The detached garage is fed from a 50A breaker from the house panel. The incoming hots are the two heavier gauge wires, and the yellow jacketed is the other incoming. They wired a 50A welder outlet right off the incoming lugs (the smaller gauge wires gout out to the left). Is that kosher??
The bare aluminum wires are the other conductor going to the welder.
What do I need to do to make this right? Photos or links to photos to help me understand would be great
Thanks.
PS - I did not wire this. It was the previous owner or his son, both of whom run a contracting firm building high-end lake homes up here.
Lots wrong here. smh
the welder circuit wires need to go to a breaker.
You will need to torque the feed lugs again.
How many breakers do you have there? If more than 6 handles then you will need a main breaker. It would have to be backfed since that panel is probably not convertible.
Neutral wire is wrong color.
Can't tell if you have a GEC wire that would go to grounding electrodes. Is there ground rods? If not you will need 2 ground rods.
How long ago was this hooked up? If after 2008 code cycle then the bonded neutral bus is incorrect. it will need either a new feeder or an additional wire for the ground as well as a ground bar. you would remove the bonding strip or screw for the neutral bar.
What kind of wire feeds this panel? jacketed/bundled wire or wire in conduit? What kind of conduit? If metal, then it most definitely needs a 4-wire feeder.
The double tapped wires on the neutral bar need to be fixed as well. Can only have 1 neutral per lug.
Most panels allow 2 grounds per lug...
no it does not look right.
to fix you need to:
feed the welder from a breaker.
do double tapping all those grounds/N's.
you need to have a separate ground vs N in a sub panel as well. this means pulling another wire to the sub building technically.
you need local ground rods as well on the sub building.
otherwise it looks great. did they chew the wires bare?
that actually depends on when this was installed. If before 2008 code cycle, then it is permissible to have a bonded neutral on a detached as long as there are no parallel metallic pathways.