. The white is re-tagged as the other hot for the motor - no neutral required. The heater uses 10-2, no neutral required. Unless the end piece needs a neutral for something specific, you could pull whatever was cheaper.

Technically, NM-b 12/2 is too small for that motor because a 3HP(17a FLC) motor needs ~21a rated wired. #12 NM-b is limited to 20a and your motor is a bit over 3HP.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,754
Thanks. And, re-labeling white neutral wires as hot in romex is code compliant?

As long as it is part of a cable assembly it is permitted to re-mark the white conductor but it is not allowed to do it with a white conductor in a conduit.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Does NEC require all 240v circuits to have a neutral wire in new construction? I know that the neutral is required for some appliances such as washers and dryers that would utilize 120v thus requiring the neutral but what about our garage tools like tablesaws and welders? Is it OK to use 3 wires (hot, hot, ground)?


You are correct, if its a straight 240 v load, water heater, AC condenser, electric furnace then yes, all you need is 2 hots and a ground. In the old days, electric dryers and ranges only had a 3-prong plug. They bonded the neutral and equipment ground together, but later figured out that this was not such a good idea. So now, all new circuits installed for these appliances has to be 4 wire, which separates the neutral and ground. You can still buy 3-prong cords and receptacles for replacement. But if you are running a new circuit for these appliances, it should and needs to be a 4 wire circuit. You would use a 10/3 or 8/3 and so on depending on the load. And yes the neutral in these appliances is required because they also need 120 volts, like a electric dryer, the heating element is 240v but the motor is 120v
 

checkthisout

Well-known member
Joined
Sep 5, 2008
Messages
5,232
What did you breaker the circuit at?



Technically, NM-b 12/2 is too small for that motor because a 3HP(17a FLC) motor needs ~21a rated wired. #12 NM-b is limited to 20a and your motor is a bit over 3HP.

All the automotive lifts I have installed in the last 10 years or so have always spec'd a 25 AMP breaker and 10 gauge wiring.

Of course there are different lifts but most automotive lifts seem to use the same SPX pump/motor assembly.
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
>What did you breaker the circuit at?

20A. The wires in the motor control box are 14 gauge so 20A is plenty even though I pulled 10 gauge. No trips.

Technically, NM-b 12/2 is too small for that motor because a 3HP(17a FLC) motor needs ~21a rated wired. #12 NM-b is limited to 20a and your motor is a bit over 3HP.

Interesting. No trips in 8 years. (3.2 HP x 745w/HP) ./ 240v = 9.93A. Assume the 21A requirement is for that momentary start surge?
 
Last edited:

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
Found a table that listed 3 HP motor as 17A FLA, 30A "Optimal branch circuit protection" and "Min copper wire Table 310.16" as 12. This should right? 3.2 is a bit over, agree. I should put a clamp on it running and see if that import motor is really pulling the expected current.
 

MattT

Well-known member
Joined
Feb 20, 2010
Messages
3,201
Interesting. No trips in 8 years. (3.2 HP x 745w/HP) ./ 240v = 9.93A. Assume the 21A requirement is for that momentary start surge?

Your calc is for output mechanical power not input electrical power. Motor isn't 100% efficient.

21A is a 1.25 times FLA sizing requirement in the NEC. It's basically so the motor can be ran continuously at FLA without the wire overheating.

Found a table that listed 3 HP motor as 17A FLA, 30A "Optimal branch circuit protection" and "Min copper wire Table 310.16" as 12. This should right? 3.2 is a bit over, agree. I should put a clamp on it running and see if that import motor is really pulling the expected current.

That table is for THHN wire which is good for 25A. #12 romex is only good for 20A which is why Wylie said you should have used #10.

And don't read too much into whatever amp readings you get. A lot of modern motors actual FLA is lower than the NEC FLA. And the compressor might not be designed to load the motor to 100% either.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,590
Location
BC
Found a table that listed 3 HP motor as 17A FLA, 30A "Optimal branch circuit protection" and "Min copper wire Table 310.16" as 12. This should right? 3.2 is a bit over, agree. I should put a clamp on it running and see if that import motor is really pulling the expected current.

Are we not using nameplate data before we revert to generic table values?

I have a 3hp 240V compressor also. (Speedaire portable.) Nameplate says 15.7amps FLA. Ships with a 6-20P plug. You guessed it... I wired it with #12 and 6-20R on a 20A breaker. Has worked that way in two different shops for 20 years.
 

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
Are we not using nameplate data before we revert to generic table values?

I have a 3hp 240V compressor also. (Speedaire portable.) Nameplate says 15.7amps FLA. Ships with a 6-20P plug. You guessed it... I wired it with #12 and 6-20R on a 20A breaker. Has worked that way in two different shops for 20 years.

These NEC tables don't apply to cord-and-plug connected portable equipment. If you're hard-wiring a compressor, you're supposed to go by HP rating and follow the tables in the NEC. The nameplate data is basically irrelevant.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,590
Location
BC
These NEC tables don't apply to cord-and-plug connected portable equipment. If you're hard-wiring a compressor, you're supposed to go by HP rating and follow the tables in the NEC. The nameplate data is basically irrelevant.

That's funny. CEC says go by the nameplate. And somehow a cord-and-plug and makes undersized wire ok (according to NEC).

Its hard to take either Code seriously at times :wtf:
 
To avoid these ads, REGISTER NOW!

