Supply house sold me the wrong wire

OptionalStop

Well-known member
Joined
Mar 23, 2018
Messages
128
Location
Rochester NY
Last spring I bought the service wire for my new building which I specified I needed 2-2-2-4 MHF. Well they sold me URD cable instead which as 3 black and 1 black with white stripe. This is rated for direct bury but not to go inside the structures. Is my only option to mount junction boxes on the outsides of each building to transition to the proper wire to go inside? Pretty pissed they sold me the wrong wire when I specified, but I should have known better and was just in a hurry. My URD cable is already buried and installed so I just need to dig up at each building.
 
To avoid these ads, REGISTER NOW!

SGKent

Banned
Joined
Feb 12, 2010
Messages
1,959
Location
Citrus Heights CA
look at the receipt and see what it says they sold and what they shipped. Then call them and see if they will exchange and bill you the difference.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Read the markings on the side of the URD.

The stuff they sell over is here is Alcan cable brand and it carries the RHH, RHW, etc markings on it which allow it to enter a structure.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,581
Location
Fullerton, CA
Is my only option to mount junction boxes on the outsides of each building to transition to the proper wire to go inside?

The only option I can see (besides the boxes) is to use an outside disconnect on the building you're planning on and make the transition there.
The 'future' 2020 Code will require them anyway.
You're pretty much stuck with a box for the transition on the existing building.
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,334
Location
Northern Virginia
The only option I can see (besides the boxes) is to use an outside disconnect on the building you're planning on and make the transition there.
The 'future' 2020 Code will require them anyway.
You're pretty much stuck with a box for the transition on the existing building.

OP said the URD is already buried so he is committed...

Sounds like he is also committed now to junction boxes for the transitions.
 
OP
O

OptionalStop

Well-known member
Joined
Mar 23, 2018
Messages
128
Location
Rochester NY
Yes, if this doesn't pass inspection I will have to install boxes. However I talked to 2 licensed electricians this morning and they said this cable is OK to run inside conduit in the buildings.
 

slow

Well-known member
Joined
Feb 26, 2006
Messages
2,596
Location
near Orlando
honest question, would an LB on the outside of the structure going into the back of the panel be a violation? Or would that still be considered "inside the structure"
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,633
Location
Richmond, VA
honest question, would an LB on the outside of the structure going into the back of the panel be a violation? Or would that still be considered "inside the structure"

How wouldn't that be inside the building? Of course it is.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,030
Location
Modesto, CA
honest question, would an LB on the outside of the structure going into the back of the panel be a violation? Or would that still be considered "inside the structure"

And LB cannot be used for splicing so thus the cable would end up going inside the building.
 

nh_yota

Well-known member
Joined
Mar 10, 2015
Messages
4,077
Location
Seacoast New Hampshire
If you run it up the outside wall through conduit and straight into the back of the panel using an LB then I think you would be okay. Running it through the walls is a different story. Of course it really depends on how picky the local inspector will be.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,633
Location
Richmond, VA
The pickiness of the inspector doesn't matter. It is either to code or not.

You may skate by but that doesn't make it right. Any the position your insurance company takes may differ from the inspector's opinion
 

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,449
Location
USA
Supply houses in my region dont carry MHF at all. If you ask for 2-2-2-4, you're gonna get URD.
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,975
Location
NJ
OP, did you double-check the marking on the conductors?

USE comes in 2 flavors - single rated and triple rated.

Here is the details on triple rated USE cable. Triple rated permits interior use while a straight single rating of USE only is not permitted inside.

http://www.stabiloy.com/NR/rdonlyre...1-8AEF294E0295/0/BW0015ASTABILOYBrandUSE2.pdf

General Cable seems to offer only triple rated USE while Southwire offers single and triple rated.
 
Last edited:
OP
O

OptionalStop

Well-known member
Joined
Mar 23, 2018
Messages
128
Location
Rochester NY
OP, did you double-check the marking on the conductors?

USE comes in 2 flavors - single rated and triple rated.

Here is the details on triple rated USE cable. Triple rated permits interior use while a straight single rating of USE only is not permitted inside.

http://www.stabiloy.com/NR/rdonlyre...1-8AEF294E0295/0/BW0015ASTABILOYBrandUSE2.pdf

General Cable seems to offer only triple rated USE while Southwire offers single and triple rated.

My wire only has USE-2 marking on it, RHH RHW-2 is not there. So, I will have to install boxes outside both buildings. Not exactly thrilled about this.
 

Bretny

Well-known member
Joined
Jul 31, 2017
Messages
3,918
Location
Dutchess county NY
I had a similar situation with a local supply house. I measured out the wire i needed and tripple checked everything then added 10ft extra. I get digging and installing my service for my garage and the guy shorted me 25ft. It had to be backfilled that day so i had no choice but to use it. Went back and they guy basicly threw the piece at me and told me to get out. No connectors or anything. Il buy my wire from home depot now.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,030
Location
Modesto, CA
I had a similar situation with a local supply house. I measured out the wire i needed and tripple checked everything then added 10ft extra. I get digging and installing my service for my garage and the guy shorted me 25ft. It had to be backfilled that day so i had no choice but to use it. Went back and they guy basicly threw the piece at me and told me to get out. No connectors or anything. Il buy my wire from home depot now.

If you gave them the correct footage and they shorted you then it’s on them to give you the new piece of wire at the correct length
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,633
Location
Richmond, VA
If you gave them the correct footage and they shorted you then it’s on them to give you the new piece of wire at the correct length

But what are you really going to have done about it? They aren't going to redig the trench. Sure, you could take them to small claims court...
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,581
Location
Fullerton, CA
I had a similar situation with a local supply house. I measured out the wire i needed and tripple checked everything then added 10ft extra. I get digging and installing my service for my garage and the guy shorted me 25ft. It had to be backfilled that day so i had no choice but to use it. Went back and they guy basicly threw the piece at me and told me to get out. No connectors or anything.

I would have asked you to return the wire they gave you as proof of their mistake. Did you return the old connectors and not receive any back?
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,581
Location
Fullerton, CA
Ya, cause there is no such thing as a shady, hack contractor - right?

That's not the reason. Contractors know what they want and they specify, often by the part #.

DIYs often don't know, and they expect the counterman to know exactly what they need. If they don't understand the terms, or use the wrong terms (ie: a plug vs a receptacle) they waste the counterman's time.
 

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
That's not the reason. Contractors know what they want and they specify, often by the part #.

DIYs often don't know, and they expect the counterman to know exactly what they need. If they don't understand the terms, or use the wrong terms (ie: a plug vs a receptacle) they waste the counterman's time.
And theres your answer.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,030
Location
Modesto, CA
that's not the reason. Contractors know what they want and they specify, often by the part #.

Diys often don't know, and they expect the counterman to know exactly what they need. If they don't understand the terms, or use the wrong terms (ie: A plug vs a receptacle) they waste the counterman's time.

bingo! :+1: :+1: :beer:
 