MattT

Well-known member
Joined
Feb 20, 2010
Messages
3,201
That's funny. CEC says go by the nameplate.

NEC method makes more sense IMO. Their FLA covers any ** HP motor so you know the wire is good for a replacement motor so long as it's the same HP. Using the CEC method you might need to pull new wire if your replacement motor is less efficient.

NEC also makes quoting & running motor circuits really easy. All you need to know is HP. No trying to hunt down nameplate data, which can be a real problem if the motor isn't even on site yet.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,590
Location
BC
NEC method makes more sense IMO. Their FLA covers any ** HP motor so you know the wire is good for a replacement motor so long as it's the same HP. Using the CEC method you might need to pull new wire if your replacement motor is less efficient.

NEC also makes quoting & running motor circuits really easy. All you need to know is HP. No trying to hunt down nameplate data, which can be a real problem if the motor isn't even on site yet.

Not really... you simply size and quote on the info you have available. Machine first, table second. Its not like we get a choice which Code to use. :beer:
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
These NEC tables don't apply to cord-and-plug connected portable equipment. If you're hard-wiring a compressor, you're supposed to go by HP rating and follow the tables in the NEC. The nameplate data is basically irrelevant.

LOL, I'm off the hook - my 60 gallon compressor is cord-and-plug. Portable....well, sure - it sits on a skid in a closet and can be slid out and pushed around for service.
 

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
LOL, I'm off the hook - my 60 gallon compressor is cord-and-plug. Portable....well, sure - it sits on a skid in a closet and can be slid out and pushed around for service.

But, is it ALLOWED to be cord-and-plug connected? Motors over 3 HP must be hard-wired, unless you're using a pin and sleeve type plug/receptacle that's rated for the HP.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,590
Location
BC
But, is it ALLOWED to be cord-and-plug connected? Motors over 3 HP must be hard-wired, unless you're using a pin and sleeve type plug/receptacle that's rated for the HP.

So why are 3-5HP compressors in the tool stores and Costco with 6-20P and 6-30P cords? :headscrat
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,590
Location
BC
Those are "SP" HP ratings and greatly inflated^^^^^ due to the different way of computing versus the "true hp".

Agreed... in which case my compressor is '6HP' per the propaganda. My shop vac is at least 4HP. :spit:
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,590
Location
BC
And the plate says 5HP or SPL?

Ive never seen a motor rated 5HP with a cord and plug.

Plate says SPL. FLA 15A. Then further down it says electrical output: 2.98kW (which is almost 4hp). Motor is a Dayton. KMS Tools called it 6hp. Acklands/Grainger calls it 3hp. Factory 6-20P cord.

The 5HP/6-30p corded machine was something I saw at Costco a couple years ago. Coleman or DeWalt 60gal upright model, I forget. Odd electrical things stick in my head.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,754
Plate says SPL. FLA 15A. Then further down it says electrical output: 2.98kW (which is almost 4hp). Motor is a Dayton. KMS Tools called it 6hp. Acklands/Grainger calls it 3hp. Factory 6-20P cord.

The 5HP/6-30p corded machine was something I saw at Costco a couple years ago. Coleman or DeWalt 60gal upright model, I forget. Odd electrical things stick in my head.

CEC may have different rules then the NEC.
 

checkthisout

Well-known member
Joined
Sep 5, 2008
Messages
5,232
750 watts per horsepower.

5 Hp harbor freight plug in compressor working off a 15 amp outlet. The math doesn't really workout.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,590
Location
BC
CEC may have different rules then the NEC.

Sure. Don't have my book, but IIRC, cord-connected things get to skip motor circuit sizing.

The speedaire 1NNF7 3hp portable compressor lists on US websites just the same. The online manual says it uses a plug connection. Would be an odd 'portable' if it needed hardwiring.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,011
Location
Modesto, CA
Plate says SPL. FLA 15A. Then further down it says electrical output: 2.98kW (which is almost 4hp). Motor is a Dayton. KMS Tools called it 6hp. Acklands/Grainger calls it 3hp. Factory 6-20P cord.

The 5HP/6-30p corded machine was something I saw at Costco a couple years ago. Coleman or DeWalt 60gal upright model, I forget. Odd electrical things stick in my head.

SPL is meaning less. 15a FLA is close to 3HP and can be plug connected.

Was the 5HP with the 6-30p labeled 5HP on the motor nameplate?

750 watts per horsepower.

5 Hp harbor freight plug in compressor working off a 15 amp outlet. The math doesn't really workout.

That figure is for 100% efficiency but no motor is 100% efficient

Sure. Don't have my book, but IIRC, cord-connected things get to skip motor circuit sizing.

The speedaire 1NNF7 3hp portable compressor lists on US websites just the same. The online manual says it uses a plug connection. Would be an odd 'portable' if it needed hardwiring.

The issue with plug connected motors above 3HP is that there are no NEMA plugs rated for more than about 3HP and NEC code requires that the plug HP rating matches the motor HP rating
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,590
Location
BC
Was the 5HP with the 6-30p labeled 5HP on the motor nameplate?

I can't remember. What I do remember is it needed more power and had a higher cfm than my Speedaire. Vertical 40-60gal tank. Probably a 3.7 or 5hp motor. I'm beginning to wonder if it was pre-wired with an minimal contactor/disconnect; I do know Costco often has products tailored for them specifically.
 